Sorry, I didn't received it... I don't have any REPLBATT message, but when in battery test I have OL CAL status: it would be good to have the result. Anyway I still not receive any email on any test (power cord disconnected and/or reconnected for example)
Does the runtime calibration test alter the values of ups.conf? Or do I have to change it manually? Which would be the right procedure for changing the battery for calibrating NUT (over the manufacturer's suggestions)? Thank you lots, Andrea 2017-06-27 14:50 GMT+02:00 Charles Lepple <clep...@gmail.com>: > On Jun 26, 2017, at 7:03 AM, Andrea de Lutti <adelu...@gmail.com> wrote: > > > > Are there no warnings for battery test? > > not sure if you saw my reply on 2016-06-17: > > Do you mean a notification that a test is in progress, or something for > the results? > > There is the REPLBATT message in upsmon when the battery test fails, but I > don't think the generic Qx protocol supports the RB status flag. > > You could possibly trigger on the OB status and look for the CAL flag in > ups.status as well, but I haven't tried to automate that. > > ^^^ If you run "upsc $UPSNAME ups.status", do you see CAL in the status > string during a battery test? If not, your UPS is not reporting this the > way that the driver expects.