Great point, Bob.  It is my intent to recommend the reductions not be
combined.  I felt that was correct initially, but the wording of the
section in the standard was proving to be troublesome.

Thank you,
Micah Davis
(931) 242-1299


On Tue, Mar 19, 2024 at 8:29 AM <[email protected]> wrote:

> Micah,
>
>
>
> I understand your project will be reviewed based on the language in the
> 2029 edition of NFPA 13. However, section 1.5 Equivalency allows you to use
> alternate arrangements with technical documentation submitted to the AHJ.
> What better way to show the level of safety is not being lowered, than to
> share the language from the next edition of the standard?
>
>
>
> Yes, the letter of the law is important, but so is the intent.  We know
> what we know when we know it and the arrangement of sprinklers or allowable
> modifiers in design applications that will exist in the next edition
> provide clarity and more so, in this case, a literal interpretation of this
> section, from the entire balloted committee.
>
>
>
> I would encourage you to adopt Mr. Denhardt’s advice and share it with
> your AHJ.
>
>
>
> This is (of course) just my personal opinion and not intended to sound
> condescending in any way
>
>
>
> Best regards,
>
>
>
> Bob
>
>
>
>
>
>
>
> *Bob Caputo, CFPS*
>
> *President*
>
> *American Fire Sprinkler Association*
>
> c:     760-908-7753
>
> p:
>
> 214-349-5965 ext124
>
> w:
>
> firesprinkler.org
>
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
>
>
> *Treat Your Apprentices Like VIPs!*
>
> AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that
> comes straight from our expert instructors. They lead the way to ensure
> your men and women are trained, letting you focus on OJT. Click here
> <https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn
> more and enroll
>
>
>
> *From:* Micah Davis <[email protected]>
> *Sent:* Tuesday, March 19, 2024 7:09 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: EH 11k & High Temp RA reduction
>
>
>
> Thank you, John.  That is MUCH clearer.  Unfortunately, the project in
> question is under the 2019 edition which leaves us with the uncertain
> language.  Your feedback helps me with my next steps, though.
>
>
>
> Thank you,
> Micah Davis
> (931) 242-1299
>
>
>
>
>
> On Tue, Mar 19, 2024 at 12:40 AM John Denhardt <
> [email protected]> wrote:
>
> For the 2025 edition of NFPA 13, the proposed language is below:
>
>
>
> Second Revision number 1084
>
>
>
> *19.2.3.2.7 *Extra Hazard Occupancies.
> *19.2.3.2.7.1 *
> For extra hazard occupancies with ceilings not exceeding 30 ft (9.1 m) in
> height, the system area of sprinkler operation shall be permitted to be
> reduced by 25 percent without revising the density, but not to less than
> 2000 ft2 (185 m2). where one of the following conditions occurs:
> (1)  High-temperature sprinklers are used.
> (2)  K-11.2 (160) or larger sprinklers are used.
>
> *19.2.3.2.7.2*
>
> The 25 percent reduction permitted by 19.2.3.2.7.1 shall only be permitted
> to applied once.
>
>
>
> *This language is pretty clear to me.  *
>
>
>
> *The technical committee statement for this second revision is telling:*
>
> The current structure for the 25% reduction is unclear that the reduction
> can only be taken once with either high-temperature sprinklers or large
> orifice sprinklers. This revision makes the intent of the section clearer
> and will clarify the application of the requirements for multiple
> adjustments. Based on the fire testing data available at this time, the
> ceiling heights have been limited to 30 feet in height for taking the
> reduction.
>
>
>
>
>
> *While this language looks like it will make it into the 2025 edition of
> NFPA 13, it still is subject to change until the Standards Council approves
> the release of this document around September 2024.*
>
>
>
>
> *The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the **AFSA, and/or NFPA or its
> technical committees.**AFSA cannot provide design or consulting
> engineering services, and this opinion should therefore not be considered,
> nor relied upon, as such.*
>
>
>
> Thanks,
>
> John
>
>
>
> [image: Image removed by sender.]
>
> John August Denhardt, PE
>
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
>
> m: p:
>
> 301-343-1457
> 214-349-5965 ext 121
>
> w:
>
> firesprinkler.org
>
>
>
>
>
> *Treat Your Apprentices Like VIPs!*
>
> AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that
> comes straight from our expert instructors. They lead the way to ensure
> your men and women are trained, letting you focus on OJT. Click here
> <https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn
> more and enroll.
>
>
>
> On Mon, Mar 18, 2024 at 3:16 PM John Denhardt <[email protected]>
> wrote:
>
> For this, high temperature or 11.2K is allowed, not both.
>
>
>
> I’m currently on a plane but I will quote you the reference later today.
>
>
>
> Either or, not both.
>
>
>
> John
>
> John August Denhardt, P.E.
>
> Vice-President Engineering and Technical Services
>
> American Fire Sprinkler Association
>
> 301-343-1457
>
>
>
> On Mar 18, 2024, at 15:03, Mike Morey <[email protected]> wrote:
>
> 
>
> I believe the intent was always that the K11.2 reduction was an
> alternative to high temp heads and not intended to allow both but it was
> never spelled out (other than that omission perhaps).  The revisions to the
> next edition are significant, but this item is consolidated into one that
> says you can take 25% reduction to no less than 2000 for one or the other.
>
>
>
> *Mike Morey*
>
> *CFPS 3229 • NICET S.E.T. 123677*
>
> *Project Manager* • Fire Protection Group
> *Shambaugh & Son, LP **an EMCOR Company*
>
> 7614 Opportunity Drive • Fort Wayne, IN • 46825
>
> *direct *260.487.7824* /  cell *260.417.0625* /  fax *260.487.7991
> *email *[email protected]
>
> <image001.png>
>
>
>
> *From:* Micah Davis <[email protected]>
> *Sent:* Monday, March 18, 2024 2:51 PM
> *To:* SprinklerForum <[email protected]>
> *Subject:* [Sprinklerforum] EH 11k & High Temp RA reduction
>
>
>
> Hey everyone!  I need some help with the application of the remote area
> adjustment provisions in Chapter 19 (2019) of NFPA 13.   19. 3. 3. 2. 8
> addresses multiple adjustments but, interestingly, omits 19. 3. 3. 2. 7
> in the list.   Should I interpret
>
> ZjQcmQRYFpfptBannerStart
>
> *This Message Is From an Untrusted Sender *
>
> You have not previously corresponded with this sender.
>
> ZjQcmQRYFpfptBannerEnd
>
> Hey everyone!  I need some help with the application of the remote area
> adjustment provisions in Chapter 19 (2019) of NFPA 13.  19.3.3.2.8
> addresses multiple adjustments but, interestingly, omits 19.3.3.2.7 in the
> list.  Should I interpret this to mean that no other adjustments for EH
> design areas can be applied if the 11.2k or larger reduction is used?
>
>
>
> Thank you,
>
> Micah Davis
>
> Ferguson Fire Design
>
> 931-242-1299
>
> This message is for the named person's use only. It may contain
> confidential, proprietary or legally privileged information. No
> confidentiality or privilege is waived or lost by any mistransmission. If
> you receive this message in error, please immediately delete it and all
> copies of it from your system, destroy any hard copies of it and notify the
> sender. You must not, directly or indirectly, use, disclose, distribute,
> print, or copy any part of this message if you are not the intended
> recipient.
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>