I have always believed most surges come in on the power, not via the tower.  
But the tower and building grounding are where they are looking to go and once 
they get into a weak grounding circuit they hit everything.

From: Faisal Imtiaz 
Sent: Wednesday, December 30, 2015 8:25 AM
To: af@afmug.com 
Subject: Re: [AFMUG] WISP insurance

one of the most classic examples of a 'split ground' situation is when you 
loose gear with rain during hot days (first rains after dry season). Because 
there is rain involved most folks chalk this off to 'Lightning' ... in reality 
it is not, it is due to Tower Ground, Bldg Ground and Power Ground being at a 
different potential causing current to flow thru the ground wires etc.

:)

Faisal Imtiaz
Snappy Internet & Telecom
7266 SW 48 Street
Miami, FL 33155
Tel: 305 663 5518 x 232

Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net


--------------------------------------------------------------------------------

  From: "George Skorup" <geo...@cbcast.com>
  To: af@afmug.com
  Sent: Wednesday, December 30, 2015 12:15:33 AM
  Subject: Re: [AFMUG] WISP insurance

  For about a month at one site during the summer (maybe last year, I don't 
remember, too much shit in my head), we got a bunch of popped fuses and surge 
suppressors. Our local 911 dispatch joined the site months before and we didn't 
have any problems. We finally figured out that the grounding sorta got split. 
Everything was still interconnected, just not optimally. So we all made sure 
that everything was tied to a single point, aka R56. No more issues. We do 
still get some popped fuses once in a while, but that's mostly Chuck's surge 
suppressors clamping on nearby lightning strikes. I'd rather have that than 
dead or degraded ethernet ports.

  It was also a very wet spring and then things dried out. We've noticed this 
pattern for >10 years. If the soil is pretty dry for a lot of the year, we lose 
more gear. Which brings up another point. Up to a couple years ago, we had a 
site where we'd lose everything 2-3 times per year. The power company came out 
and ran a load test at our transformer. 20A is all it would do. The ground rod 
at the pole/transformer was almost completely gone. I think they said there was 
maybe 2 feet left and they pulled it out by hand. Of course it was probably 40 
years old.


  On 12/29/2015 10:28 PM, Jaime Solorza wrote:

    When I wear  my SCADA hat grounding takes a front seat.   We take great 
care to insure we follow sound methodology and take no short cuts.  I have 
shared many posts on how we do it... basically all of it hinges of Franklin 
method.  Those who know me, know I don't pull punches...if we were getting hit 
allot I would post it.  Yes we have had hits and lost equipment but it is 
extremely rare. Consider that one SCADA network alone  has over 500 sites with 
elevated tanks, towers and masts all with yagis, sectored and omni antennas 
with heliax cabling.  Wisps around here get more hits.  I will share some links 
you might find useful. 

    On Dec 29, 2015 8:08 PM, "Faisal Imtiaz" <fai...@snappytelecom.net> wrote:

      I thought about commenting, walked away,  but decided to comment at the 
risk of offending someone, but it would be worth it if the point being made and 
the information being shared was understood properly..

      So here goes... Joshaven took the time and provided a farily accurate, 
detailed post on how to do grounding properly, and the potential issues when it 
is not proper. There is a lot of good information in there.....

      Glen I don't know if you realize what you did with your replies .... 
while sounding dismissive you actually have described the exact thing that 
Joshaven was trying to point out, as to what happens when grounding is not 
proper !

      'Grounding' is not just running some copper wires to be visually 
satisfying.... your statement about  'it is grounded pretty well...'  followed 
by .. I have lost equipment there is an Oxymoron....

      Grounding when done correctly will protect your equipment from having the 
type of damage you are describing.... and yes there are some ways to measure 
and determine if your grounding is proper !


      BTW, Audio affects of a Lightning strike,  shaking stuff etc etc is due 
to sound waves generated.. (sort of a mini explosion)... makes for great sound 
effect, but has nothing to do with electrical damage to equipment.

      :)



      Faisal Imtiaz
      Snappy Internet & Telecom
      7266 SW 48 Street
      Miami, FL 33155
      Tel: 305 663 5518 x 232

      Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net


--------------------------------------------------------------------------

        From: "Glen Waldrop" <gwl...@cngwireless.net>
        To: af@afmug.com
        Sent: Tuesday, December 29, 2015 6:02:24 PM
        Subject: Re: [AFMUG] WISP insurance

        Forgot to mention, this was one hell of a storm.

        Lightning from *several* miles away shook my home enough that the 
dishes rattled, the TV moved, cabinet doors opened and closed, etc, for upwards 
of 45 seconds.

        I’m honestly surprised we only lost one tower in that storm. I was 
preparing myself for putting up at least a couple of replacement towers over my 
Christmas break instead of goofing with the wife and kids. We got lucky and 
only lost some electronics.



        From: Glen Waldrop
        Sent: Tuesday, December 29, 2015 4:57 PM
        To: af@afmug.com
        Subject: Re: [AFMUG] WISP insurance

        It is grounded pretty well, couple of ground rods, tower is grounded 
and the copper goes to the top, tallest point for quite a ways out there. The 
strike also blew out the neighboring transformer (didn’t hit my equipment 
directly).

        I have not been tying in my electrical ground with my tower ground. I 
do believe I’m about to change that.

        I do have a few other towers where the electrical ground is tied into 
the tower ground which is also tied to a copper wire (6 or 8, depending on what 
I had at the time) the entire length of the tower, bolted to the tower at the 
top and bottom.

        Those have also been struck.

        One of my most recent ones ran up the ethernet cable, fried the 
equipment at the top. POE on the ground survived, UPS survived and the surge 
suppressor (10/100M fusible link essentially) survived. The only radio to 
survive the strike was the only one I had forgotten to install a suppressor on. 
They were all replaced of course. The only equipment I’ve seen survive an 
actual lightning strike without a hiccup is the RB600. Everything else seems to 
die within 6 months.

        It appears the surge went through the ground (which we’ve gone over 
several times) into the surge suppressor, into the ethernet and blew out the 
radios.

        Any speculation on that would be awesome. The only thing that makes 
sense is that maybe the static was close enough to hit the electrical ground 
and go up the tower, but we’ve checked the ground rods and copper, bolts, etc.




        From: Joshaven Mailing Lists
        Sent: Tuesday, December 29, 2015 1:18 PM
        To: af@afmug.com
        Subject: Re: [AFMUG] WISP insurance

        Kinda off topic... Insurance of another type (avoidance)

        I often find locations where the grounds are hooked up to the tower 
ground which includes one or more ground rods… but what often goes unrealized 
is that the system is also grounded to another system through the utility 
company… and the tower and the utility company may not be properly bonded.  So 
the lightning finds the big tower, and thinking it is a lightning rod… uses 
some of the path to ground through rods at the base of the tower but then also 
uses the path through the equipment to get to the power utility ground…. and 
pop goes the radio and router and such… Just don’t be that guy that connects 
the big lightening rod to the utility power ground through your router...


        Your equipment should be surviving lightning strikes.  Large towers can 
be struck multiple times per month and equipment can be on them for years 
without any damage at all.  The fact that you lost equipment says that the 
strike was either direct to your equipment or you have a grounding issue that 
made your equipment a better path to ground.

        At some sites commercial radio engineers will even bring in a beaded 
cable from the tower and spread it across the floor to set all equipment on 
just to be sure that the ground panes are entirely bonded.  The reason that 
equipment blows is that the difference in positive to negative current is out 
of range.  When you get a lightning strike and things are not well bonded then 
you can have variances between grounds in the order of thousands of volts which 
will make your equipment pop like a fire cracker…  if your ground is at 10,000v 
(relative to an average earth voltage) and your equipment is at 10,024v then 
the potential between them is 24v.  It is like a bird setting on a high voltage 
line… somehow they don’t “feel” the high voltage… The trick to surviving a 
lightning strike is to bond all grounds well so ground is constant and then to 
have your power level referenced from that ground.  This way if the earth 
ground or the tower ground or anything else has a sudden change then your 
equipment changes with it and remains relatively the same.  After bonding your 
grounds properly so that you don’t end up with thousands of volts difference 
between two grounds like your power company ground and the tower that your 
equipment is mounted to… then you can install good surge equipment that will 
handle current overages in the event that you need it.

        The thing to keep in mind when grounding your equipment is that you 
don’t want your equipment to experience a situation like 0v for negative, 24v 
for positive and 50,000v for ground.  If your equipment ground plane floats 
with a strike then it won’t even know that it experienced a surge.  Just like a 
boat going over shallower and deeper water — who knew unless they had a fish 
finder running? 

        During a strike, you don’t want a 5,000v on the utility ground while 
you have a 25,000v on the tower… If the cable between the two (or patch of 
earth between rods) won’t handle the surge or the impedance is too high then 
your equipment will possibly have two grounds with two very different power 
levels so the power will transfer from your shielded cable through your router 
chassis to the utility power until a something pops.  The bottom line make the 
tower, earth, & utility power all the same and properly ground your equipment 
to that and you’ll survive most strikes perfectly fine.

        if you want some good reading google the terms: “copper.org lightning”  
they have some great write-ups with pictures of the good, bad and ugly.

        Sincerely,
        Joshaven Potter
        Google Hangouts: j...@g2wireless.co
        Cell & SMS: 1-517-607-9370
        supp...@joshaven.com

          On Dec 27, 2015, at 10:31 PM, Craig House <cr...@totalhighspeed.net> 
wrote:

          2 in a year?  We had 7 last night.   

          Sent from my iPhone

          On Dec 27, 2015, at 21:22, Glen Waldrop <gwl...@cngwireless.net> 
wrote:


            We’ve had another lightning strike, at least the second one this 
year.

            I’ve got this feeling that our insurance company is probably going 
to start to get a little difficult in the near future.

            Who do you guys recommend?

            I’ve read about a few that cover everything, CPE, tower equipment, 
towers, labor, etc... I imagine those probably cost roughly what we bring in a 
year, but...

            Thanks guys.







Reply via email to