A project is to follow the 2022 edition of NFPA 13.
The apparatus bays of a fire station have been designated on the plan as ordinary hazard, group 1. When I look at the examples in §A.4.3.3.2, it seems to me that those spaces would be similar to (2) "automobile parking garages", or (14) "machine shops", or (24) "repair garages." This would make the space similar to ordinary hazard group 2, which increases the required density from 0.15 gpm/ft² to 0.20 gpm/ft².
Am I looking this incorrectly? Any help greatly appreciated.