2022 edition of 13:  We're calculating four sprinklers in a 1 BR dwelling unit 
that has a sprinklered clothes closet with two sliding doors and a footprint 
area of about 25 sq. ft.    We've never included a sprinkler in such a small 
compartment in any calc area, whether it's a residential calculation of 4 or 8 
sprinklers, or applying the Room Design or Residential Sprinkler methods.   
We've got a comment from a plan reviewer to include one, based on the 
requirement in ?19.3.1.1, "The design area shall be the area that includes the 
four adjacent sprinklers that produce the greatest hydraulic demand."   Per 
?28.2.4.2.7.2, we can omit these sprinklers from calcs so long as the design 
area is equal to or greater than the areas specified in Table 28.2.4.7.2, which 
is for area/density calculations only.

Does anyone currently or previously on 13 have an opinion on whether the 
exception is intended to apply to the residential sprinkler calculation method 
as well?    The annex is mute, which seems to suggest that it may only be 
applicable to area/density designs.


 [cid:[email protected]]
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<https://url.avanan.click/v2/r01/___https:/urldefense.com/v3/__http:/www.protectiondesign.com/__;!!OBed2aHXvKmHymw!xUP_44imxZbNarYK4A-T5bTTThDYa0yfWnYjTflMMWnrGIjCKgkSfp93-VfkONuBdgFUqckgAlRqJYwt2l_VlQhycZynMg$___.YXAzOnByb3RlY3Rpb25kZXNpZ25hbmRjb25zdWx0aW5nOmE6bzoyZGRjZTc0MjZlMzNjZjAwM2ViYjYwNDAzYzk5ZTY4NTo3Ojc3MTk6OGI3ZjI3ZGQwNWRjZjlkYzljNzU3OTViNGFmZGI3NDlkMmYyZWExYWEwMmU5NjQwMjg3ZTg4NTBmYzY5ZGNmYTpoOlQ6Rg>
2851 Camino Del Rio South  |  Suite 210 |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to