American Fire Sprinkler Association [http://www.firesprinkler.org/] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
AFSA Technical Update ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ A newsletter dealing with codes and other technical issues April 10, 2013 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Two Systems Connected at Remote Cross Main "A location appears to have two systems interconnected at a distant location from the risers likely to improve hydraulic conditions. When service is to be performed, both risers need to be shut down. Is there any code that indicates that systems cannot be tied together?" We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal interpretation is that a system can have multiple water supplies. A diagram was provided that shows two 19,000 sq. ft. gridded sprinkler systems in a building. Each system has a separate riser with a butterfly valve and flow switch. The two remote cross mains were tied together. The NFPA 13 standard does not prohibit this arrangement. Section 6.7.4.3.1 says that systems that have more than one control valve that must be closed to work on a system or space shall have a sign referring to existence and location of other valves. The annex material in A.6.7.4.3.1 further clarifies that care should be taken to ensure that all water supplies are isolated before work begins. Work on systems by shutting one valve and not knowing about another valve could result in unexpected water discharge. Thus the standard acknowledges that more than one water supply can be provided to a system. Next is Section 8.16.1.1.3.1 where there is more than one source of water supply, a check valve shall be installed in each connection. The diagram provided does not show check valves. Lastly, the two systems together do not exceed the system area limitations of 52,000 sq. ft. in Section 8.2.1 so there is no controversy over area limitations. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBkTVYWGGE7nkc8MDepB3ZlZtPTlOtY1I4R9t-elFBjOAjIfsxHXUkSaBBYJnyKH1oYaV69NY63r3EVjsUdCW84vVFx_dDRpBYcTZU1H9cBpg==] Hosted by the American Fire Sprinkler Association ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered in fire protection engineering. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright 2012, American Fire Sprinkler Association. All Rights Reserved ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ PDF Version PDF Link [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBQckm_Yttwn8NKMlPznk0NkuUB3zC3aVVDvHHfoziIIE1AioAOQgu3Es_qy6_Vt40h3mVOPWmtbRNm0WtFP9KHAiiZsRsj9cNjkIj5w6dnPqxoK9QCUwEQ_zw2bj0sCXS8Uv3c7iVvpUF_AGOy_oLKg5p6VEOmVRBWKda7h2SVqS_yo1i66aRAZNLjy1G7PNY=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Webinar Bob Caputo to Present an AFSA Webinar on "Technical Changes from the 2010 ed. to the 2013 ed. of NFPA 13 Part 2 - Installation Requirements" Wed., April 17, 2013 Free to AFSA members! Register Button [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUCVgzJjiNUnRXEf0F5abLlUtzmNmz44BQFDNES4NiwN4rx3ngJ7YOrjSmrFV9PlXUmN0NApWw5b419pSyAG_VZxSKumhSlPgTuo0GMhLPig1Wop1xRA_2vWBjenuXFGiBsGwYkuMkfqZkeIDBtywUe8] For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUAtKi4iVo9Fk2E_iIx317dxGYFmoB8ue3-LWW_El5oF6wth155i2iWkby9JZiYCPdeznqOZ90BXGx-PQSA5Qr1LauRUeAnlvoi28Rn56op_mVuF0Zp4D9-f-uGi897iL-IeRuosZh17W4AMVKSOlSWs57EsWoMEt120P2uXxGAeBm19lAs3GkFJAMLVTP76bof1WZWN09rGDqZU-noYz1FAmbmxo5938g6IhXb1CCGsbjUnWaHOuKvBawaIQMkJYv_oU69dz7xnfeRzs7gJWZEQ]. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Calendar AFSA Beginning Fire Sprinkler System Planning School May 13 - May 24, 2013 Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUAtKi4iVo9Fk2E_iIx317dxGYFmoB8ue3-LWW_El5oF6wth155i2iWkby9JZiYCPdeznqOZ90BXGx-PQSA5Qr1LauRUeAnlvoi28Rn56op_mVuF0Zp4D9-f-uGi897iL-IeRuosZh17W4AMVKSOlSWs57EsWoMEt120P2uXxGAeBm19lAs3GkFJAMLVTP76bof1WZWN09rGDqZU-noYz1FAmbmxo5938g6IhXb1CCGsbjUnWaHOuKvBawaIQMkJYv_oU69dz7xnfeRzs7gJWZEQ]. e-campus_logo [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUDPVtPTIKsBFYycu-0MFHJr3VZvgzjcos5s1mxfGHJxUK2hJwxpu1JIqQC4CwynuYUtc_GpHtjBVkvLpcItA4vULltJVXmzgW7krbdgSJUx3Ilf_Tav9jAo] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Free Subscription to Sprinkler Age [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBAc8ZkF7A4hCQ1NFGEGHixogOfSTmiYzXziB_DQUVd7V-E3Za7wlLTsHPYNIgFlkv7SxfQ705siI-nP6QkeJS2pd-EsQ7xRM-yCEzFWroI0RHso7qo0a24bn9o6_1uIxehqHx6CgLnEGVo34mWkv6QNiniidjlscM=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quality Contractor [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUCJ5ZWKVNdGcYUBbXA76Iq6VAdEo1AyI6lVSLfMs8Fh-zdf-PnfXY_dytXjt2uVCeDAQh36Wx7f78zJ6soXYSKriDSvzpcZaAwwCMlFzcZk2DHaFct3j9S4hYCw0zk0SKFOmBnJnfcHibSDrp_2v8eEslOmobYybc4=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quick Links Firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBkTVYWGGE7nkc8MDepB3ZlZtPTlOtY1I4R9t-elFBjOAjIfsxHXUkSaBBYJnyKH1oYaV69NY63r3EVjsUdCW84vVFx_dDRpBYcTZU1H9cBpg==] AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUAtKi4iVo9Fk2E_iIx317dxGYFmoB8ue3-LWW_El5oF6wth155i2iWkby9JZiYCPdeznqOZ90BXGx-PQSA5Qr1LauRUeAnlvoi28Rn56op_mVuF0Zp4D9-f-uGi897iL-IeRuosZh17W4AMVKSOlSWs57EsWoMEt120P2uXxGAeBm19lAs3GkFJAMLVTP76bof1WZWN09rGDqZU-noYz1FAmbmxo5938g6IhXb1CCGsbjUnWaHOuKvBawaIQMkJYv_oU69dz7xnfeRzs7gJWZEQ] Buyer's Guide [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBbtDQf7Uk5kUkmm5pwXAwBC26FckhEJYTTZ2TMKQnzwcdaFb8qaxQFOag5w3yVOyD_24tu1FBa1cthOGnqb0Nq-odzX2QjANz0xP3C6gEaBayCPZWZ8874jsfWlhs0sO2i-db3JD3b7Q==] Join AFSA Video [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBJBl6oy2z981p-sh2VG-Vx8BIMjyLAltjZO25X_BFz1ONGxGxpvvE42dF5V2obOdiCCmgRTs_-Evcc-rzDtxonmXLVeLDe9IyfgPLleqXOJUGV8SbDZc8UAtAoRLPpcnQUpsBtZZ_39tsM2pRHtrOp] National [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUDhAtncGw-NcjiX2Bl0YGQeHfLEMJmMrqmiBvdtyWpRNOiv4P6afUUKeC3qQgZdJq1EzydqgSdWuevyc_ydkGSsb6-KkYIed1Fl0JtqZVjfMg==] Scholarship Contest [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUDhAtncGw-NcjiX2Bl0YGQeHfLEMJmMrqmiBvdtyWpRNOiv4P6afUUKeC3qQgZdJq1EzydqgSdWuevyc_ydkGSsb6-KkYIed1Fl0JtqZVjfMg==] OSHA Alliance [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUAUqhm8GUr2zHe21u8iYPDKRHxkdQQWOYvWqHEaykclv_dzO1i3XojIKmv4gaCDALBsCT5DEZioTBI9qtmpw0trnkmnKW1pHR0HY-al4aqyCLKnw_HITNEe-W-yGrShGqnMCEtNhbgEggsRBcUiW0In] Technical Services [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUBqYZx0y4TNDjYi0zNyS_cEzoY60YauIUbrdGuMEov99uIQw9myen8KNpm0smp7kn6XB8_IMWOD9Ebr3_iykTyVcMPkFuVGgyRm7CQr1_t14Lur93VYZ6cI2-bcwKh7JLM=] Informal Interpretation Request Form [http://r20.rs6.net/tn.jsp?e=001RULs9zVAgUDF08dtiiq5573lnK9VEtdrWuniT5XQL0gYDfqAlRtRrXOe4r_yKmvUCFSFRy0-OKHDMKJDG38LY2CsmBCSPdiq_qMpeR51Q9aEWjDNL2YxDsiac1mVp_95jR_2gEKF7GHimAR4n390w4UWFLfl4BeBQCuyuSlP4qw=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Join Our Mailing List [http://visitor.constantcontact.com/email.jsp?m=1102312387686] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Forward email http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1113028869274 This email was sent to [email protected] by [email protected]. Update Profile/Email Address http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001302TtUJqQp4xR_HNUdVQTw%3D%3D&llr=gdnaptcab Instant removal with SafeUnsubscribe(TM) http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001302TtUJqQp4xR_HNUdVQTw%3D%3D&llr=gdnaptcab Privacy Policy: http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp Online Marketing by Constant Contact(R) www.constantcontact.com American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | TX | 75251 _______________________________________________ Sprinklernotes mailing list [email protected] http://firesprinkler.org/mailman/listinfo/sprinklernotes