Sounds like they're asking for a vestibule or some sort of enclosure, but I'm 
not going to speculate.   Are you asking this in the context of fire sprinkler 
protection or general building code requirements?

Steve L.

From: Anthony Carrizosa <[email protected]>
Sent: Tuesday, July 26, 2022 8:57 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Do separate fire areas require sprinkler system 
to be separated

[cid:[email protected]]
Per the Architect: Their scope was to create a separation between QFC and the 
parking garage as they are both part of the same base building.  Separating the 
two areas into separate fire areas was reviewed and ultimately approved by City 
of Kirkland as the means to achieve this scope.
They have interpreted that if we separate the spaces into different fire areas, 
the fire alarm will need to be separated and are asking if the fire sprinkler 
system also needs to be separate.

Any ideas? I don't think the fire sprinkler system needs to be separated but 
they are asking me to confirm.

Thanks

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:[email protected]]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>



From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 26, 2022 8:42 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: Do separate fire areas require sprinkler system 
to be separated

The building code requires that high-rise sprinkler systems be controlled and 
the waterflow/tamper alarms be annunciated per floor, but not fire area on a 
given floor.   You are describing a situation that requires opening protection 
because of the floor-to-floor penetration, which in and of itself doesn't 
create a separate "fire area" but does communicate between different floors.   
If you end up placing a water curtain around the opening at the lower level, it 
should be supplied by the floor control assembly for that floor.   The market 
above is supplied by its floor control assembly.

Hope that I'm understanding your question,

Steve L.

From: Anthony Carrizosa 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, July 26, 2022 8:33 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Do separate fire areas require sprinkler system to be 
separated

We are working on a high rise building were the below grade parking has a 
grocery store above on the grade floor, an escalator/stairs provides access 
between the garage and the store and has a non-rated enclosure around it. The 
Architect is now saying that it needs to be rated and is asking if since there 
will now be two separate fire areas does the fire sprinkler system need to be 
separated along with the fire alarm system?

I cant find anything in the IBC that clearly states one system is acceptable or 
that two separate systems are required. Anyone have any thoughts on this?


Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222
[cid:[email protected]]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>



Anthony Carrizosa | Fire Protection Estimator / Project Manager
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office: 253-872-7222

[https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2fwp-content%2fuploads%2f2021%2f04%2farcher_logo.jpg&c=E,1,iOru29gH30krLbLDfm-Oz2HCyNeYqSXtrqUrkw_82eYd74Tatbn9Mk2KIexAq2Tfr9N77oRmZ4tB8GeX8wG8XFsOckz8m_WRDR27y2jCbXO1Nm-PHdjf&typo=1]
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,uOFpKnXoKAqtsbPiPnEzK69II4nW0DEqGmpOCB6ra0lazLcQJDB699ihE90BpKZsk-5CqI67z4Qt41O5eVR5sjrtKYEHmJFPpsUyv8GUYda3YO3g&typo=1>




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to