Remote Areas With Walls

"Figure A.23.4.4 gives some guidance on setting the remote area but there are no
 walls shown. How are remote areas determined for the density/area method when 
there
are walls?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  The same 
process
is followed per the figure where the walls are ignored.  However, walls can also
 be used when determining the outer boundary of the remote area.

The NFPA 13 standard offers little explicit guidance on this issue and this can 
lead to some confusion.  Thus, one needs to consider the intent and apply good 
judgment.
 There are two requirements to be met.  One is to meet or exceed the minimum 
remote
area size with any modifiers from Section 11.2.3.2.  The other is the remote 
area
has to be a relatively rectangle with the longer leg parallel to branch lines 
and
measures a minimum 1.2 times the square root of the remote area per Section 
23.4.4.1.1.1.
 With that said, walls are generally ignored in assigning the location of the 
remote
area or the most hydraulically demanding area.  This is done predominately for 
ease
of application as well as the fact that initially ignoring them presents no 
negativeconsequences.
 The remote area determines themost hydraulically demanding piping configuration
 and not necessarily where the heat will flow and activate sprinklers during an 
actual fire.  Guidance on setting the remote area is located in Figure A.23.4.4.
  This methodology requires more sprinklers on the branch line to be calculated 
because it is more hydraulically demanding.  This also defines the length of the
 remote area parallel to the branch lines.  The boundaries for the remote area 
are
placed at the midpoint between the sprinklers for both the width and length.  
Figure
A.23.4.4 works well for symmetrical layouts and can be a little more difficult 
to
apply with varying lengths between the sprinklers.  Where the remote area falls 
beyond the midpoint between two sprinklers for the length, the area has to be 
extended
to include the additional sprinkler(s).  Regarding walls, they are typically 
shown
on plans.  When the remote area is placed on the plan, the remote area boundary 
and the wall locations likely won't match.  This can create disagreements and 
debates
with AHJs.  For instance, if the branch line is one foot off a wall, the remote 
area boundary is initially shown to extend past that wall to the midpoint of the
 sprinklers.  The AHJ will likely comment the adjacent branch line (or portion 
thereof)
will also have to be included to pick up that additional area.  Also, when the 
minimum
length extends just beyond a wall, the additional sprinkler on the other side of
 that wall would have to be included on the branch line.  Thus, walls are 
typically
used during layout to define the remote area boundary to avoid this conflict.  
The
remote area may have to be extended or reduced to include the coverage area of 
sprinklers
within walls provided the minimum remote area distance parallel to the branch 
lines
is maintained.

Either methodology discussed would work provided the two requirements of the 
standard
are satisfied, minimum area and minimum length parallel to the branch lines.  
The
last step in the remote area process is to verify the minimum square footage of 
the remote area has been satisfied (actual floor area and not the summation of 
the
areas of coverage).  If not, additional sprinklers have to be included on the 
forth
branch line and should be placed closest to the cross main since that should be 
more hydraulically demanding. Keep in mind that heat flow for an actual fire 
scenario
is totally ignored regarding walls and their associated openings.  An exception 
to that would be the room design method.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjlhE_GzWr5L4D8EuGA-xcSkvgD1OhWeXG5ce2qY9z8B78ws0I3A-ECdCy12PStD3EOkRD2rjTzDr9ULxSRxSfw1yK0bAC5nBjD82eLc3YdmkjtDPp4Z2wv85wYm_k63IYQ==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjtAbQ2Xhc-ezBR4FCRrUXhVnleRb0IL8kJPMnP7xF1FZcspZq6jACy8uhOK0vJcm0_2bC-X5t666yoFZys88Qjfm_ySxq6GQPQQwNcUB3fJToPTjPRQFPq0NrZYdQoiMQaTPc6F6PrNYGK-aXWSX7w3zCT3Z_g5DFvHjv7qRy-d2Cb2oqV81Uw-OeDVN2o2eQ3YYXpCbkVIQEWK4mwY_MaY=&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information [http://www.firesprinkler.org/education-center/schools/]
January 19 - 30, 2015
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjgl4OypCjC7XfrkA9VXDS-j01F4wGzy6Ogfqh8Ru5YUEJClXJcL4m5RlBCXEposvso5HV3YiQB2sbTQ2rR186Bwtn-TdT_7wZS7gMLYTPQcMlsHl-ZKF48_t0EKcgb_OHw==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]
Join AFSA [http://www.firesprinkler.org/membership/purchase-membership/]
National  
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjpr-wJtrkKIiAJkcdZhAx8NKJzEVZS5BwhrQbqPZuLm8_xqXi39RDz9dUEcjvEUYu7VqZlWasZPgcRY5YB7WiyOrpkNO0D-w7qostP-UKF1e1WdDNBDkpsIx1o8f4uyjMw==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjpr-wJtrkKIiAJkcdZhAx8NKJzEVZS5BwhrQbqPZuLm8_xqXi39RDz9dUEcjvEUYu7VqZlWasZPgcRY5YB7WiyOrpkNO0D-w7qostP-UKF1e1WdDNBDkpsIx1o8f4uyjMw==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjo1PSmFLjW6WWRwcV3RRfOInocgZrolldmq23V3-ilcKnLW8E5TBJKELnnDOj8MdcJvSY-yGhqRl-StccfUfgt7vcquMksiLqQCJoHiL3fFaSIsTYGy-25ipuHLfOJhxgjSv4WRyYy-aDYPXITw19Pwb2njYC_MJ6NYgbBzSYrh9covZKJT8D5o=&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjkBbJ8sZT2UFT6x5_10ytAcLQ4XvFcq0tmfWd32GgYOtGpK508gmLj5mcV8sBBgFqBVjxIlFj-ueqF5naX7XPWEb1s-lsqJDp0OQR5div6-gW3juPf9GS5mNcM1VgyxFw0URUiTluQ7K8-dkjE6GjdrKxWbw4S26AA==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001Fuif2Clz5oCJXc6qMxCRUayR2DAjv0uyethZtNa8p-7sdrU6TESSjkBbJ8sZT2UFIw0jMllZ5GDjqd0E3VfhSrsgFSao3m0Liqgulxw3E_6g89gQ7_E1qUG7qMvuM47JGYZ98Qd0dp1LsayJIkCoDZqwrycmZ5eenVXYqevAu9J0m3OtJ1aOeMZREm0GYR6wOyop-gNynQVMQHQW60Edk8Ijx-1cC2c-gMwkK5fPFydLrbTKCRTyPA==&c=2WMu01LAqpF46Kvk4ow6YM6tCmQ__P9cCIzwQ-lh-D7dijZ7feqYGQ==&ch=a42ycTVSrNIGoEBdhfJYnQN8LpNLkcu8ACImrDOsNDpXZeoC_v3h6w==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119275607583

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=0ddf265a-7ee9-44e3-8746-1819346cf267


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=0ddf265a-7ee9-44e3-8746-1819346cf267


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to