For this, high temperature or 11.2K is allowed, not both. 

I’m currently on a plane but I will quote you the reference later today. 

Either or, not both. 

John

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

On Mar 18, 2024, at 15:03, Mike Morey <[email protected]> wrote:



I believe the intent was always that the K11.2 reduction was an alternative to high temp heads and not intended to allow both but it was never spelled out (other than that omission perhaps).  The revisions to the next edition are significant, but this item is consolidated into one that says you can take 25% reduction to no less than 2000 for one or the other.

 

Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP
an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email
[email protected]

<image001.png>

 

From: Micah Davis <[email protected]>
Sent: Monday, March 18, 2024 2:51 PM
To: SprinklerForum <[email protected]>
Subject: [Sprinklerforum] EH 11k & High Temp RA reduction

 

Hey everyone!  I need some help with the application of the remote area adjustment provisions in Chapter 19 (2019) of NFPA 13.  19.3.3.2.8 addresses multiple adjustments but, interestingly, omits 19.3.3.2.7 in the list.  Should I interpret

ZjQcmQRYFpfptBannerStart

This Message Is From an Untrusted Sender

You have not previously corresponded with this sender.

ZjQcmQRYFpfptBannerEnd

Hey everyone!  I need some help with the application of the remote area adjustment provisions in Chapter 19 (2019) of NFPA 13.  19.3.3.2.8 addresses multiple adjustments but, interestingly, omits 19.3.3.2.7 in the list.  Should I interpret this to mean that no other adjustments for EH design areas can be applied if the 11.2k or larger reduction is used?

 

Thank you,

Micah Davis

Ferguson Fire Design

931-242-1299

This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to