Thanks mates,
as suggested I have added

    runtimecal = 240,100,720,50
    default.battery.voltage.low = 10.4
    default.battery.voltage.high = 13.8 (the actual charging voltage)

In ups.conf

I have also added the startup procedure in rc.local file, everything is
fine...
I have only to make a deep test.

Is there a way to add a NOTIFYMSG value for the battery test?

Thank you lots

Andrea

2017-06-16 14:50 GMT+02:00 Charles Lepple <clep...@gmail.com>:

> On Jun 16, 2017, at 2:20 AM, Andrea de Lutti <adelu...@gmail.com> wrote:
> > Using 'guestimation' (low: -0.866667, high: -1.083333)!
> > Initial battery charge undetermined
> > Driver failed to start (exit status=1)
>
> The "low" and "high" voltages should correspond to the battery voltage
> when it is discharged (LB) and charged, respectively. For a 12V (nominal)
> battery, they should not be less than zero :-)
>
> There is a check for whether the nominal battery voltage is 1, but it
> should be looking for -1. (This has been fixed in nutdrv_qx, but was not
> backported to blazer*)
>
> As Manuel suggested, you can use the "defaults.battery.voltage.low" and
> "defaults.battery.voltage.high" options in ups.conf - there is a bit of a
> chicken-and-egg problem here, but you can still put in approximate values
> (say, 10.4 and 13.0) in order to run the calibration, and then adjust them
> to the actual reported values.
>
>
>