Calc them as one calc. Sprinkcad has a designator for in racks. It's the easiest way to balance the two systems
Benjamin Young On Mon, Sep 22, 2025 at 10:11 PM Lawrence Dirks <[email protected]> wrote: > Dear Sprinkler Forum Representative, > > > > The question I have today is pertaining to “balancing” in-rack sprinkler > output with that of the ceiling output in a high-risk commodity > application. I am using SprinkCAD within AutoCAD for this project, and I > believe that the only way for me to run the calculation is with two > separate calcs; however, I understand that the fire scenario would be such > that the in-racks would need to operate simultaneously with the ceiling > sprinklers. I assume that to represent this within calcs, I would need to > modify the input criteria for the two separate calcs such that the outputs > are adjusted as representative of simultaneous discharge. Towards this end, > what strategy should one use for generating this balance across the two > separate design areas? > > > > I look forward to your reply. > > > > Kindly, > > Lawrence > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected]