For about a month at one site during the summer (maybe last year, I don't remember, too much shit in my head), we got a bunch of popped fuses and surge suppressors. Our local 911 dispatch joined the site months before and we didn't have any problems. We finally figured out that the grounding sorta got split. Everything was still interconnected, just not optimally. So we all made sure that everything was tied to a single point, aka R56. No more issues. We do still get some popped fuses once in a while, but that's mostly Chuck's surge suppressors clamping on nearby lightning strikes. I'd rather have that than dead or degraded ethernet ports.

It was also a very wet spring and then things dried out. We've noticed this pattern for >10 years. If the soil is pretty dry for a lot of the year, we lose more gear. Which brings up another point. Up to a couple years ago, we had a site where we'd lose everything 2-3 times per year. The power company came out and ran a load test at our transformer. 20A is all it would do. The ground rod at the pole/transformer was almost completely gone. I think they said there was maybe 2 feet left and they pulled it out by hand. Of course it was probably 40 years old.

On 12/29/2015 10:28 PM, Jaime Solorza wrote:

When I wear my SCADA hat grounding takes a front seat. We take great care to insure we follow sound methodology and take no short cuts. I have shared many posts on how we do it... basically all of it hinges of Franklin method. Those who know me, know I don't pull punches...if we were getting hit allot I would post it. Yes we have had hits and lost equipment but it is extremely rare. Consider that one SCADA network alone has over 500 sites with elevated tanks, towers and masts all with yagis, sectored and omni antennas with heliax cabling. Wisps around here get more hits. I will share some links you might find useful.

On Dec 29, 2015 8:08 PM, "Faisal Imtiaz" <fai...@snappytelecom.net <mailto:fai...@snappytelecom.net>> wrote:

    I thought about commenting, walked away,  but decided to comment
    at the risk of offending someone, but it would be worth it if the
    point being made and the information being shared was understood
    properly..

    So here goes... Joshaven took the time and provided a farily
    accurate, detailed post on how to do grounding properly, and the
    potential issues when it is not proper. There is a lot of good
    information in there.....

    Glen I don't know if you realize what you did with your replies
    .... while sounding dismissive you actually have described the
    exact thing that Joshaven was trying to point out, as to what
    happens when grounding is not proper !

    'Grounding' is not just running some copper wires to be visually
    satisfying.... your statement about  'it is grounded pretty
    well...'  followed by .. I have lost equipment there is an
    Oxymoron....

    Grounding when done correctly will protect your equipment from
    having the type of damage you are describing.... and yes there are
    some ways to measure and determine if your grounding is proper !


    BTW, Audio affects of a Lightning strike,  shaking stuff etc etc
    is due to sound waves generated.. (sort of a mini explosion)...
    makes for great sound effect, but has nothing to do with
    electrical damage to equipment.

    :)


    Faisal Imtiaz
    Snappy Internet & Telecom
    7266 SW 48 Street
    Miami, FL 33155
    Tel: 305 663 5518 x 232 <tel:305%20663%205518%20x%20232>

    Help-desk: (305)663-5518 <tel:%28305%29663-5518> Option 2 or
    Email: supp...@snappytelecom.net

    ------------------------------------------------------------------------

        *From: *"Glen Waldrop" <gwl...@cngwireless.net
        <mailto:gwl...@cngwireless.net>>
        *To: *af@afmug.com <mailto:af@afmug.com>
        *Sent: *Tuesday, December 29, 2015 6:02:24 PM
        *Subject: *Re: [AFMUG] WISP insurance

        Forgot to mention, this was one hell of a storm.

        Lightning from *several* miles away shook my home enough that
        the dishes rattled, the TV moved, cabinet doors opened and
        closed, etc, for upwards of 45 seconds.

        I’m honestly surprised we only lost one tower in that storm. I
        was preparing myself for putting up at least a couple of
        replacement towers over my Christmas break instead of goofing
        with the wife and kids. We got lucky and only lost some
        electronics.
        *From:* Glen Waldrop <mailto:gwl...@cngwireless.net>
        *Sent:* Tuesday, December 29, 2015 4:57 PM
        *To:* af@afmug.com <mailto:af@afmug.com>
        *Subject:* Re: [AFMUG] WISP insurance
        It is grounded pretty well, couple of ground rods, tower is
        grounded and the copper goes to the top, tallest point for
        quite a ways out there. The strike also blew out the
        neighboring transformer (didn’t hit my equipment directly).

        I have not been tying in my electrical ground with my tower
        ground. I do believe I’m about to change that.
        I do have a few other towers where the electrical ground is
        tied into the tower ground which is also tied to a copper wire
        (6 or 8, depending on what I had at the time) the entire
        length of the tower, bolted to the tower at the top and bottom.

        Those have also been struck.

        One of my most recent ones ran up the ethernet cable, fried
        the equipment at the top. POE on the ground survived, UPS
        survived and the surge suppressor (10/100M fusible link
        essentially) survived. The only radio to survive the strike
        was the only one I had forgotten to install a suppressor on.
        They were all replaced of course. The only equipment I’ve seen
        survive an actual lightning strike without a hiccup is the
        RB600. Everything else seems to die within 6 months.

        It appears the surge went through the ground (which we’ve gone
        over several times) into the surge suppressor, into the
        ethernet and blew out the radios.

        Any speculation on that would be awesome. The only thing that
        makes sense is that maybe the static was close enough to hit
        the electrical ground and go up the tower, but we’ve checked
        the ground rods and copper, bolts, etc.
        *From:* Joshaven Mailing Lists <mailto:lis...@joshaven.com>
        *Sent:* Tuesday, December 29, 2015 1:18 PM
        *To:* af@afmug.com <mailto:af@afmug.com>
        *Subject:* Re: [AFMUG] WISP insurance
        Kinda off topic... Insurance of another type (avoidance)
        I often find locations where the grounds are hooked up to the
        tower ground which includes one or more ground rods… but what
        often goes unrealized is that the system is also grounded to
        another system through the utility company… and the tower and
        the utility company may not be properly bonded.  So the
        lightning finds the big tower, and thinking it is a lightning
        rod… uses some of the path to ground through rods at the base
        of the tower but then also uses the path through the equipment
        to get to the power utility ground…. and pop goes the radio
        and router and such… Just don’t be that guy that connects the
        big lightening rod to the utility power ground through your
        router...
        Your equipment should be surviving lightning strikes.  Large
        towers can be struck multiple times per month and equipment
        can be on them for years without any damage at all.  The fact
        that you lost equipment says that the strike was either direct
        to your equipment or you have a grounding issue that made your
        equipment a better path to ground.
        At some sites commercial radio engineers will even bring in a
        beaded cable from the tower and spread it across the floor to
        set all equipment on just to be sure that the ground panes are
        entirely bonded.  The reason that equipment blows is that the
difference in positive to negative current is out of range. When you get a lightning strike and things are not well bonded
        then you can have variances between grounds in the order of
        thousands of volts which will make your equipment pop like a
        fire cracker…  if your ground is at 10,000v (relative to an
        average earth voltage) and your equipment is at 10,024v then
        the potential between them is 24v.  It is like a bird setting
        on a high voltage line… somehow they don’t “feel” the high
        voltage… The trick to surviving a lightning strike is to bond
        all grounds well so ground is constant and then to have your
        power level referenced from that ground.  This way if the
        earth ground or the tower ground or anything else has a sudden
        change then your equipment changes with it and remains
        relatively the same.  After bonding your grounds properly so
        that you don’t end up with thousands of volts difference
        between two grounds like your power company ground and the
        tower that your equipment is mounted to… then you can install
        good surge equipment that will handle current overages in the
        event that you need it.
        The thing to keep in mind when grounding your equipment is
        that you don’t want your equipment to experience a situation
        like 0v for negative, 24v for positive and 50,000v for
        ground.  If your equipment ground plane floats with a strike
        then it won’t even know that it experienced a surge.  Just
        like a boat going over shallower and deeper water — who knew
        unless they had a fish finder running?
        During a strike, you don’t want a 5,000v on the utility ground
        while you have a 25,000v on the tower… If the cable between
        the two (or patch of earth between rods) won’t handle the
        surge or the impedance is too high then your equipment will
        possibly have two grounds with two very different power levels
        so the power will transfer from your shielded cable through
        your router chassis to the utility power until a something
        pops.  The bottom line make the tower, earth, & utility power
        all the same and properly ground your equipment to that and
        you’ll survive most strikes perfectly fine.
        if you want some good reading google the terms: “copper.org
        <http://copper.org> lightning”  they have some great write-ups
        with pictures of the good, bad and ugly.
        Sincerely,
        Joshaven Potter
        Google Hangouts: j...@g2wireless.co <mailto:j...@g2wireless.co>
        Cell & SMS: 1-517-607-9370 <tel:1-517-607-9370>
        supp...@joshaven.com <mailto:supp...@joshaven.com>

            On Dec 27, 2015, at 10:31 PM, Craig House
            <cr...@totalhighspeed.net
            <mailto:cr...@totalhighspeed.net>> wrote:
            2 in a year?  We had 7 last night.

            Sent from my iPhone

            On Dec 27, 2015, at 21:22, Glen Waldrop
            <gwl...@cngwireless.net <mailto:gwl...@cngwireless.net>>
            wrote:

                We’ve had another lightning strike, at least the
                second one this year.

                I’ve got this feeling that our insurance company is
                probably going to start to get a little difficult in
                the near future.

                Who do you guys recommend?

                I’ve read about a few that cover everything, CPE,
                tower equipment, towers, labor, etc... I imagine those
                probably cost roughly what we bring in a year, but...
                Thanks guys.



Reply via email to