I agree with your interpretation of my remarks.  I know that the Committee 
intended to require pressure treating and made changes to the rules to prevent 
the widespread use of coated applications........, however........ rules is 
rules and equivalency is in the eye of the beholder and can be granted by an 
AHJ....... I am thusly aligned with NFPA.




It should be recognized that the above is my opinion as a member of the NFPA 13 
Committee, and has not been processed as a formal interpretation in accordance 
with the NFPA Regulations Governing Committee Projects and should therefore not 
be considered, nor relied upon, as the official position of the the NFPA, nor 
any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com<http://www.sprinkleracademy.com>
[email protected]<mailto:[email protected]>
??
OUR STUDENTS SAVE LIVES!!


________________________________
From: Sprinklerforum <[email protected]> on behalf 
of tstone52--- via Sprinklerforum <[email protected]>
Sent: Wednesday, February 10, 2021 11:15 AM
To: [email protected] 
<[email protected]>
Cc: [email protected] <[email protected]>
Subject: RE: Fire Retardant Coating used in Combustible concealed spaces

Greg, Cecil,
I just want to verify that if a Coating is applied, I will still need to
apply the 3,000SF design area rule because this in not Treated Lumber or
filled with noncombustible insulation.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Greg McGahan via Sprinklerforum
Sent: Wednesday, February 10, 2021 11:20 AM
To: [email protected]
Cc: [email protected]
Subject: RE: Fire Retardant Coating used in Combustible concealed spaces


And the ones I have looked at had to be reapplied in the future. They have a
lifespan of effectiveness.
Respectfully,

Greg McGahan



4187 Farrington Rd. Milton, FL 32583
P- 850-637-8535
C- 850-712-9555

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Fpdcdesign via Sprinklerforum
Sent: Wednesday, February 10, 2021 10:06 AM
To: Sprinklerforum <[email protected]>
Cc: Fpdcdesign <[email protected]>
Subject: Re: Fire Retardant Coating used in Combustible concealed spaces




 Flame retardant coatings has to be installed according to strict guidelines
and the thickness of the coating needs to be verified after installation.
Tends to be expensive. Most projects I have worked on have junked that idea
for that reason.








>
> On Feb 10, 2021 at 10:34 AM,  <tstone52--- via Sprinklerforum
(mailto:[email protected])>  wrote:
>
>
>
>  Project is a 100 year old 6 story Steel  &  Concrete Hotel building.
> The
roof is steel framed with concrete above and the Sixth floor ceiling is
Plaster over metal lath. Over the years the building has been added onto
with wood framing above the Sixth floor ceilings. As Part of a major
renovation started in 2020, the installation of a complete NFPA 13 sprinkler
system and Standpipes is taking place. A few substantial combustible
concealed spaces have been discovered throughout the building on other
floors too. If nothing is done the sprinkler design areas would need to be
increased to 3,000 SF as outlined in Chapter 11.2.3.1.5. The sprinkler
contractor and I have suggested filling these spaces with noncombustible
Insulation. The architect and builder are discussing Flame Retardant Coating
to be applied to the wood framing in order meet the Non-Combustible and
Limited Combustible concealed space definition. In reviewing Chapter
11.2.3.1.5.2 I don't see where Flame Retardant Coating  is an option in
order to reduce the  design area. I believe In order to reduce the Design
areas these combustible spaces need to be filled with noncombustible
Insulation. Would "Flame Retardant Coating" be considered an option as
outlined in A.8.15.1.2.11 (commentary text) the equivalency provisions in
Section 1.5? Thank you for your imput. Regards, G. Tim Stone G. Tim Stone
Consulting, LLC NICET Level III Engineering Technician Fire Protection
Sprinkler Design and Consulting Services  117 Old Stage Rd. - Essex Jct
(x-apple-data-detectors://3).,  VT. 05452
(x-apple-data-detectors://4/0)  CELL:  (802) 373-0638 (tel:(802)%20373-0638)
TEL:  (802) 434-2968 (tel:(802)%20434-2968)   <mailto:[email protected]>
[email protected] (mailto:[email protected])
_______________________________________________ Sprinklerforum mailing list
[email protected]
(mailto:[email protected])
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-f
iresprinkler.org
>
>



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to