Remember, Standards (and Codes) are minimums, not absolutes. A hazard can be 
upgraded if warranted. Home Depot is not protected as Retail.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Oct 8, 2025 at 3:17 PM,  <Parsley Consulting (mailto:[email protected])>  
> wrote:
>   
>   
>   Having a bit of confusion.
>   
>  A project is to follow the 2022 edition of NFPA 13.
>   
>  The apparatus bays of a fire station have been designated on the plan as 
> ordinary hazard, group 1.    When I look at the examples in §A.4.3.3.2, it 
> seems to me that those spaces would be similar to (2) "automobile parking 
> garages", or (14) "machine shops", or (24) "repair garages."    This would 
> make the space similar to ordinary hazard group 2, which increases the 
> required density from 0.15 gpm/ft² to 0.20 gpm/ft².
>   
>  Am I looking this incorrectly?    Any help greatly appreciated.
>   
>  sincerely,   
> --
>   Ken Wagoner, SET
>   Parsley Consulting
>  3002 Younger Drive
>  Harrisonville, Missouri 64701-3909
>   Phone: (760) 745-6181
>    Visit the website 
> (https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1)
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to