It seems like this is a question for State/Local Codes and any amendments or 
modifications. I don’t know of anything in NFPA that restricts this.   
  
  
  
  
  
  
  

  
  
>   
> On Jul 26, 2022 at 2:07 PM,  <Anthony Carrizosa 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
> Agreed, it’s mainly the Architect that wants to verify this. Because the 
> floor separating the garage and store protrudes into the vestibule and has 
> two sprinklers on a line from the garage system covering below this floor 
> area within the vestibule, they are looking for confirmation that it’s not 
> required to be separate.
>
>   
>
> Like you said earlier we do this within stairs when protecting the landings 
> or below the lowest landing, we feed these sprinklers from the floor at that 
> level.
>
>   
>
>   
>
>   
>
> Thanks again for your input.
>
>   
>
>   
>
>   
>
>  Anthony Carrizosa
>
>   
>
>  Project Manager  |  Fire Protection
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>
>
>   
>
>  https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Steve Leyton  <[email protected]>
>   Sent:  Tuesday, July 26, 2022 10:35 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> In situations where we’re directed to undertake a design element that I don’t 
> agree with, or informed that something is required or not allowed, I always 
> ask for the fire or building official to cite the section number they are 
> relying on.      The two floors are separate fire areas and the configuration 
> of a high-rise sprinkler system already addresses that.      And protection 
> of the opening in the fire separation – in this case the floor assembly – is 
> also spelled out in the code.      If they’re asking for more than opening 
> protection, they should be able to cite the code section that prescribes 
> whatever they’re looking for.    If they say you have to have a separate 
> sprinkler system on one or the other floor because of a fire separation, ask 
> them where they’re getting that as well.
>
>   
>
>   
>
>   
>
> Steve
>
>   
>
>   
>
>   
>   
>   
>
> From:   Anthony Carrizosa  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 10:28 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> Your opinion is much appreciated and falls in line with what I am thinking as 
> well. Just hoping to find some verbiage that could satisfy them.
>
>   
>
> I may bring out the NFPA requirement on system size limitation in    8.2 
> System Protection Area Limitations. and then 8.2.3 that each floor can have 
> multiple hazards protected by the same system as long as the limitations in 
> square footage of the highest hazard are not exceeded and or the total system 
> area does not exceed the maximum for the lighter hazard.
>
>   
>
>   
>
>   
>
> Thanks again for your input.
>
>   
>
>   
>
>   
>
>  Anthony Carrizosa
>
>   
>
>  Project Manager  |  Fire Protection
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>
>
>   
>
>  https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Steve Leyton  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 10:14 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> To my knowledge, it does not.      Look at a typical stair shaft – it’s 
> 2-hour and we sprinkler stair landings and arrange floor control assemblies 
> and pass in and out of that shaft on each floor in mid- and high-rise 
> buildings all the time.    I think you sprinkler the spaces at the lower 
> level from the lower level system and penetrate into any vestibule that you 
> may have to build at the bottom of your escalators.      The market above is 
> controlled by the sprinkler system on that floor above.   
>
>   
>
>   
>
>   
>
> I have to add the disclaimer that as a former member of the NFPA technical 
> committee on fire sprinklers, all of the information we’ve exchanged is my 
> opinion only.      And as a consultant who’s client roster is mostly 
> architects, this is something that the architect of record should assess and 
> specify.      The sprinkler design is subordinate to the building code 
> requirements, AS INTERPRETED by the building official.        So if somebody 
> up the food chain is saying it has to be a separate fire area, or just 
> separated by something more than opening projection, then the architect is 
> responsible for sorting that, and the sprinkler design can be done pursuant 
> to finalizing the configuration.        HOWEVER… openings are allowed in 
> floor assemblies with adequate protection, so it should also be investigated 
> whether or not a water curtain and requisite smoke barriers will be 
> acceptable to the building official.
>
>   
>
>   
>
>   
>
> Steve Leyton
>
>   
>
> Remember, MY OPINION ONLY.
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Anthony Carrizosa  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 10:03 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> Yes, Fire Sprinkler protection question. They are asking if the fire 
> sprinkler system also needs to be separate per Fire Area. I know it typically 
> does not have to be separate and our system can span across two different 
> fire areas, we just have to protect our penetrations.
>
>   
>
>   
>
>   
>
>   
>
>   
>
>  Anthony Carrizosa
>
>   
>
>  Project Manager  |  Fire Protection
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>
>
>   
>
>  https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Steve Leyton  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 9:46 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> Sounds like they’re asking for a vestibule or some sort of enclosure, but I’m 
> not going to speculate.      Are you asking this in the context of fire 
> sprinkler protection or general building code requirements?
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>   
>   
>
> From:   Anthony Carrizosa  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 8:57 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
>
>
>   
>
> Per the Architect: Their scope was to create a separation between QFC and the 
> parking garage as they are both part of the same base building.    Separating 
> the two areas into separate fire areas was reviewed and ultimately approved 
> by City of Kirkland as the means to achieve this scope.
>
>   
>
> They have interpreted that if we separate the spaces into different fire 
> areas, the fire alarm will need to be separated and are asking if the fire 
> sprinkler system also needs to be separate.
>
>   
>
>   
>
>   
>
> Any ideas? I don’t think the fire sprinkler system needs to be separated but 
> they are asking me to confirm.
>
>   
>
>   
>
>   
>
> Thanks
>
>   
>
>   
>
>   
>
>  Anthony Carrizosa
>
>   
>
>  Project Manager  |  Fire Protection
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>
>
>   
>
>   https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Steve Leyton  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 8:42 AM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  [Sprinklerforum] Re: Do separate fire areas require sprinkler 
> system to be separated
>
>   
>   
>   
>
>   
>
>   
>
> The building code requires that high-rise sprinkler systems be controlled and 
> the waterflow/tamper alarms be annunciated per floor, but not fire area on a 
> given floor.      You are describing a situation that requires opening 
> protection because of the floor-to-floor penetration, which in and of itself 
> doesn’t create a separate “fire area” but does communicate between different 
> floors.      If you end up placing a water curtain around the opening at the 
> lower level, it should be supplied by the floor control assembly for that 
> floor.      The market above is supplied by its floor control assembly.
>
>   
>
>   
>
>   
>
> Hope that I’m understanding your question,
>
>   
>
>   
>
>   
>
> Steve L.
>
>   
>
>   
>
>   
>   
>   
>
> From:   Anthony Carrizosa  <[email protected] 
> (mailto:[email protected])>
>   Sent:  Tuesday, July 26, 2022 8:33 AM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  [Sprinklerforum] Do separate fire areas require sprinkler system 
> to be separated
>
>   
>   
>   
>
>   
>
>   
>
> We are working on a high rise building were the below grade parking has a 
> grocery store above on the grade floor, an escalator/stairs provides access 
> between the garage and the store and has a non-rated enclosure around it. The 
> Architect is now saying that it needs to be rated and is asking if since 
> there will now be two separate fire areas does the fire sprinkler system need 
> to be separated along with the fire alarm system?
>
>   
>
>   
>
>   
>
> I cant find anything in the IBC that clearly states one system is acceptable 
> or that two separate systems are required. Anyone have any thoughts on this?
>
>   
>
>   
>
>   
>
>   
>
>   
>
> Anthony Carrizosa
>
>   
>
> Project Manager  |  Fire Protection
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>
>
>   
>
>  https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>  Anthony Carrizosa |    Fire Protection Estimator / Project Manager
>
>   
>
>  7855 S 206th  St Kent, WA 98032
>
>   
>
>  Cell:  206-679-5283  | Office:  253-872-7222
>
>   
>
>     
>
>   
>
>
>
>   
>
>   https://archerconstruction.com 
> (https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,uOFpKnXoKAqtsbPiPnEzK69II4nW0DEqGmpOCB6ra0lazLcQJDB699ihE90BpKZsk-5CqI67z4Qt41O5eVR5sjrtKYEHmJFPpsUyv8GUYda3YO3g&typo=1)
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to