Fire Department Connection Inlets

"There is some confusion between NFPA 13 and NFPA 14 regarding the number of 
inlets
for fire department connections (FDC).  What is the proper number of inlets 
required
on the FDC for a standpipe system that has a fire pump with a 750 gpm demand?"

We have reviewed the 2013 editions of NFPA 13 and NFPA 14 as the applicable 
standards.
 Our informal interpretation is that three inlets will be required with a 
750-gpm
demand and four inlets with a 1,000-gpm demand.

The requirements of the NFPA 14 in Section 7.7.1 indicates that Class I and 
Class
III standpipe systems shall be designed so that the system demand can be 
supplied
by each fire department connection, which is provided in accordance with Section
 7.12.  Section 7.7.2 indicates that where an automatic or semiautomatic water 
supply
is required for a Class I, II, or III standpipe system by Section 5.4, the 
standpipe
system shall be designed so that the system demand can be independently supplied
 by the attached water supply and each fire department connection provided on 
the
system.  This tells us that even with an automatic water supply, the demand also
 has to be supplied through the fire department connection.  The number of hose 
inlets is determined by Section 7.12.3 that indicates fire department connection
 sizes shall be based on the standpipe system demand and shall include one 2-1/2
 in. inlet per every 250 gpm.  Thus, if the standpipe system has a demand of 750
 gpm, there will need to be three 2-1/2 in. inlet connections.  If the standpipe
 has a 1,000-gpm demand, four 2-1/2 in. inlet connections are required.  A 
single
inlet such as a Storz connection is also permitted as the fire department 
connection
by Section 7.12.3.1 where it allows an approved large diameter hose connection 
of
a size to accommodate the require flow.  NFPA 13 addresses the number of inlets 
differently on FDCs to supplement the water supply rather than accommodate the 
demand
flow in Section 6.8.1.  This section indicates that the fire department 
connection(s)
shall consist of two 2-1/2 in. connections using NH internal threaded swivel 
fitting(s)
with "2.5-7.5 NH standard thread," as specified in NFPA 1963, Standard for Fire 
Hose Connections.  The annex clarifies in A.6.8.1 that the purpose of the fire 
department
connection is to supplement the water supply but not necessarily provide the 
entire
sprinkler system demand.  Section 6.8 also permits threadless couplings and a 
single
inlet connection for risers 3 in. and smaller.  Fire department connections are 
not intended to deliver a specific volume of water.  As such, NFPA 14 requires 
the
system demand to be supplied through the FDC whereas NFPA 13 does not.  This 
difference
affects the number of required inlets.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrRuyjYQ3tUH5491idCrtKpDQqzbTlLLmSqHyjD8zmshHReWYBg5goH6dgY2oIY5bs0W9-7pCn3U8Ol6y9-xhrQjt4QnMB3Tikc7Fwx2zLp1hwQ-1cYndM6QoLawYbvIOWA==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrSiZ1kJUo-3lPoxkKpjZgy68dlNRPfvP37qw-E0a46An41CKpn-P-7glMi6BVDnH1Y4b5stFtzoxlZ0z64cEYR--lmVbUwmIIvdHc3rEu2Sh1qUsdCPsDwLC9NkIz0gvTg==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrSiZ1kJUo-3lPoxkKpjZgy68dlNRPfvP37qw-E0a46An41CKpn-P-7glMi6BVDnH1Y4b5stFtzoxlZ0z64cEYR--lmVbUwmIIvdHc3rEu2Sh1qUsdCPsDwLC9NkIz0gvTg==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrdllY6t5w8Mt0QTn0H38iUdMZYPKVxaGmvNkQOOvg4VTdrCTsNsw-kRXPr-t0uP0dSAzhNgYZ7nkfGPwQYOn2nWW9YNwJDlZwmAUkAuZPmAYjPAoHi1lyNCiWpe4RtuSJ0Rxu3S8g0QjIQbYj03wP6XlKBoBPX2rsPpZ2Rjs9ktDbmJ-m9CkIGY=&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrUPc0Lsx7xR0rWX0fej6OCr5kph0nFA7Toe8Y_z5_o4RrOSscRGxNPlBNiUG-L7ca5HjRpOfQbpllQcGBI6u0SuiCVyTdsJKCAuWpZPNidoQF5JNc4cnIioazrxd6VsYnwLzEqby6IFDUzQLBOzkMII0MYyg8S5xJQ==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrUPc0Lsx7xR0WFis5ugagoUcEiN66KvnMCoiWnbj5nGA_2D4rmBuXTL5dUF6nqzsE9cumIEyYM5xHlKo0lFQ47gp_zjw09o0xS0Vz1kS4jUeRqRJV4oiWsslQK97xhfUryGAQ7TrNulSwBHLDG9u0W0xW_nUklVdRo3NmH7_LgZKlgUYnnmg2O45N-oGBxCjJQ==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrXAh9qrSaZMcO94yvpEWYpCd5ZfF2QP9QaOgzhBAsSRqyosJEjnrBrvh77tYinqAPXfBRyzVrOpDak5XKCzYF7QCYNdMSuUv2nQbX5kbhPqWSQRIQKMSwlP_lUOT7p5mB-np5BTnTPbeJm81V6Bgz7aL_8ZbY-xccO70sG8epgJoq9UB-iC5abxxo5MWumfghg==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrbB2ma2YJZjJRJ4TMttVQrDJkZUpLkJCYnhoYhyecJN6cXBRKJJrfz4_Ucqt_yddxc8snONi9OBrHMSSgt_uM861KjmBzI1NcXqodEnhQHoXKqPpIP8jzWu5f-f434YBzyLVjqK0yaB7elOpe5wlYVBr9xDj5ix-jvlDTGkFhbk1qx8RuyV6wZ4t62KbdC6T9w==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Webinar
Sprinkler Pipe Corrosion: Mitigating It With a Nitrogen System

January 28

11:00a - 12:30p (CST)
This webinar offers 1.5 CPD and 0.15 CEU for a $15.00 fee.
AFSA MEMBER BENEFIT
This webinar is free to all AFSA member companies and their employees!

Register Button 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrUQra8SMt_CJdN23wR-YSpDZRMXHAkM6mxHZS30c_M9GG4mzOiE6xZ3v_VOmvNFNBYnkMI-FWbTkgMoDnAKOUSOYTh1xWqAe0-y7PwBVlzUIlpkm2hEk0Rzfmp4UKboGxNY3C39556Khye-N0ZH1VcC5atToIAKxCw==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrbB2ma2YJZjJvYjBrx3ZWlluENEprRH4zQ8f_F18VSIdyMAWE0xlkMcnoNnrd0CV8Jw9csHgFaWVM2Cx8quFsjtGvs4WMkUXhLm-Uge3_UBvL1-qzRVl8luf8pw5tBJ5nGAL-9xmafOm&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
January 19 - 30, 2015
(Sold Out!)
March 16 - 27, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001CVavMTT2HdC_TNVhMbZd7q5LUrHlnuKfRLB-EYMS2imT0fR45qzgrV6y94Rbxa4lIHEKn6_zzDoExnr9zKqrD6QgvHCjW7Lc_ehX2fIgEJ-Sd4INhgaM4fdbDTyrRwcSpiIoeOeGIBPwbpMpvr6OZu-2QjTmn3hQE4N0CR12PqiKGNEUBCmnuw==&c=A_0utaqpea81WQqf_myEXG8rshKC2V4B4lp6sAKAevo_LW9kK6iTcA==&ch=GeyvdVreF8-4Pnf_3m7IQ7bnnowW07X11WqbzuXg16pY8lHRGDmjHw==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1119847416623

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=5c163860-843f-414a-b5e5-e1437b4f07ee


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=5c163860-843f-414a-b5e5-e1437b4f07ee


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to