I am still pissed at getting marked wrong on an exam in college.  Freshman EE 
class.   

The question was: What is Power Factor.
My answer: Cosine of the Phase Angle

I was right.  They were wrong.  I was robbed of some points.  Somebody has to 
pay someday...

From: Mark Radabaugh via Af 
Sent: Tuesday, October 28, 2014 9:32 AM
To: af@afmug.com 
Subject: Re: [AFMUG] APC "load in watts"

For what it's worth since most people are not used to power factor (PF)

Power is measured as volts * amps * PF = Watts
VA ratings are volts * amps 

For DC the power factor is effectively 1 and can be ignored (we are talking 
supply power here... you RF guys don't need to go off on a tangent here...).

The current draw of a load does not always track the voltage supplied.   If the 
load is purely resistive (no inductors, no capacitors) then rising voltage and 
current track linearly.  Most AC loads are not purely resistive and the current 
may lag or lead the voltage - meaning the current rise lags behind what would 
be expected for the voltage applied.   The power factor (PF) is the ratio 
between the (expected) current and voltage and it's expressed as a number 
between -1 and 1.    Old switching power supplies have a PF around .8

A 500W, 120V power supply with a PF of 1 draws:  Voltage: 120V,   Current 
(500/120) = 4.16A

A 500W, 120V power supply with a PF of 0.8 draws:  Voltage: 120V, Current 
(500/120/.8) = 5.21A

The power supply with the PF of 0.8 requires considerably more current from the 
UPS than the power supply with a PF of 1 ~ 25% more.

UPS manufacturers rate power supplies based on VA rather than Watts since (take 
your pick here...) they don't have control over the power factor of the 
equipment you are adding, or the VA number is bigger and looks better on the 
box.

You can get more runtime out of your UPS if you pay attention to the power 
factor of the computers you attach to them.   Better power supplies have better 
power factors.   They cost a little bit more but can save you money on your UPS.

Mark

On 10/28/14, 10:35 AM, Robbie Wright via Af wrote:

  Under, about click on UPS. You'll see apparent power rating in VA and real 
power rating in watts. Under status>ups, you should also see output voltage and 
amps so you can figure out watts if you want. It also logs your usage in kWH as 
well. 


  Robbie Wright
  Siuslaw Broadband
  541-902-5101



-- 
Mark Radabaugh 
Amplex

m...@amplex.net  419.837.5015 x 1021

Reply via email to