My take as well, and we're looking at the same criteria.

SL
________________________________
From: Brett Peters <[email protected]>
Sent: Tuesday, December 9, 2025 10:56 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: CMSA or ESFR solutions for Combustible Liquids

I just went through this on a project, we had to install a 2000gpm pump with 
11k SSU (.60/3000) at the ceilings and in rack sprinklers, we were not able to 
find any other solutions for the combustible liquids.





Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at 
www.proudline.ca<https://url.avanan.click/v2/r01/___http://www.proudline.ca/___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo4OWE1MTMwMTc5YWYyYjIzMmY4ZjdkZjNjZTMzN2ZlNTo3OjAwZWM6ZTI5ZDAwYjJlMDhlMzYxYTE2NzVkMjdhNDcwYmM4MTZhMzUxYWE1MzI0NmM4OGY3ZDMyZTYwYTdkMjk1ZGExNjpoOlQ6Rg>


On Tue, Dec 9, 2025 at 11:52 AM Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:
I admit I'm getting either lazy or old (or one being a function of the other), 
but I used to love tracking down minutiae and not I just want instant 
gratification.

We have a storage application, IBC's of 3A combustible liquid (mineral oil) 
both in stacks and racks.   I've not found any CMSA or ESFR solutions but 
someone in the trade told me they were pretty sure that there was at least one 
or two sprinklers that could be used.   Does anyone know if there are or not?   
Right now we're sitting on .60/3000 with in-racks...

Thanks and happy holidays y'all,



 [cid:ii_19b047689b4f633ef5a1]
Steve Leyton, President

T  |  619.255.8964 x 102  |  
www.protectiondesign.com<https://url.avanan.click/v2/r01/___https:/urldefense.com/v3/__http:/www.protectiondesign.com/__;!!OBed2aHXvKmHymw!xUP_44imxZbNarYK4A-T5bTTThDYa0yfWnYjTflMMWnrGIjCKgkSfp93-VfkONuBdgFUqckgAlRqJYwt2l_VlQhycZynMg$___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzoyZGRjZTc0MjZlMzNjZjAwM2ViYjYwNDAzYzk5ZTY4NTo3Ojc3MTk6OGI3ZjI3ZGQwNWRjZjlkYzljNzU3OTViNGFmZGI3NDlkMmYyZWExYWEwMmU5NjQwMjg3ZTg4NTBmYzY5ZGNmYTpoOlQ6Rg>

2851 Camino Del Rio South  |  Suite 210 |  San Diego, CA  92108

Fire Protection System Design | Consulting | Planning | Training


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://url.avanan.click/v2/r01/___https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzo4OWE1MTMwMTc5YWYyYjIzMmY4ZjdkZjNjZTMzN2ZlNTo3OmFlNGY6ZWFkZmZmMWM2YTg2OWY0ZjM1YWQwYmFiYzA4MjNkZjhlYzkzNWY3MzcwNzdiMDQ5NGIyYTg3YjQyODIzMjhmNjpoOlQ6Rg>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to