Small Hose Requirement
"I have a warehouse building with 19 foot storage and determining if small hose 
connections are required.  Section 12.2.2 says that they are not required for 
storage
12 ft and less, does that mean they are required for storage above 12 ft. 
Section
8.17.5.1.1.1 states they are not required if the building is protected 
throughout
by an approved automatic sprinkler system."

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that NFPA 13 does not require small hose stations.

Section 12.2.1 states, "Small hose connections (1-1/2 in.) shall be provided 
where
required by the authority having jurisdiction in accordance with 8.17.5 for 
first-aid
fire-fighting and overhaul operations." Thus this is a decision of the authority
 having jurisdiction. The annex material in Section 12.2 indicates that 
authorities
having jurisdiction have varying requirements for plant first-aid and 
firefighting
operations.  Examples include no hose stations, hose stations with hose line and
 nozzles, and hose stations with no hose line or nozzles. Section 12.2.2 
clarifies
that Small hose connections shall not be required for the protection of Class I,
 II, III, and IV commodities stored 12 ft or less in height. Section 8.17.5 
indicates
where the hose stations are to be located and connected to water supplies. Note 
that these sections start with "where required" and Section 8.17.5.1.1.1 
clarifies
for the AHJ that they can omit the small hose stations.  Note the new 
information
in 8.17.5.1.1.3 that the location of valves shall be permitted to exceed the 
distances
specified in 8.17.5.1.1.1 where approved by the authority having jurisdiction.

The handbook commentary indicates that stations are not required for all storage
 occupancies.  Many building owners are concerned that if hose stations are 
located
in their warehouse, they will be required to provide fire-fighting equipment and
 training to their employees.  Rather than providing this special training and 
equipment,
most building owners want their employees to evacuate the building if a fire 
occurs
and allow the sprinkler system to deal with the fire.  If the building has some 
specific hazard, or if the fire-fighting plan for the building includes using 
hose
connections inside the building, the authority having jurisdiction has the right
 under this section to require that hose connections be provided.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5vkr7beHIURVzWWejZcqv7NNFG8DXJW7ZVKq3d0lGBd34cNtDvmaYyI4ei9uI14UbZA_G7JRLtBquUve6M0Zg0s4zA6SdwZOEyryyjJ_Oy_A==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p4Frtui0kZq0vW5EuHWYRe6FjN6q9yvaOfM95Q7xk9LK8B5D1HHgCpw5sONfR0nz1P2QaaK4mW7Ddg2pB_G98jQDXX8iEE0NkqDZfTXFrmM4Y0xHxbdfmSYb6Sjcr7-Ieb5tChKKaxzfHhuwjcT7jSHjoX0Tq5-7zk3dLJWI2GTd9oJgkW1jMAWiyIjcFZMHG0=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
May 13 - May 24, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6IhkMFn012vk6F-tTkz1yRt2k9i5vaDctRj2YIYSwR0sSwqBmaE4yOi12FDC4f_RzJpZVigwJhZuHA_PfM_-GkDZmZ6sr-d2FhDfogQE9LUGaoOVrfHoI5kRvoS9gQgFIr1dbMPjAHsvNP83k7Q6aQYHfrVUCt2o4lwG0pMn1obXZL9n813OrGYxIWNEvvC6hzxyh2XqBTw_AyTzsPoxVcHK5maY_1MEUN7QPPnGnRSFnm4agXEmzhtlWyFRSAd5kaHM8o_d4fyDHv3QfQ3gQw].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5NpwGEcf3J9gyPO5_de4L5HVwmwZo0U1qHcSzGcRWEdAy6OOykCkVt3Du_6xCFaP1d5NhbixE8cCgKfY_yXXnXBy-hJGxk4banXPh1-wu5RyTg-qn72n5G]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Webinar
Bob Caputo
to Present an
AFSA Webinar on
"Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13
Part I - Installation Requirements"
Wed., March 13, 2013
Free to AFSA members!
Register Button 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p4fmirGn6YiNbhamInNVRKPQH__aU6J_HakNESS_eGGGyKP85ROivNwA06_2rfXfOyXAIyW35her9aT1G5RV4qZpxd-9jJeTpkpiGFnKlLUBUikVNhN4r3njshZ3YqyMM-fNUTUNAcS0deCYlYBHl7X]
For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6IhkMFn012vk6F-tTkz1yRt2k9i5vaDctRj2YIYSwR0sSwqBmaE4yOi12FDC4f_RzJpZVigwJhZuHA_PfM_-GkDZmZ6sr-d2FhDfogQE9LUGaoOVrfHoI5kRvoS9gQgFIr1dbMPjAHsvNP83k7Q6aQYHfrVUCt2o4lwG0pMn1obXZL9n813OrGYxIWNEvvC6hzxyh2XqBTw_AyTzsPoxVcHK5maY_1MEUN7QPPnGnRSFnm4agXEmzhtlWyFRSAd5kaHM8o_d4fyDHv3QfQ3gQw].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p71113ajOnd1E02vzHBj3L1EPwVNchxarLfx1ZRXPVcQwCBBLG8matBIQcn6cl1UYVviTwBI9Cry1mq9UZrd2VePAx5HwRB8tEu07mpJvCTeLgBCy6J0GfoCxUv7mGyhlE-2UVDkmts1uJyRqqEuHIn1Chu7GmSAcQ=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p7cA2W7QvVEdrK7wWw0nBu3uav6k4zKHq5eok72P7nEWKYph7a5zeYWOnxsvxz2UFypq8aIaW_yolrg41Il4AMdJIjA6mwQnYZZgwbiqfgbxe4kt5XhgvWuqkjIX7iqk_UtbfPLOh-Jc0NSckDKjqdmnFlZcqH5DwA=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5vkr7beHIURVzWWejZcqv7NNFG8DXJW7ZVKq3d0lGBd34cNtDvmaYyI4ei9uI14UbZA_G7JRLtBquUve6M0Zg0s4zA6SdwZOEyryyjJ_Oy_A==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6IhkMFn012vk6F-tTkz1yRt2k9i5vaDctRj2YIYSwR0sSwqBmaE4yOi12FDC4f_RzJpZVigwJhZuHA_PfM_-GkDZmZ6sr-d2FhDfogQE9LUGaoOVrfHoI5kRvoS9gQgFIr1dbMPjAHsvNP83k7Q6aQYHfrVUCt2o4lwG0pMn1obXZL9n813OrGYxIWNEvvC6hzxyh2XqBTw_AyTzsPoxVcHK5maY_1MEUN7QPPnGnRSFnm4agXEmzhtlWyFRSAd5kaHM8o_d4fyDHv3QfQ3gQw]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5Pi3ruocW-aLwHt8NszHXmmpT45cmBq2kmnBRtjw4VtdGNFLlBrWvNtoYO5GQWz5MTMfu7iObGGkGGPxSTqcIRUO7SAXqizigg62qPpKagPiZ1GYu0yeRSqnikEEKAeMXNrbDUQVmDoQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6PMRIU1D9fsjZFpyDmWOh9Sv70_LzJteEB-2dCSYmelmPtYMhGtBa_Yigs3tzQWOvRsmbZUzkf2FisTZKfyvDDq-PuVF1_o9R_7jKp4tIj4uV1hI4HbTaqAJvztHMoZc29jUo17rqpc7t-UTM4RQdH]
National  
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5KxKQrt820XYGNZItxjJejSRbHfNnvV1mte8Pet-U0e0c1JXSRD2igkbC1_PLqu1zNBs997OecYuUXS1S3-kCeL-0tJg__F_Wlj46woqhgqQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p5KxKQrt820XYGNZItxjJejSRbHfNnvV1mte8Pet-U0e0c1JXSRD2igkbC1_PLqu1zNBs997OecYuUXS1S3-kCeL-0tJg__F_Wlj46woqhgqQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6qlWlKfA3y4ng-4aeY-RJkM57sLMr9X-68QCPfs_cA_qW-0TgERgy26UokKCD4oRX6Z2vYx4vBZ8wCIk1t30BeJvkyNaDLmYv5hfwNjeTd36JoTF9MxCJTHhpzo2kU3tEsVZ3Xl0GBKpTF4Ma4U8Xo]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p6Vefz2rtosKAhQf--gppSXlbBvUKBX1OLe0rv-lz2NXB2CmJ0xpgy5vqcPziZ7QnpOQTaNfZMcTBuR6bMLlBG8FGsx4DosuyuCFclPm3TJjtrXdNccc2eQUNQF4Z1q-ZE=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001W3LMBBLE6p558dW7o1a0ll_uIayYVN5aGhiGV_xLQ6IUD6gP-imob15ii7-1VvKTLHOy4pJvlcBJ6DUZgby293DkHgVECUw4W94guX_KYEvavFUQng2u81O7LO-JGzBcVVheGY52cjfVw3OVvTY6Ix5Q_xfU5WWronlIqAb_gMc=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1112553247335


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001EkoQgDcdwbYa-qAcmlkyvQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001EkoQgDcdwbYa-qAcmlkyvQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to