Citeren Kevin <bakd...@gmail.com>:
[...]
but doesn't affect the initial value of ups.timer.shutdown (90)
after the shutdown.return command:
# ./clients/upscmd -u apcmon -p pass123 apc1500 shutdown.return
OK
# ./clients/upsc apc1500
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2007/07/07
battery.runtime: 5880
battery.runtime.low: 120
battery.temperature: 32.4
battery.type: PbAc
battery.voltage: 27.0
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Smart-UPS 1000
device.serial: AS0727233122
device.type: ups
driver.name: usbhid-ups
driver.parameter.offdelay: 1
driver.parameter.ondelay: 250
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.6.0
driver.version.data: APC HID 0.95-patched
driver.version.internal: 0.35
input.sensitivity: high
input.voltage: 230.4
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: disabled
ups.delay.shutdown: 30
ups.delay.start: 250
ups.firmware: 652.13.I
ups.firmware.aux: 7.3
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2007/07/07
ups.model: Smart-UPS 1000
ups.productid: 0002
ups.serial: AS0727233122
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: 82
ups.timer.start: 242
ups.vendorid: 051d
Could you try this again with
{ "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10,
"UPS.Output.APCShutdownAfterDelay", NULL, "%.0f", HU_FLAG_SEMI_STATIC,
NULL },
changed to
{ "ups.delay.shutdown", ST_FLAG_RW | ST_FLAG_STRING, 10,
"UPS.Output.APCShutdownAfterDelay", NULL, "%.0f", HU_FLAG_QUICK_POLL,
NULL },
and run this test again? I'm not sure if the value is actually
modified in the UPS. I fear that the HU_FLAG_SEMI_STATIC flag may have
prevented the driver from reading back the value from the UPS.
Best regards, Arjen
--
Please keep list traffic on the list (off-list replies will be rejected)
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@lists.alioth.debian.org
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser