NFPA 13 Formal Interpretations
NFPA has informal interpretations on the document information page for NFPA 13 
at
nfpa.org/13 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKpuv7PRwPYf0ELpf0Ro5Xr0].

Installation of Sprinkler Systems 2013 Edition

Reference: 8.15.9

F.I. No.: 13-99-2

Background: Section 8-5.6 states that the clearance between the sprinkler 
deflector
and the top of storage shall be 18 in. (457 mm) or greater. Section 8.15.9 
provides
guidance on sprinkler protection of library stacks. This guidance allows floor 
to
ceiling bookshelves and requires sprinklers to be installed in every aisle with 
a distance between sprinklers along aisles not to exceed 12 ft (3.6 m).

Question: Is it acceptable to apply the principles of NFPA 13, 8.15.9 to the 
storage
of Medical Records on fixed open bookshelves, thereby allowing the tops of the 
bookshelves
used for this purpose to come within less than 18 inches of the horizontal plane
 of the sprinkler deflector with sprinklers installed in every aisle?

Answer: Yes.

Issue Edition: 1999

Reference: 5-13.10

Issue Date: January 3, 2002

Effective Date: January 23, 2002

Reference: 11.2.3.1.8(1) and 11.2.3.2.3.1

F.I. No.: 13-02-1

Question No. 1: Is it the intent of 11.2.3.2.3.1 to permit the system area of 
operation
to be reduced below the limits of Figure 11.2.3.1.1 (e.g., less than 1500 sq 
ft)?

Answer: Yes

Question No. 2: If the Answer to Question No. 1 is yes, is the intent to allow 
the
density to be less than the limits of Figure 11.2.3.1.1 (e.g., less than 0.1 
gpm/sq
ft for Light Hazard) as long as the point was legitimately picked from the 
density/area
curve and appropriately reduced per 11.2.3.2.3?

Answer: No

Question No. 3: Is it the intent of Section 11.2.3.1.4(1) to require the 
densities
for 1500 sq ft for all applications, including when Section 11.2.3.2.3.1 is 
applied,
when the final area of sprinkler operation is less than 1500 sq ft?

Answer: Yes

Issue Edition: 2002

Reference: 11.2.3.1.8.1 (1) and 11.2.3.2.3.1

Issue Date: March 9, 2004

Effective Date: March 29, 2004

Reference: 17.3.4.1.4

F.I. No.: 13-02-2

Question No. 1: Are the dimensions in Figure 17.3.4.1.4 intended to be the only 
acceptable combination of rack height, clearance, flue space width, rack length 
and rack width?

Answer: No

Question No. 2: Are other situations not shown on the figure, such as double row
 racks with a width of 9 1/2 ft (4 ft loads with 6 inch longitudinal flue), a 
height
other than 54 ft and a length greater than 24 ft allowed as long as they comply 
with the other rules of NFPA 13?

Answer: Yes

Issue Edition: 2002

Reference: 12.3.5.4.1.4

Issue Date: July 16, 2004

Effective Date: August 4, 2004

Reference: 22.4.4.8

F.I. No.: 13-02-3

Formal Interpretation

Question No. 1: Can residential sprinklers of different orifice sizes be used 
within
a compartment provided they have different directional discharge characteristics
 (i.e. pendent vs. sidewall)?

Answer: Yes.

Question No. 2: Can residential sprinklers of different orifice sizes be used 
within
a compartment provided they have different thread sizes such that replacement 
cannot
be confused?

Answer: Yes.

Question No. 3: Can residential sprinklers of different orifice sizes be used 
within
a compartment without regard to discharge characteristics, thread sizes, or 
maximum
protection areas?

Answer: No.

Issue Edition: 2002

Reference: 8.4.4.6

Issue Date: September 9, 2005

Effective Date: September 29, 2005
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYMJtnS3v9SgM=]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxPOdEVzvNe89I0ok53jVyIHoKVME57J42oI2rZR4UF_ZPmpGp0QHyurcjwjDk4_KgppRWkXljvpsUyEBGpzanh5hQnV16ypr5NdqM1YQJiKM_ti9f8oIPgNeLZPF7xaBC1RACHbMDjxvE=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
Sept. 8 - 19, 2014
July 14 - 25, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKpToIKQHgWnc_yOqU0SoKSgm0-tc3GSyiwhFHd-C7nkgdxNsPN62vD-PkXSSAPsLZz5km1rVZzbnPMhiVS8XZ65UXwACpg2G5F5A9i16yT8btaG3PxD-GkEDyVMu1rPAyhr57EdeiGXF0OtPzVEF3hISD9pKxM6Zm3qgT757pSc_AxzupzRqymTbtz0CEsQBF0AyNooej8a9g==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKrEUGYUE-iOO53BSNdV-LHUWCtmr2ojDGvBOwgIESBr5A==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYeOuif0WkI9xvKufJHkuEYMnfNzKPQ9IayVaLRQsjJ3U2dZVmt2WsYq0B79LzrBi5]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYeOuif0WkI9ySkszrQowTBWeCMBvllsj5pxTFb0cGRhfdF1nIKiwEGGlyaP7tVviq]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYMJtnS3v9SgM=]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKpToIKQHgWnc_yOqU0SoKSgm0-tc3GSyiwhFHd-C7nkgdxNsPN62vD-PkXSSAPsLZz5km1rVZzbnPMhiVS8XZ65UXwACpg2G5F5A9i16yT8btaG3PxD-GkEDyVMu1rPAyhr57EdeiGXF0OtPzVEF3hISD9pKxM6Zm3qgT757pSc_AxzupzRqymTbtz0CEsQBF0AyNooej8a9g==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKpBWIY1TaaFBaX2h49DHUlBKOddw3jPAJ0xKJDn0U28v1eaPush2XdCFPW-_pU2sBUU3YnejEHTrQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKqEyTCNIrjio80kjvslokuGy6g5DEq87yjqYjXvTSvZJl17QPY0KVqJIs0Z8HCQ6RO7PCcaMpCVfw==]
National  
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoxw_kCEp00hmHRuCGB06syS2C4W4Zlv_MhlODcXa7EPQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoxw_kCEp00hmHRuCGB06syS2C4W4Zlv_MhlODcXa7EPQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKrKSqDNLZl27z2Q3qGMeF1KCX24-ldrJEWrFPJMPUZ2zU5JJqsiCfQ3d46XKR-d3UcMyGmmRQQ8Cg==]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYeOuif0WkI9zbBriV_8UCMklwEtiklvt0]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001yqzRgWwuQ48D22tddJ3zkliq24bVRit9UoaPclU8-kknuhhXHT34A4fXA3KjIbxP6mAPuuPAnKoR-XiFesY-lB4Oki9KASCYeOuif0WkI9zMML9ZPhPRZCVYh3D2mI9VmNEWvQbUiB96Oy88-gJd7Fuop7Ubdl9v]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686&id=preview]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1117075495290&id=preview


This email was sent to [email protected] by [email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001DPYbyWd_hTTO-jjYUCXftA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfY-V4yYxBBQbHvk74jf90rEKbatrTBH0Hw%3D%3D&t=001DPYbyWd_hTTO-jjYUCXftA%3D%3D&l=001FCSs65SMrsI%3D&id=001b-xBWU3VMkcCDNcOTBJBHAeNvyNZ1QyA&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251

THIS IS A TEST EMAIL ONLY.
This email was sent by the author for the sole purpose of testing a draft 
message. If you believe you have received the message in error, please contact 
the author by replying to this message. Constant Contact takes reports of abuse 
very seriously. If you wish to report abuse, please forward this message to <a 
href="mailto:[email protected]";>[email protected]</a>.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to