A mezzanine or equipment platform as is common in industrial type settings as 
described is very much an obstruction to the discharge of overhead sprinklers 
and NFPA 13 is very clear on the type of sprinklers that should be used to 
protect the area below the obstruction.

If the area beyond the mezzanine requires an ESFR system to provide adequate 
protection, the obvious assumption is that the space below the mezzanine which 
is part of the open area would share the same hazard and therefore require the 
same criteria in order to provide adequate protection.  The only way it could 
be anything less is if the mezzanine had a solid floor and the space below was 
separated from the adjacent production space by walls where it became a 
separated room.  Simple example of that condition is a modular office out in 
the middle of the production floor where the office could be LH while the 
surrounding areas could require a higher degree of protection.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Brett Peters <[email protected]>
Sent: Tuesday, August 29, 2023 10:08 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: ESFR Below Mezzanine

Definition of a Mezzanine from National Building Code - Alberta

Mezzanine means an intermediate floor assembly between the floor and ceiling of 
any
room or storey and includes an interior balcony.

I'm sure whatever building code you're using in your area will have the same 
definition of a mezzanine.
So NOT an obstruction, it's a FLOOR ASSEMBLY, so you would protect the floor 
below the mezzanine according to whatever hazard is present below it.

Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at 
www.proudline.ca<https://urldefense.com/v3/__http:/www.proudline.ca/__;!!B5cixuoO7ltTeg!E_vD-9mkbPTyDRs6S9u0P1tosHuAssuBGbYq9zlQMIWEZm-JFT1dggnA4PGYXyZcCsAJVBjjyT-IeLgAmvY$>

Proudline now offers ULc listed monitoring services, please contact 
[email protected]<mailto:[email protected]> for more information



[https://ci3.googleusercontent.com/mail-sig/AIorK4wRo6r0eNDUWx8YR-4XJLvwcnouQn_xEZH_HIb4jDbepWtON2RWC-ekzvZHKtncFOQqPcNQfzM]
 
[https://ci3.googleusercontent.com/mail-sig/AIorK4yJVI287VPLDWiW9maE2Np3U4CdszCY9deeyaLl8DM90wlBd7pnuOZV9U-swv-7gWN_24py6vo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wlGmqj6Ja06DKOIMLPvEE8B2W8fT_TPPA3w-4JfqygLq9n77ECSni09YLIVICXJYzWo4Z0PjU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4zEgPbs279KVEfWIpIiWNLel8zAlcloW9dNXGLTaE1cMz88CRkmg17fju5BQB_iIzhWK20DUL8]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4z7J0kfmSGA8jKvDK0pTqW3KQlc5v-tYcWosmy5W7pdok462Gzu_9Ft7UK9oJUWDT1DzhQ4hUU]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4wTVHoTZxkppBoWSCTFnGLgGTq0apivi8sNvWPyBsloO0mmy8ZYu4Ax854jo7ihTMFyeYeOceg]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4xwBWEOX5v9mpza4Jqf9lOKSwThBNvyIO7Rl-Cxo7NRiV7p70C0f1biwbh44Y-iIA5GcmD1MCo]
  
[https://ci3.googleusercontent.com/mail-sig/AIorK4yPfO1HdtbQPYiKlYE38cwc88ABhX7xN1nh0fCK5LjFXjKplJggk3Xn6_XypmtMWyADKR7ZRGk]


On Tue, Aug 29, 2023 at 7:23 AM Joe Burtell [MT-BILL] 
<[email protected]<mailto:[email protected]>> wrote:
I have a soda manufacturing warehouse with ESFR at the roof deck. They are 
building out some mezzanines in the middle of the warehouse that will have 
bottling equipment.  The engineer is requiring that below the mezzanine have 
ESFR per NFPA 13 2019 9.5.5.3.3. I am questioning if the mezzanine is really 
treated like an obstruction? I think it would be treated like in-racks would 
and have its own design based on what’s under the mezzanine.

[cid:[email protected]]
Joe​

Burtell | SET, CFPS
Fire Sprinkler Manager
D
C


406-204-4653<tel:406-204-4653>
406-861-4507<tel:406-861-4507>
3004 1st Ave South
Billings
,
MT
 59101
Office:
406‑652‑7697
www.summitfiresecurity.com<https://urldefense.com/v3/__http:/www.summitfiresecurity.com__;!!B5cixuoO7ltTeg!E_vD-9mkbPTyDRs6S9u0P1tosHuAssuBGbYq9zlQMIWEZm-JFT1dggnA4PGYXyZcCsAJVBjjyT-IONoo5gQ$>
This information transmitted, including attachments, is intended only for the 
person(s) or entity to which it is addressed and may contain confidential 
and/or privileged material. Any review, retransmission, dissemination or other 
use of, or taking of any action in reliance upon this information by persons or 
entities other than the intended recipient is prohibited. If you received this 
in error, please contact the sender and destroy any copies of this information.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!E_vD-9mkbPTyDRs6S9u0P1tosHuAssuBGbYq9zlQMIWEZm-JFT1dggnA4PGYXyZcCsAJVBjjyT-IfmBjXXI$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to