It's always been my understanding that the different hazard classifications are 
based upon the fuel load of a potential fire, not the likelihood that there 
will be a fire. So whether there is a stove in operation or not shouldn’t 
really change the hazard.

So you come back to fuel load, which is present whether you are cooking in the 
truck or the truck is parked. So, are you allowed to park taco trucks in a 
parking garage? In order to call a parking garage Ordinary Hazard Group 1, do 
we need to have signage on the entrance that prohibits taco trucks from 
entering?

My biggest questions would be: 
1. Since they are likely parked long-term, do the have additional fuel or other 
combustible supplies that wouldn't be present in a vehicle moving from location 
to location?
2. Is there a buildup of grease that needs to be considered based on how the 
ventilation air is treated?

I don't think ordinary hazard would be out of the question. I think my first 
attempt would be to go OH 2, and make someone convince me that it needed to be 
more than that. 

Full disclosure, I don't have the necessarily letters after my name to act as a 
consultant, and I tend to be a little less conservative than our other brothers 
and sisters on this forum. 

-Kyle M

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Thursday, January 13, 2022 10:30 AM
To: sprinklerforum@lists.firesprinkler.org; Edk <e...@bamfordfire.com>
Cc: Prahl, Craig/GVL <craig.pr...@jacobs.com>; Fpdcdesign <fpdcdes...@gmail.com>
Subject: [EXTERNAL] RE: [EXTERNAL] Re: Food trucks inside a building

Shielded fires wouldn't be my primary concern, fuel density and fire intensity 
would be my concerns.  A little fire in a truck can be handled by a fire 
extinguisher. I'm not sure if food trucks are required to have anything other 
than that for fire control.  But a fire in one of these units is not going to 
be shielded for very long if it isn't brought under control almost immediately.


Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 
craig.pr...@jacobs.com | 
https://urldefense.com/v3/__http://www.jacobs.com__;!!Ba8_KKAT!ZrXP5SK6t5glR-DVUQLAZqoO-M8IgbnbLSNz1_g0q5s8iY5IgvuCyhGm_e3Ao6KYcFE$
 
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: email or MS TEAMS



-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Fpdcdesign via Sprinklerforum
Sent: Thursday, January 13, 2022 11:57 AM
To: Edk <e...@bamfordfire.com>; Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org>
Cc: Fpdcdesign <fpdcdes...@gmail.com>
Subject: [EXTERNAL] Re: Food trucks inside a building




  When I saw this, my knee-jerk reaction was EH2 for shielded fire. However, I 
was on a job site and had a 1:15 ride back to think about it.



Most automobiles are enclosed and any fire started inside would be “shielded”. 
But a parking garage has been OH1 for a long time (although that may be 
reassessed). Also, the examples in NFPA 13 of shielded occupancies are very 
large (Modular houses). Where is the cut off between what OH1 would protect and 
EH2 be necessary? Who knows? A pick up truck has a lot less shielded space that 
an SUV. It is most likely a function of the size of the shielded area but how 
do you regulate that?



Most food trucks are little more than delivery vans with kitchens and a side 
window. If 6 regular delivery vans were parked there, how would you protect it?



I would lean toward EH2 because of the combination of the shielded space and 
the kitchen inside.



To Ron’s point, there are a lot of other health and safety regulations 
(commercial kitchen without adequate ventilation, etc) that make this whole 
occupancy sketchy to begin with.



 Todd G Williams, PE
Fire Protection Design/Consulting

Stonington, CT

860-535-2080 (tel:860-535-2080)  (ofc)

860-554-7054 (tel:860-554-7054)     (fax)

860-608-4559 (tel:860-608-4559)  (cell)







>
> On Jan 13, 2022 at 10:08 AM,  <Ed Kramer via Sprinklerforum 
> (mailto:sprinklerforum@lists.firesprinkler.org)>  wrote:
>
>
>
>  I'm working on a small project (approx. 7,200 sf) that is a noncombustible 
> structure used for parking operating food trucks indoors. The plan shows 6 
> trucks spread out near the perimeter with the middle of the building open for 
> pedestrian traffic (maybe tables?). Ordinary Group I hazard (parking garage) 
> seems very inadequate. Extra hazard group II (manufactured home assemblies) 
> seems a bit strong. Thoughts? Ed K 
> _______________________________________________ Sprinklerforum mailing list  
> Sprinklerforum@lists.firesprinkler.org 
> (mailto:Sprinklerforum@lists.firesprinkler.org)   
> https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!RcX5JP4LeGO09FAr8CBattqY0kW-M8-52sufDsdeL1NcQ7PBWPXO05AHXjBEwkvHNg$
>
>



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!RcX5JP4LeGO09FAr8CBattqY0kW-M8-52sufDsdeL1NcQ7PBWPXO05AHXjBEwkvHNg$

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!Ba8_KKAT!ZrXP5SK6t5glR-DVUQLAZqoO-M8IgbnbLSNz1_g0q5s8iY5IgvuCyhGm_e3AEePNlfA$
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to