Another way is to calc both separately, but make sure you have a node that acts 
as the connection point between the two systems (easiest way is to include the 
base of system riser node for each system in each calc). You can create a 
k-factor for each system at this node ( k = Q / sqrt(p), although the calc 
program may already show you the k-factor at each node). Open the calc of the 
more demanding system (higher pressure required), input the k-factor of the 
other system at the balance point and run it. The more demanding system will 
cause the less demanding system to overflow (Q is higher than when you 
calculate the system on its own), but that’s OK as long as it still works with 
the flow and pressure you have available. If not, make modifications to the 
more demanding system to decrease the pressure required at the balance point, 
thus decreasing the overflow.

It’s definitely simpler (less thinking required and less iterations) if you can 
do it all in one calc. But that sometimes creates a calc that looks very 
complicated (lots of nodes).

-Kyle M at Aero

From: Ben Young <[email protected]>
Sent: Tuesday, September 23, 2025 3:33 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [External][Sprinklerforum] Re: Calculating in-rack sprinklers along 
with ceiling sprinklers

Calc them as one calc. Sprinkcad has a designator for in racks. It's the 
easiest way to balance the two systems


Benjamin Young


On Mon, Sep 22, 2025 at 10:11 PM Lawrence Dirks 
<[email protected]<mailto:[email protected]>> wrote:
Dear Sprinkler Forum Representative,

The question I have today is pertaining to “balancing” in-rack sprinkler output 
with that of the ceiling output in a high-risk commodity application. I am 
using SprinkCAD within AutoCAD for this project, and I believe that the only 
way for me to run the calculation is with two separate calcs; however, I 
understand that the fire scenario would be such that the in-racks would need to 
operate simultaneously with the ceiling sprinklers. I assume that to represent 
this within calcs, I would need to modify the input criteria for the two 
separate calcs such that the outputs are adjusted as representative of 
simultaneous discharge. Towards this end, what strategy should one use for 
generating this balance across the two separate design areas?

I look forward to your reply.

Kindly,
Lawrence

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to