For the 2025 edition of NFPA 13, the proposed language is below:

Second Revision number 1084

*19.2.3.2.7 *Extra Hazard Occupancies.
*19.2.3.2.7.1 *
For extra hazard occupancies with ceilings not exceeding 30 ft (9.1 m) in
height, the system area of sprinkler operation shall be permitted to be
reduced by 25 percent without revising the density, but not to less than
2000 ft2 (185 m2). where one of the following conditions occurs:
(1)  High-temperature sprinklers are used.
(2)  K-11.2 (160) or larger sprinklers are used.
*19.2.3.2.7.2*
The 25 percent reduction permitted by 19.2.3.2.7.1 shall only be permitted
to applied once.

*This language is pretty clear to me.  *

*The technical committee statement for this second revision is telling:*
The current structure for the 25% reduction is unclear that the reduction
can only be taken once with either high-temperature sprinklers or large
orifice sprinklers. This revision makes the intent of the section clearer
and will clarify the application of the requirements for multiple
adjustments. Based on the fire testing data available at this time, the
ceiling heights have been limited to 30 feet in height for taking the
reduction.


*While this language looks like it will make it into the 2025 edition of
NFPA 13, it still is subject to change until the Standards Council approves
the release of this document around September 2024.*


*The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the **AFSA, and/or NFPA or its
technical committees.**AFSA cannot provide design or consulting engineering
services, and this opinion should therefore not be considered, nor relied
upon, as such.*


Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org



*Treat Your Apprentices Like VIPs!*
AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that
comes straight from our expert instructors. They lead the way to ensure
your men and women are trained, letting you focus on OJT. Click here
<https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn
more and enroll.

On Mon, Mar 18, 2024 at 3:16 PM John Denhardt <[email protected]>
wrote:

> For this, high temperature or 11.2K is allowed, not both.
>
> I’m currently on a plane but I will quote you the reference later today.
>
> Either or, not both.
>
> John
>
> John August Denhardt, P.E.
> Vice-President Engineering and Technical Services
> American Fire Sprinkler Association
> 301-343-1457
>
> On Mar 18, 2024, at 15:03, Mike Morey <[email protected]> wrote:
>
> 
>
> I believe the intent was always that the K11.2 reduction was an
> alternative to high temp heads and not intended to allow both but it was
> never spelled out (other than that omission perhaps).  The revisions to the
> next edition are significant, but this item is consolidated into one that
> says you can take 25% reduction to no less than 2000 for one or the other.
>
>
>
> *Mike Morey*
>
> *CFPS 3229 • NICET S.E.T. 123677*
>
> *Project Manager* • Fire Protection Group
> * Shambaugh & Son, LP **an EMCOR Company*
>
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
>
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> * email *[email protected]
> <image001.png>
>
>
>
> *From:* Micah Davis <[email protected]>
> *Sent:* Monday, March 18, 2024 2:51 PM
> *To:* SprinklerForum <[email protected]>
> *Subject:* [Sprinklerforum] EH 11k & High Temp RA reduction
>
>
>
> Hey everyone!  I need some help with the application of the remote area
> adjustment provisions in Chapter 19 (2019) of NFPA 13.   19. 3. 3. 2. 8
> addresses multiple adjustments but, interestingly, omits 19. 3. 3. 2. 7
> in the list.   Should I interpret
>
> ZjQcmQRYFpfptBannerStart
>
> *This Message Is From an Untrusted Sender *
>
> You have not previously corresponded with this sender.
>
> ZjQcmQRYFpfptBannerEnd
>
> Hey everyone!  I need some help with the application of the remote area
> adjustment provisions in Chapter 19 (2019) of NFPA 13.  19.3.3.2.8
> addresses multiple adjustments but, interestingly, omits 19.3.3.2.7 in the
> list.  Should I interpret this to mean that no other adjustments for EH
> design areas can be applied if the 11.2k or larger reduction is used?
>
>
>
> Thank you,
>
> Micah Davis
>
> Ferguson Fire Design
>
> 931-242-1299
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]