First off, it needs to be determined based on the CODE or local ordinance if 
this is even allowed.  Forget NFPA 13 for the moment.

The fuel loading within a typical food truck is pretty high considering the 
amount of gasoline and propane in each truck.  If you look at this simply from 
a chemical loading standpoint, Class IB liquids have a limit based on the 
Building and Fire codes before you are in an "H" occupancy even in a 
sprinklered building.  Once you are an "H" occupancy there are other numerous 
requirements and limitations related to the building construction, egress, 
HVAC, life safety, etc., etc.  Access by the public is not a typical condition 
of an "H" occupancy.  Also consider the normal firefighting approach for a 
propane fire is to keep the vessel and surrounding area cool but let it burn 
out.  That's not a good scenario within a building.

So before going any further, I'd recommend that you push back on this and 
require whoever dumped this in your lap to hire an architect or FPE to do an in 
depth code analysis and have a discussion with the local fire code authority to 
see if this is even permissible in this jurisdiction.

And, no this is nowhere near the same as a parking garage and EH2 would not be 
out of the question.  It may not even be adequate.  Do some Googling for Food 
truck fires.  They ain't pretty and a fire is the lesser of the problem.  
Explosions are a real possibility as well.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 
craig.pr...@jacobs.com | www.jacobs.com
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Mike Morey via Sprinklerforum
Sent: Thursday, January 13, 2022 10:16 AM
To: e...@bamfordfire.com; sprinklerforum@lists.firesprinkler.org
Cc: Mike Morey <mmo...@shambaugh.com>
Subject: [EXTERNAL] RE: Food trucks inside a building

If I, as a non-PE was sticking my neck out on this where it sort of doesn't 
belong, I'd have to go with EH-2: "Spaces where shielding of combustibles is 
extensive" being the key phrase to me.  Parking garage IMHO is intended for 
parking a car and leaving it, not using heat/fire producing equipment inside of 
it.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Manager * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 /  cell 
260.417.0625 /  fax 260.487.7991 email mmo...@shambaugh.com



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Ed Kramer via Sprinklerforum
Sent: Thursday, January 13, 2022 10:07 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Ed Kramer <e...@bamfordfire.com>
Subject: Food trucks inside a building


BE ADVISED - This email originated outside EMCOR.


I'm working on a small project  (approx. 7,200 sf) that is a noncombustible 
structure used for parking operating food trucks indoors.  The plan shows 6 
trucks spread out near the perimeter with the middle of the building open for 
pedestrian traffic (maybe tables?).



Ordinary Group I hazard (parking garage) seems very inadequate.  Extra hazard 
group II (manufactured home assemblies) seems a bit strong.



Thoughts?



Ed K





_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!L5iDA4qw94TTHadwZuct5Z9Abenek8n_pUDvsqDN3slVvGdRHyMSnnegmWstS_SP$

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!VtJkLj380Usp5dSGSvRp9DBdPBg3cvzxP5x_nwd0Xk-ACkEpJszECvlGvsHthnat1w$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.