on 22/01/2011 15:35 Arjen de Korte wrote:

Sorry for the confusion. Yes the value hasn't changed, but I didn't expect that to happen. It should however be modifiable through 'upsrw', so that you might be able to set it to a lower value.

In the usbhid-ups driver, the 'ups.delay.(start|shutdown|reboot)' values are driver variables. They are only send to the UPS when you initiate the corresponding command. However, on the APC it seems to be possible (mandatory) to store them in the UPS itself.

So try if you can change this value through upsrw to something like 20 seconds and lower the 'offdelay' value to 30 seconds.

I don't pretend to understand this fully at the moment, the driver.parameter.offdelay is set to 1, as is the ups.delay.shutdown:

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 1
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d

#./clients/upsrw -s ups.delay.shutdown=30 -u apcmon -p pass123 apc1500
OK

This sets it to 30:

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.4
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 230.4
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d

but doesn't affect the initial value of ups.timer.shutdown (90) after the shutdown.return command:

# ./clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
OK

# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: 82
ups.timer.start: 242
ups.vendorid: 051d