What is the "roof" deck of the mezzanine constructed of?

On Tue, Aug 29, 2023 at 8:24 AM Joe Burtell [MT-BILL] <
[email protected]> wrote:

> I have a soda manufacturing warehouse with ESFR at the roof deck. They are
> building out some mezzanines in the middle of the warehouse that will have
> bottling equipment.  The engineer is requiring that below the mezzanine
> have ESFR per NFPA 13 2019 9.5.5.3.3. I am questioning if the mezzanine is
> really treated like an obstruction? I think it would be treated like
> in-racks would and have its own design based on what’s under the mezzanine.
>
>
> Joe​
>
> Burtell | SET, CFPS
> Fire Sprinkler Manager
> D
> C
>
>
> 406-204-4653
> 406-861-4507
> 3004 1st Ave South
> Billings
> ,
> MT
>  59101
> Office:
> 406‑652‑7697
> www.summitfiresecurity.com
> This information transmitted, including attachments, is intended only for
> the person(s) or entity to which it is addressed and may contain
> confidential and/or privileged material. Any review, retransmission,
> dissemination or other use of, or taking of any action in reliance upon
> this information by persons or entities other than the intended recipient
> is prohibited. If you received this in error, please contact the sender and
> destroy any copies of this information.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>


-- 
Shawn Foor, SET

*FOOR DESIGN, LLC*
*10208 E 98TH ST*
*TULSA, OK 74133*
*P:918-237-1400*
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to