June 8, 2015
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 13D - Architectural Features Outside the Sprinkler Listing

"The AHJ wants clarification of using listed residential sprinklers in a 
residence
with a barrel ceiling in hallway and various rooms.  The radius of the barrel 
ceilings
range from approximately 42 in. to 12 ft.  We proposed pendant sprinkler 
applications
per the listed spacing.  Are there any restrictions?"

We have reviewed NFPA 13, 2013 edition as the applicable standard.  Our informal
 interpretation is that the standard permits residential sprinklers to be used 
for
a barrel shaped ceiling.

Section 8.1.3.1.2 indicates where construction features or other special 
conditions
exist that are outside the scope of sprinkler listings, listed sprinklers shall 
be permitted to be installed beyond their listing limitations.  The Automatic 
Sprinkler
Systems for Residential Occupancies Handbook has commentary that says in 
situations
where no listed residential sprinklers exist for the application or arrangement 
under question, NFPA 13D allows listed residential sprinklers to be installed 
beyond
their listing limitations with the approval of the authority having 
jurisdiction.
Residential sprinklers can be used beyond the scope of their listing, provided 
the
designer develops and appropriately justifies a design and installation approach
 that identifies the number of sprinklers expected to operate during a fire.  
The
commentary goes on to say that since NFPA 13D mandates the use of residential 
sprinklers
for the majority of areas in one- and two-family dwellings, some leniency was 
provided
to help address the installation of sprinklers in the wide array of ceiling 
arrangements
encountered in the field.  For life safety purposes in one- and two family 
dwellings,
the Committee on Residential Sprinkler Systems believes that it is more 
beneficial
to use residential sprinklers beyond their listing than it is to use other types
 of sprinklers.  Regarding the number of sprinklers to calculate, the standard 
requires
up to two design sprinklers within a compartment.  There are new limitations 
placed
on compartment features, depending upon the situation in Section 10.2.1.  This 
section
does not address a barrel shaped ceiling.  As such, if one or two sprinklers 
protect
compartments with barrel shaped ceilings, only the flow from those sprinklers 
are
considered.  If the compartment with a barrel shaped ceiling has more than two 
sprinklers
and does not meet Section 10.2.1, Section 10.2.4 indicates that the number of 
sprinklers
in the design area shall be determined in consultation with the authority having
 jurisdiction as appropriate for the conditions.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Call for Trainers

AFSA continues to grow and evolve in response to the needs of our members. As 
training
development continues, we call out to those in our membership 'family' 
(contractors,
manufacturers, designers, etc.) who can serve as trainers: either as instructors
 or as content developers.

If you, or someone you know, are well versed in any (or all) of the following 
areas:
installation, layout, or inspection/testing/maintenance of fire sprinkler 
systems,
and want to teach or develop courses, let us hear from you!

Please visit firesprinkler.org/trainers 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJTTDnUYoB5NuR1IFYJ87DX76YV1Y8OmTLKk0DDliYvExy7DxBGdgG5qXMxQDk1X7uVrdrrpNBLDbsMAImh5GC5VJLuZYIpzHZ7uh7jguZGtT_QJvh2RQ19O1ABWv_D0fGUSDttc9mR4_&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
for more details.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJXn6WRAv5yGwMrhcAqJ8yo0nIxvswkplhHTWTydL-zJ-pKNV_SPHcGIvzh8RuxfOru2YwS3EO-PBDrqw_cROnEO3Oiv-EgIAiG1lmwSnZxXPup5JHhRSRQwp1LhgmxEBwA==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
  Join AFSA 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJXb0gJNCHIGpk-0HHUMhErLKupaUTL-UGmsGsa4CPXeij6s8oye2lj5U8jibWppezKRyYvMP2_gfdsacojdb735RENgaIqfBLPiXmHbzbZpnxFu62BYWNFvbijvFKhFqMIkLT4yI8Q8VyMhJiQ70LFe8hIoPzmIgv2JSD0UW4mIR&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
  Scholarships 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJZkT0C0QbhmeUBR5s4N2xqWmuHoxpyoG2ZzGtGRQMHFZixgfe6GxyfeeMwwHjiuqNUUl83sCxglITkiMclthaG8QOyq_9sAGn-c9wFIaSqp-zrxccnE-hpboy_YOJxNJfA==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJR1ndanB6nKVIh6yt18Ujg_utxZxVpMEeMYNjHLn0lVSTgNRt90kj8mv0Edw5t6nSK938gR9SQjBsh1Q5hlZ03gOeOW9De5Uyw1bq5y6M5ndQHO9O1x9v_mWhIhj8kZQ6AyoFCETaTbNZUiWY9d8eqU1Z4aUYs4HNQ_5qvBgCfAy6IdM1jGrxHk=&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
  Technical Services 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJV5WJ6B9_hxSO7_sllsbqqlaIg36-MapzyT-8eqYAlxA2hD28y0fq62IxOjEYM9OO-CFvdAKWC5C0pXifCURkVCa67nyYqWWKbbJXcmrTG_zt2JW0BrqxyG9-lkzIpPJRDbAFFTmMad096CG0JOSzfWvCzH4WCpTFg==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJZZrJrY2af8EPU7DQSQkoNWsBq59x6pg_ew5nZ4iXaBGhHnaG78ls6CPgbhsjPWTqzcm3icD_w_UaI_-J_CfbyhB2-0rKy7mkCq6qyyBhMMMde2XcOiHsSFSkh5Ywn5escKBVT8A5dg6vI8qlHRHTciuYlQmIl68wnR6tTznqcGDZIAWVWf3RDw1S0nKwIcyFetEEaDqi5AdGCu_DWQ4l6jPAXHPqmKrWI2dzG1z3qkO&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJaV1iZegUxmRcDU--kV35vLmeKCp4X_I4th_k4iDV7jogIgkgL_l-HPdy7-MvWdDXgFut8-UOQyD7h8dfpWuz2oR1ikl3d48MUz6V6jd1QSvU9dlnZYVAYbs80RxRwXNu2DuNu8YNE6JhfCyw_HcKJ-pm_lIn8D38VdITEdmVylcQOx4vpM0YU17p5PCcqcCMA==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJdcDzt4vNvIMgwblrXMpr9Bnw-FsQSHXMIRyCW0BQWMK2NOP-7SrDhXF3uwJSzhCHkUbf_AiwU_7QqzFtCRaUNR2n-51IrQcXlejqPVSNrycGtxl8HFsbdGUtAxrBGExoSDYdi4kFdAj6MgO9773uIA2WVjcMhKByWot-BcO3j7-EmsyUg9XwUY72e6NDsUNww==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJdcDzt4vNvIMGOhWV7o60IlLK_Luf5RYH-mEt3Ib33co0Jm5Oq3lTlWKItNMYIXlNhnehccn6zPkNoZt1at5kc7DC-sOG8EtxRra7XwhGs5WsVFrXbH4BjP8bt9_ZKimGp2Br3puQ4kg&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
July 20-31, 2015
Sold Out!
September 14-25, 2015
November 2-13, 2015

For additional details, register, or view upcoming training, visit the
AFSA Calendar [http://www.firesprinkler.org/events/].
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

SA Cover for TU 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJR1ndanB6nKVCl40Dd474D3o_veDsC89xTBZP5Gi7yv7ycQaYzYZ7XM4LXTJYW35OYM2HIPmXDhvYCrGUhbHYfNA--uaXB1BGV1btVZEc5EVyu0faFEqgPrX2m-ABZ8i5xK6wfEHcNWbePDKC3zPPA6-4wfz1N02vQ==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
Free Subscription
to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJUUqkc38w01n4jHXFxI1zpXzW6tZN3cNLhPvQ6WXkqesbbEaJhzGYF-wYtfHokEy_zsrxOrI_cjNMTOiu5U8nYecsDcphizOgmjgzR-xhwsy8yTFT756R2fNSdoxXRvyOyiPC1FEwX8YOItTKkz_ryMtjW9pcT1YbQ==&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]
AFSA Quality Contractor Recognition 
[http://r20.rs6.net/tn.jsp?f=001N6bzskzH3havW-5Fmmrz7Vj5BFcIf7CCaubsGYLjJrBPA8WxjUgWJTM3bOXuoikcmfN9-_qkE_MAKhetDXy5hwsxw8Qj_NGu81GJevIJ0h3gqSPZJcOdyy8AeLYOLcF8pCAXUAHbw_rzlP-ASCBT-O0AoRD_obFyvVN4U5wMHs2fzJr3j-KmmD9BENyNo60J6k_mNt0Yqiw9KSBUMbn9vDiCHK_JgA92X8I2cbbmZ1uCgXfDasP432YenNeZHeZV&c=w8_ViGZuSxKu9qJMAq6CrzL48MOM8rs2LipFMfKgK_nQPH-2YUReAg==&ch=vc12M1uhaVESKfBiBdSYUsz_cOihihBfpLWv3KpzJhcgabPMcT9HfQ==]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1121273797560

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=a5e56c72-f3db-41d7-9271-1253ee74ae06


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=a5e56c72-f3db-41d7-9271-1253ee74ae06


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to