Look at the Victaulic V4804   25.2K.....Read page 2 of the datasheet.  Same   
.6/3000






On Tuesday, December 9, 2025 at 02:38:49 PM EST, Steve Leyton 
<[email protected]> wrote: 







My take as well, and we're looking at the same criteria.


SL


________________________________ 
From: Brett Peters <[email protected]>
Sent: Tuesday, December 9, 2025 10:56 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: CMSA or ESFR solutions for Combustible Liquids 
 




I just went through this on a project, we had to install a 2000gpm pump with 
11k SSU (.60/3000) at the ceilings and in rack sprinklers, we were not able to 
find any other solutions for the combustible liquids.













































Thanks




Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

[email protected]

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca


































On Tue, Dec 9, 2025 at 11:52 AM Steve Leyton <[email protected]> wrote:


>  
>  
>  
>  I admit I'm getting either lazy or old (or one being a function of the 
>other), but I used to love tracking down minutiae and not I just want instant 
>gratification.  
> 
>  
> 
> 
>  We have a storage application, IBC's of 3A combustible liquid (mineral oil) 
>both in stacks and racks.   I've not found any CMSA or ESFR solutions but 
>someone in the trade told me they were pretty sure that there was at least one 
>or two sprinklers that could be used.   Does anyone know if there are or not?  
> Right now we're sitting on .60/3000 with in-racks...
> 
>  
> 
> 
>  Thanks and happy holidays y'all, 
> 
>  
> 
> 
>  
> 
> 
>  
>  
> Steve Leyton, President
> 
> T  |  619.255.8964 x 102  |  www.protectiondesign.com
> 
> 2851 Camino Del Rio South  |  Suite 210 |  San Diego, CA  92108
> 
> Fire Protection System Design | Consulting | Planning | Training
> 
>  
> 
> 
> 
> 
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to  [email protected]
> 




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to