Water Supply for Cooking Hood System

"I have a kitchen hood fire suppression system that cannot take a static 
pressure
above 125 psi.  The supplier wants to connect it to the fire sprinkler system.  
The system has a fire pump that will provide 162 psi adjusted for elevation to 
the
hood system.  They propose installing a pressure-regulating valve on the feed.  
Is this a violation of 6.1.3 and or 7.7.1.1.5 because the suppression system is 
not rated for at least 175 psi?"

We have reviewed NFPA 13, 2013 edition as the applicable standard as well as the
 2014 edition of NFPA 96. Our informal interpretation is that the water supply 
can
be provided from a fire sprinkler system.

Section 10.2.9.2 of NFPA 96, Standard for Ventilation Control and Fire 
Protection
of Commercial Cooking Operations, addresses this question.  It says where the 
water
supply is from a dedicated fire protection water supply in a building with one 
or
more fire sprinkler systems, separate indicating control valves and drains shall
 be provided and arranged so hat the hood system and sprinkler systems can be 
controlled
individually. The manufacturers of the hood fire suppression system will have 
information
on how to pipe and valve the water supply coming from the fire sprinkler system.
  The installation manual for the hood fire suppression system also provides 
information
on appropriate pressure reducing valves to be used to reduce the sprinkler line 
supply pressure and flow rate down to the manufacturer requirements.  As such, 
this
is not a violation of Sections 6.1.3 and 7.7.1.1.5 of NFPA 13.  Since the valve 
is capable of shutting down the water flow, it can be supervised with an 
electronic
switch.  A pressure supervision switch can also be used to verify incoming water
 pressure to the hood suppression system.  NFPA 96 in Section 10.3.2.1 says that
 where an automatic sprinkler system is used in conjunction with a water-based 
fire-extinguishing
system served by the same water supply, hydraulic calculations shall consider 
both
systems operating simultaneously.  One manufacturer says the gallon per minute 
is
calculated by multiplying the length of the hood by 1.5 gpm.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 14 - Comments Close on Nov 14th

The first draft 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlODT3Zh4KwmOPBnR088dz7aPv2H2gImS_1v4X72nXeT3FfzAO39G2wMGhUJrS50cUTSPVLmgEG5yWJTKEJWIoxu8p1gfyuQoZkrvhaL1P9FrIcvh-JxG4KVwg1kX9sEMIFFCSBwrwcRkwl7tPM2O8eCHqeASoLD4RgvvqiQzJpJlDoRUBnRPOnb5roK2ngHO_0PcCVlcaD5jQu6ubPj8vQ_4=&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
for the next edition of NFPA 14 has been published and available for comment.

The Public Comment closing date for Fall 2015 documents is October 10, 2014 for 
paper submissions and November 14, 2014 for online submissions.

SUBMIT YOUR PUBLIC COMMENTS ELECTRONICALLY!  The Fall 2015 documents are active 
and accepting Public Comments electronically through the Electronic Submission 
(e-PC)
System.  The system will automatically pull in the text and will show changes in
 track changes.  It will even save your Comments.

e-PC System and Instructions.  Submit Public Comments by selecting your document
 from the list at  http://www.nfpa.org/aboutthecodes 
[http://www.nfpa.org/codes-and-standards/document-information-pages],
then Click on the "Next Edition" tab (see screenshot below).  You can submit 
comments
or just start and save your work in progress.  If you would like to review 
instructions
on this process, please go to http://www.nfpa.org/submitcomment 
[http://www.nfpa.org/submitcomment].
 For your information, a list of the Fall 2015 Revision Cycle documents can be 
found
at: 
http://www.nfpa.org/codes-and-standards/document-information-pages?cycle=Fall%202015
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlODT3Zh4KwmOPZ-3HL45cCpBGpinF2zM8hqjlsZV9qKiyAaICu4eRN3pkBaemLedB8dTG8SPzGTSrJJ1gyeqtVLeMUjwfGjqFkHctfXITvPwhr4QZHTCDnwnQhYQOjX1JxwOUTYYNoXYwdYF7knb-vakLdlmFa-iCJM8eA-C9TsULkV36Z2a_GOrjqAceLvv4hOaunhLvh_MYuvIo6P9PC0w=&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOOAnKG0r0rGoZ78SezQfI1szs5emLvj2pAK7Pn6xmRXKhufIZKSDC129R0mjSJYTcMh_mFInR7M6ekdgeju9Ou4LbB65Q4d55eb42Mm-4ESQnJZfNwIf280vI0B1q59hUQ==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOE6pp6daSJfTnBscShSzQhH7AnT0NO_zf-N08BsYdTL6QZ2wikwbGVCnfdiUiULD01DQHNqYioNBhIr68ST28BDGk0wmpu4yrs_jEoUxW2NViQ39vk0aL1C1Ri8UPDd3LJN5z_-xCyp1yVy5XJ6gnLRDtU9sgkxrqAstGab3Qv_ioZDjor1PsOrDjMMmABhEx4tr4fX2BOTTApfs-gnJP2E=&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
The 2015 Schedule will be
published soon.
More Information [http://www.firesprinkler.org/education-center/schools/]
Nov. 10 - 21, 2014
SOLD OUT!

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOFmGtskGzv_P8pfUiqerAs1Jc1hAVjPbecxYiSabM7sjDXtR1fPzFLviCC62wjTwldgPM8RvZ-OTe1qovkFcGkr4zhllyfbBboPiutoHOUlMDPAMGXD_tsDH4axgX2ioPQ==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOE6pp6daSJfTDdyeo4b7zBBxUI78YsBzT-4ht4Uz7FeodXa5VxeOLHiRVI-VmN4F4heXmLb_OEFWs5XNSpsLzM9SRsVgDFDumsAU5rELoIo7Lzblx9gZSaNatvmvkQuV1u6AMd8vpdUG&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOOAnKG0r0rGoPe_skY1xP0s_Nq_X0tNmWX_1D0srj46qDa_CB8lpFydSbdfdyN0YPqCARP2QMaukK1pfQwX9daLyjS7frGXw-BW-UgN3cQu6QQeamQ_uWSolE3P_yr2bEBoyZQqStXIwgzVZ09y7agJ9uNTTCOun8w==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National  
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOB6W5ldthUygFn5jbX-7RAvmPsLWR6OfK44RnJI4w4athMVywg9hNjQNda8GDrQnfwmSd_Qrc4swTpNdcVHEBWRSMkKYUzlnrtRwPe6w3mSoeW9QsDjnOsM_kFbc-OktTg==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOB6W5ldthUygFn5jbX-7RAvmPsLWR6OfK44RnJI4w4athMVywg9hNjQNda8GDrQnfwmSd_Qrc4swTpNdcVHEBWRSMkKYUzlnrtRwPe6w3mSoeW9QsDjnOsM_kFbc-OktTg==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOOAnKG0r0rGolEcSGey9O8A7plFgEvwCA1mpgQe6UINMpqPULoWHoRzEaGJIH3Q0-wSuo9vMlRWIRoQaOkcd3B980boKGdMoOWjeOUZpXTPGYOaqDCO9ac3ALbb2QCh5GLnX70RZWapyCerb9F8LaBtVFVwGNcliNQ==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOE6pp6daSJfTlAqzOM79vbMCOpiuVEaSUtEhDR0f294vrZofs7X-zgi8k-QZzZvRgSufmo1291eQ_6VsyPTFXa_PSkFKpnxBnhAlPUfsMU57GP3JmQla0vWZmnoLTqqkq7j-w9hRng2mX1O7HpwVfwPZllDEODqRaA==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001_As6mfei_9oadomZ17Fziy6FE93eURt3pNDXxpobvYB1wE3kwmPlOE6pp6daSJfTHxK_Z4Qo70hhNI3ucYVghvYfINQKpM0fyXIFq6UjJJD5sSvQYY8iHLcRMETe_67Puf7p3uvdKHcvqUahUGy-E7COrbEPHtJp4WOZDAQ2zzBpy9_G7VM02aF4RrwNdUSgOWGMbvInzGJ_oaqDigcDug8fzOzy8OyB-vtVF5vvnwwPtj24v5O9Pw==&c=O2DijyClF_XQRH39CPQNZAJDrbBgqdPY-agQpIJr7SdtMO1UadhZ2w==&ch=Vez_844fcIdmumjPe2YXu0s9YUzcVDraANyt9mC8cLP3O7jTDVmjAw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1118816657373

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=1d3f8821-0c32-4ad1-ad81-57f8a8299f84


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=1d3f8821-0c32-4ad1-ad81-57f8a8299f84


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to