I do not follow how the set point can be the operating temperature.  How is 
this inputting to the comparator?  Are you proposing some external heat source 
which remains constant at that temperature?  For a loop to function it must 
have a reference that does not change with the controlled parameter.  If this 
is not the case, then the temperature will drift toward one of its limits.

The beauty of positive feedback is that this type of behavior is exactly what 
you desire.  As long as you can reverse the drift direction periodically you 
are in control.

Dave


-----Original Message-----
From: Andrew <andrew...@att.net>
To: vortex-l <vortex-l@eskimo.com>
Sent: Mon, May 27, 2013 2:23 pm
Subject: Re: [Vo]:Re: Constant temperature Operation of ECAT?



Sure, the reference would be the set point, and that's simply the operating 
temperature. Notionally you set this as high as possible, consistent with 
materials integrity and the ability to regulate a strongly 
intrinsically-positive feedback system (the device itself). The idea is that 
you end up with Kp*Kn <= 1, where Kp is the intrinsic positive feedback gain 
(>1, and becoming higher at higher temperature), and Kn is the negative 
feedback gain (<1, representing the characteristics of the active cooling 
system). Of course, it's more complex than that due to first (and higher) order 
time differentials, and an integral term due to stored heat energy, but that's 
the basic proportional rule.
 
Designing that would be fun. The most fun I had in my 40+ engineering career 
was designing industrial robots. Right now, I'm looking for a new job.
 
Andrew
  
----- Original Message ----- 
  
From:   David   Roberson 
  
To: vortex-l@eskimo.com 
  
Sent: Monday, May 27, 2013 10:49 AM
  
Subject: Re: [Vo]:Re: Constant   temperature Operation of ECAT?
  


  
Rossi keeps this information   secret.   It is unfortunate that he does this, 
but that is his   nature.  I would love to see a number of measurements 
associated with his   material, but all questions of that sort are blocked due 
to IP   concerns.
  
 
  
It is frustrating to be kept at arms length from such important and   history 
making knowledge.
  
 
  
You mention active cooling in the context of negative feedback and I   suppose 
that might be somewhat applicable.  Systems can be stabilized by   adding an 
overall negative feedback loop around the process but in this case I   do not 
see how any form of reference temperature can be used to generate an   error 
signal for correction.   Do you detect a reference   upon which this loop would 
act?
  
 
  
Dave
  
 
  
  
  
-----Original   Message-----
From: Andrew <andrew...@att.net>
To: vortex-l   <vortex-l@eskimo.com>
Sent: Mon, May 27, 2013 1:30 pm
Subject: Re:   [Vo]:Re: Constant temperature Operation of ECAT?

  
  
  
OK, thanks for the info - I had not seen those reports. Certainly it is   in 
general expected to happen if it's known that the reaction rate increases   
with temperature. So the trick with active negative feedback (cooling) applied  
 at higher temperature is that this technique holds the promise for much higher 
  COP values. Indeed, an excellently engineered device promises to be very hot, 
  to be under complete temperature control, and to perhaps to generate double   
digit COP values. Assuming that at some point Rossi licences this technology,   
the thermal control and the temperature operating point look like they would   
be key market differentiators.
  
 
  
Do we have data as to how low the temperature can go, and still maintain   
over-unity COP?
  
 
  
Andrew
  
    
-----     Original Message ----- 
    
From:     David     Roberson 
    
To:     vortex-l@eskimo.com 
    
Sent:     Monday, May 27, 2013 10:18 AM
    
Subject:     Re: [Vo]:Re: Constant temperature Operation of ECAT?
    


    
The earlier posts by Rossi on his blog     mention many cases where thermal run 
away happened.  Most of these were     when he was developing the earlier 
versions of his mechanism.  The fact     that thermal run away can occur has 
been common knowledge for a very long     time.
    
 
    
Anytime a positive temperature coefficient is present thermal runaway     is 
possible under certain conditions.  Power transistors are a prime     example 
of this when they self destruct unless the heat sinking is adequate     to 
reduce the thermal resistance so that the positive feedback loop gain is     
below unity.  Rossi has a similar problem to deal with.  In his     case, he is 
using what is normally a problem to his advantage to improve his     COP.  
Without this help he would have a far lower COP.  You get a     COP of 1 for 
free, and much beyond that might result in unstable     operation.  Even 
operating at a COP of 3 has risk of thermal     run away.
    
 
    
Dave
    
    
    
-----Original     Message-----
From: Andrew <andrew...@att.net>
To: vortex-l     <vortex-l@eskimo.com>
Sent: Mon,     May 27, 2013 1:03 pm
Subject: Re: [Vo]:Re: Constant temperature Operation     of ECAT?

    
    
    
Glad we're back in sync. Although there's definite evidence for thermal     
runaway 25 years ago with P&F, with Rossi's kit I'm not so certain. In     
fact, I don't know of a single example. He only got the meltdown when he     
applied continuous power at a level far above that which he uses now.
    
 
    
Andrew
    
      
-----       Original Message ----- 
      
From:       David       Roberson 
      
To:       vortex-l@eskimo.com 
      
Sent:       Monday, May 27, 2013 7:00 AM
      
Subject:       Re: [Vo]:Re: Constant temperature Operation of ECAT?
      


      
I suppose that it would be easier in person to discuss this issue,       but 
that is not available.  Yes, we are on the same page regarding       the 
positive feedback threshold leading to self destruction.
      
 
      
I refer to what you mention as active cooling of the system.  We       have 
discussed this in vortex on several occasions in the past.  I       think that 
it is a winning idea, but so far I have not detected Rossi       putting it 
into his design.  It appears to be a technique that would       allow Rossi to 
force the loop gain back to below unity at an elevated       temperature that 
would normally be beyond recovery with heat input       modulation alone.  This 
should result in a downward retreat of his       temperature excursion and 
looks very promising for high power       operation.
      
 
      
Dave
      
      
      
-----Original       Message-----
From: Andrew <andrew...@att.net>
To: vortex-l       <vortex-l@eskimo.com>
Sent:       Mon, May 27, 2013 1:35 am
Subject: Re: [Vo]:Re: Constant temperature       Operation of ECAT?

      
      
      
      
We are totally at cross-purposes here; if we were in the same room,       this 
crap wouldn't happen. So here's the deal. I'm considering the       scenario 
whereby we operate the heating system to bring the device just       past the 
stable temperature; further heating results in thermal runaway       (at least, 
that's what's claimed for Rossi's device - it actually melted       down due to 
the application of constant heating, but       whatever).
      
 
      
To keep the thing stable when it wants to apply positive feedback to       
itself, we need to apply negative feedback. And hence I began       to discuss 
and describe characteristics desirable of an       active cooling system.
      
 
      
You dig?
      
 
      
        
-----         Original Message ----- 
        
From:         David         Roberson 
        
To:         vortex-l@eskimo.com 
        
Sent:         Sunday, May 26, 2013 5:22 PM
        
Subject:         Re: [Vo]:Re: Constant temperature Operation of ECAT?
        


        
But, we are talking about the         ECAT.  It operates by using positive 
feedback to get high         gain.  You are the one that mentioned a negative 
feedback system         that achieves the same thing.  That is not comparable.  
Stable         operation of negative feedback systems is trivial.  
        
 
        
Think of taking a tunnel diode and         keeping it within the negative 
resistance region without heavy resistive         loading.  The problem is 
similar to that which Rossi         faces.
        
 
        
Dave
        
        
        
-----Original         Message-----
From: Andrew <andrew...@att.net>
To:         vortex-l <vortex-l@eskimo.com>
Sent:         Sun, May 26, 2013 8:14 pm
Subject: Re: [Vo]:Re: Constant temperature         Operation of ECAT?

        
        
        
Of course I'm talking exclusively about a negative feedback         system!! 
        
The positive feedback purportedly occurs internally to the device         
itself.
        
 
        
Andrew
        
          
-----           Original Message ----- 
          
From:           David           Roberson 
          
To:           vortex-l@eskimo.com 
          
Sent:           Sunday, May 26, 2013 5:09 PM
          
Subject:           Re: [Vo]:Re: Constant temperature Operation of ECAT?
          


          
No, there is a large difference           between a negative feedback system 
and a positive feedback           system.  Tell us how to make your temperature 
controller hold a           constant temperature with positive feedback and a 
loop gain of greater           than 1.  If you do, you might find that it 
matches my           model.
          
 
          
Dave
          
          
          
-----Original           Message-----
From: Andrew <andrew...@att.net>
To:           vortex-l <vortex-l@eskimo.com>
Sent:           Sun, May 26, 2013 8:05 pm
Subject: Re: [Vo]:Re: Constant           temperature Operation of ECAT?

          
          
          
See my follow-up on this. There's always going to be a tracking           
error, no matter how sophisticated the regulation algorithm. I think           
the prime objective here is not to have absolutely constant           
temperature per se; rather, it's to guarantee that thermal           runaway 
cannot occur. 
          
 
          
Andrew
          
            
-----             Original Message ----- 
            
From:             David             Roberson 
            
To:             vortex-l@eskimo.com 
            
Sent:             Sunday, May 26, 2013 5:00 PM
            
Subject:             Re: [Vo]:Re: Constant temperature Operation of ECAT?
            


            
How many of these controllers             use positve thermal feedback to keep 
the sink at a constant             temperature?
            
 
            
Dave
            
            
            
-----Original             Message-----
From: Andrew <andrew...@att.net>
To:             vortex-l <vortex-l@eskimo.com>
Sent:             Sun, May 26, 2013 7:52 pm
Subject: [Vo]:Re: Constant temperature             Operation of ECAT?

            
            
            
Seems to me that if active cooling control is used as the only             
control input, thus satisfying the "unplug it!" sceptics (and I'm             
one of them), then it only has a chance of working if there is good             
thermal contact and good thermal conductivity and substantial enough            
 heat capacity in the active cooling implementation. I don't know why           
  this is supposed to be hard. Gaming PC's of the high-end variety use          
   this all the time. Prompt temperature feedback to the cooling pump           
  is all that's needed, plus a simple PID controller. This is             very 
well-known technology.
            
 
            
Andrew
            
              
-----               Original Message ----- 
              
From:               David               Roberson 
              
To:               vortex-l@eskimo.com 
              
Sent:               Sunday, May 26, 2013 4:44 PM
              
Subject:               [Vo]: Constant temperature Operation of ECAT?
              


              
My model demonstrates that               constant temperature operation of the 
ECAT is not going to work               under normal conditions.  The 
relatively high value of COP               when temperature control is used 
depends upon operation in a               positive feedback region.  This can 
be thought of as related               to the question that always arises about 
why the device does not               supply its own drive and therefore run 
continuously in               SSM.
              

Once the loop gain becomes greater than 1, the device               will tend 
to move in the direction that it is currently               heading.  This 
allows it to heat up to a relatively larger               temperature than that 
due to the drive alone.  When rising in               temperature, the device 
begins to put out additional heat, more               with time.  The trick is 
to turn the process around at a good               point before it goes too 
far.  The best turn around               temperature is well defined and shows 
up as a tendency for the               device to continue putting out power at 
a constant rate with               time.  Unfortunately, this exact point would 
be impossible to               achieve while maintaining control.  It is a 
balance between               how long you want the temperature to remain 
nearly constant and               the risk of loosing control.
              

Rossi chose a relatively safe turn around temperature for               the 
last test which caused the COP to drop below his desired value               of 
6.  I suspect he chose this because a COP of 3 well               demonstrates 
that the process is real and also has enough margin               to keep the 
device safe from melt down.  I think I would have               done the same 
under the same constraints.
              

Dave
              

 














Reply via email to