I think the simple email alert is what we are looking for..  No NMS needed.  



From: castarritt 
Sent: Wednesday, May 8, 2024 3:33 PM
To: AnimalFarm Microwave Users Group 
Subject: Re: [AFMUG] SNMP

We've done stuff as ghetto as powering an old wrt54g through the alarm contacts 
and monitoring its IP address to see when it comes up and goes down.  These 
days all of our sites have either an Alpha or ICT UPS or DC shelf that has 
alarm monitoring inputs.

On Wed, May 8, 2024 at 4:30 PM Ken Hohhof <khoh...@kwom.com> wrote:

  As long as you support SMTP AUTH, I think that should be sufficient.  If 
necessary, someone could always create a Gmail account for this purpose.



  Yes, there are some older devices that expect you to set them up as an MTA 
rather than MUA so they can send unauthenticated SMTP on port 25.  That sounds 
like a really bad plan to me unless you time travel back to maybe 1999.  I 
don’t want to be creating SPF and DKIM and DMARC records for a little contact 
monitoring box, and it sounds like a security nightmare.



  From: AF <af-boun...@af.afmug.com> On Behalf Of Forrest Christian (List 
Account)
  Sent: Wednesday, May 8, 2024 4:13 PM
  To: AnimalFarm Microwave Users Group <af@af.afmug.com>
  Subject: Re: [AFMUG] SNMP



  Some devices can be configured to send an email if a contact closes, but the 
way this happens varies between devices.



  My problem with integrating this on the the sitemonitor platform has 
traditionally been that you need a rule system in order to determine when to 
send the email.  I.E. what threshold of voltage, and so on.   This is obviously 
easy in a on/off situation, but not so much in a voltage.   Plus you need 
additional rules so when the voltage is bouncing between 24.0 and 24.1 and you 
have the threshold set at 24.0 you don't get an email every time it flaps to 
24.0.    All of this was impossible to do on the older hardware just because of 
code space limitations.  



  The Base 3 has the resources to do this, but the firmware has not yet been 
completed.  There is a rules engine about 3/4 built for the sitemonitor system, 
how long until it sees the light of day, I don't know at this point.   The 
email itself is somewhat easy but I also need to provide some sort of email 
server resources for those who don't have an email system which will accept 
email from random devices.



  On Wed, May 8, 2024 at 2:55 PM Ken Hohhof <khoh...@kwom.com> wrote:

    Not following how you are going to use SNMP without a monitoring system.

    Packetflux Sitemonitor can turn a contact closure into a 1 or 0 OID that an 
SNMP monitoring system can check at regular intervals, mine mostly polls every 
1 minute. But then you would typically have your NMS send an alert by email or 
text message.

    I tend to monitor analog parameters like voltage or current, then set trip 
points for the NMS to send an informative message. Like UPS input voltage at 
the Podunk site has been below the minimum value of 100 V for more than 2 
minutes.

    ---- Original Message ----
    From: "Chuck McCown via AF" 
    Sent: 5/8/2024 2:41:36 PM
    To: "TJ Trout" , "AnimalFarm Microwave Users Group" 
    Cc: ch...@go-mtc.com
    Subject: Re: [AFMUG] SNMP

    So how do Forrest’s products let you know of an issue?  Traps?



    \Would love to NOT have to have NMS just for this.  





    From: TJ Trout 

    Sent: Wednesday, May 8, 2024 1:35 PM

    To: AnimalFarm Microwave Users Group 

    Cc: Chuck McCown 

    Subject: Re: [AFMUG] SNMP



    Packet flux can do it all too, the base unit can monitor two voltages and 
temp and a few contact closures, if you need more volt inputs or closures you 
add a expansion unit. No email that I'm aware of



    On Wed, May 8, 2024, 12:23?PM Chuck McCown via AF <af@af.afmug.com> wrote:

      No, we have fuse alarms, rectifier, inverter, and other comm equipment 
alarm contacts.  Circuit breaker alarms.  That is why historically I liked the 
netguardian product.  It eats everything.  Monitors DC voltages etc.  Temps







      From: Bill Prince 

      Sent: Wednesday, May 8, 2024 1:13 PM

      To: af@af.afmug.com 

      Subject: Re: [AFMUG] SNMP



      I think if your installed equipment all came from one vendor, there might 
be some way to do their proprietary monitoring solution.

      However, SNMP as flawed as it might be, is the only standard that is 
nearly universal (because some implementations are better than others).



bp<part15sbs{at}gmail{dot}com>On 5/8/2024 11:30 AM, Chuck McCown via AF wrote:

        We are needing to add some monitoring of old fashioned alarm contacts 
in one of our sites.  In the past I used Netguardians.  Not sure what Forrest 
has.  



        Is SNMP still the defacto NMS comm method or are there better more 
modern stuff out there we should be looking at?





        Best Regards,
        Chuck McCown

        McCown Technology Corporation 
        8401 N Commerce Dr
        Lake Point, Utah 84074
        801-250-9503 Office
        435-830-4306 Cell
        www.mccowntech.com
        www.microtrench.pro
        www.terabitnetworks.com




--------------------------------------------------------------------------

      -- 
      AF mailing list
      AF@af.afmug.com
      http://af.afmug.com/mailman/listinfo/af_af.afmug.com

      -- 
      AF mailing list
      AF@af.afmug.com
      http://af.afmug.com/mailman/listinfo/af_af.afmug.com

    -- 
    AF mailing list
    AF@af.afmug.com
    http://af.afmug.com/mailman/listinfo/af_af.afmug.com






  -- 

  - Forrest

  -- 
  AF mailing list
  AF@af.afmug.com
  http://af.afmug.com/mailman/listinfo/af_af.afmug.com



--------------------------------------------------------------------------------
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to