March 2, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Protection of Group I-1 Occupancies - IBC 2015 Edition
The 2015 edition of the IBC has removed NFPA 13D systems as an option for
Institutional
I-1 occupancies for more than 16 persons. Section 903.2.6 for Group I says an
automatic
sprinkler system shall be provided throughout buildings with Group I fire area.
Exception No. 1 states, "An automatic sprinkler system installed in accordance
with Section 903.3.1.2 shall be permitted in Group I-1 Condition 1 facilities."
The NFPA 13D systems in Section 903.3.1.3 referenced in Exception No. 2 was
removed.
As such, the protection referenced is Section 903.1.2 for NFPA 13R systems.
Group
I-1 occupancies 6 to 16 persons are Group R-4 occupancies Condition 1 (308.3.3)
and 5 or fewer persons are Group R-3 occupancies (308.3.4) and still qualify for
NFPA 13D systems per Section 903.3.1.3.
The 2009 edition allowed NFPA 13D systems in Section 903.2.6, Exception No. 2 as
an automatic sprinkler system installed in accordance with Section 903.3.1.3
shall
be allowed in Group I-1 facilities when in compliance with all of the following:
2.1. A hydraulic design information sign is located on the system riser;
2.2. Exception 1 of Section 903.4 is not applied; and
2.3. Systems shall be maintained in accordance with the requirements of Section
903.3.1.2.
The 2006 edition reference is in Section 903.2.5, "An automatic sprinkler system
shall be provided throughout buildings with a Group I fire area.
Exception: An automatic sprinkler system installed in accordance with Section
903.3.1.2
or 903.3.1.3 shall be allowed in Group I-1 facilities."
The 2006 and 2009 editions of the IBC recognized the mobility of the occupants
in
Group I-1 occupancies as well as the basic life-safety intent to protect the
main
occupied areas.
An Institutional Group I-1 definition changed in the 2015 in Section 308.3.
Institutional
Group I-1 occupancy shall include buildings, structures or portions thereof for
more than 16 persons, excluding staff, who reside on a 24-hour basis in a
supervised
environment and receive custodial care. Buildings of Group I-1 shall be
classified
as one of the occupancy conditions specified in Section 308.3.1 or 308.2. This
group
shall include, but not be limited to, the following: Alcohol and drug centers,
assisted
living facilities, congregate care facilities, group homes, halfway houses,
residential
board and custodial care facilities, and social rehabilitation facilities. The
"convalescent facilities" reference was deleted from the list.
The Group I-1 occupancy includes two new conditions. Condition 1 in Section
308.3.1
include buildings in which all persons receiving custodial care who, without any
assistance, are capable of responding to an emergency situation to complete
building
evacuation. Condition 2 in Section 308.3.2 includes buildings in which there
are
any persons receiving custodial care who require limited verbal or physical
assistance
while responding to an emergency situation to complete building evacuation.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTicyMe6YTN0rIy-2unwkIgf8ykXsvrcftoeiKHfgVesV3Ip55FqEU3VpJ_fmuc-jMGlCpn0aZaCdMNTF7dJn4hukcRYxMxu9Ik5NwWgWpugct62CiSosfs2FWYz-dyq8wA4Q==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org [http://www.firesprinkler.org] Join AFSA
[http://www.firesprinkler.org/membership/purchase-membership/]
National
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTicyqipiUwf-dZB8J-3ck7acbRctAPrwp-xO4zrFxWtJAzZA_tePWuc3As0JL5yMDMi8HTTTEtAE1-_M3xDvENHruAHSVub2yN0eVGfBK79kPs90GtJ_0HeFMYplDg9YTbiQ==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTicyqipiUwf-dZB8J-3ck7acbRctAPrwp-xO4zrFxWtJAzZA_tePWuc3As0JL5yMDMi8HTTTEtAE1-_M3xDvENHruAHSVub2yN0eVGfBK79kPs90GtJ_0HeFMYplDg9YTbiQ==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Safety Training
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic1Ep_Mz1Sf9BdTG7Lzim8S03anJtmUml-DJeUVu7OvwJh28u3Nit7QBHiin30SxN2wkpKFP4AHLAh1g-cnhlpz0irlnhi-hPkkkML-iPEpo9m6rH0m9bLcPSRf-WrYEILCbDW_xX73iezH0pEhdqRiTtfnvEElGZy3DkOBX_pS3_65bIp1J1H34=&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic7QzRY16mqaN5OdPDrXGxp1RurvHT3v7ixegJnkQSPMVoWkMAOm8_GPH7afnp4R0EKoKhoSCyKKOL1Cs3UgINk4XXHbdlbFgtN5dMpJsVI_BdcblZ7HmaoguIR7VBi64otjAe2TBlXhGkxxME5y80c96GUB6hDnS7w==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Informal Interpretation Request
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic7QzRY16mqaNq0zBHd9KOT8OlB0X8uD2CYv_xatdB4J1qMe7mT57bZfMZSIPHkulw4Q3_mdBIDQekKXA8C-o39ZWombvseACXv4em8jFTvep5rfvWQhQZisqJ2SKIQLSBRDqdXuqyZ0KkF780oTRjCoLivo9zwb9u0_BF4390dPVr012hUNG06-IzZ7-m3bn1g==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTiczlN2SfNPbceIcPSC6q803qMtH2vHMKOjFrbx2mVsTnJx_HgTxsU193CM5MKw8jkWt9Hg6aa6l01S-VLnVAHvgNsBcKV_JZ-r5dI0jTkzlBQYu3FE_tfAOFnsO9_eEf85TEHrZmyeq575yE4uHxhbDhBkDCvNQjOcTXpGOV7300iM08kqX1xNv5yKGgzq4ed8w==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
Archives
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic4dnhXCRrMCD3FkD-cbTZyU0ezq2Upk-KOFs18aT1mthAJ--zyBbRnxhP7uSIh7xgqcFLVCMC8QWMRpOSt5aonK8Phd9brvI25Wokld3HZP10hiHDw92Nd2jmJk4rjT7oNU7xLy_ikgxsXGpGKt5IKUWgcBIgq_UJrolEyB7O9ysdnG0hbAG-hMLDAiMte5IYQ==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Webinar
Building Information Modeling: What, How, Why
by
Ray Lambert
and
Kenneth Stowe, PE
Wednesday
March 25, 2015
11:00 a.m. - 12:30 p.m. Central.
This 1.5-hour webinar will be presented FREE to all AFSA members.
Register Button
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic1Ep_Mz1Sf9Br5KTYCmGLDHdGFAbOww5wXPCPjQ5lyUnyttDcAtDEoNK2vlFp9zcEMPm9U5GF7pT10mr8-UVuqLcHNRwOIveXTG9tX9YXk7EQGqkAxp25iHNUVENiySHR94lqUneVAvI4o7pNRoTOn2iH8UF26vHtwSkByKAZf80&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
This webinar offers 0.15 CEUs and 1.5 CPDs. To receive continuing education
credit
for this webinar you must register for credits for a nominal fee.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTic4dnhXCRrMCDQdLNwLvjSBpJwoK4tPYXNKjhCkQm33culXyc3Cte_MhJgPq-YN5-eU5WeJHdIbMdp7_TRGBcYH1XV5PMmQC5awfEK2jxWCOAZybulQRgR_s-jQZ4jIzmCWCPt2b9GtSR&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
May 11 - 22, 2015
March 16 - 27, 2015
Sold Out!
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://www.firesprinkler.org/events/].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001Z64Eygv3R4Jc1afgEJyH202zqZDOc-hEz5bto_p0FYuD_0aIDjTicwCT5XnpVUv4Mz_L3dz6XIESLiXpdo4EHTI0cuc4F1-HE-oKG8ZHpJ-TLEvlaozyl8uScMeQS7K1KGn-FrWd2eLlAqqlbTz2NlOmSRwZxnVt_FNysvy4HTfrLD8u31tK_g==&c=yZNJBqZh_d7pCzsaIJai62yBUNzVqd9djdfQ9RLsR18JZuSGsig-Cg==&ch=OvdN2YN468juesmVnMpSLnezzrp8NW6HewWe6Vg3tPztSPqY_qVdSQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1120260022747
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=3972420e-2b31-4a56-99e0-f0f5f16d882f
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=3972420e-2b31-4a56-99e0-f0f5f16d882f
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org