There is a ground testing method called the “decline of potential” or “fall of 
potential”.  You can do it with three ground rods, 100’ of cat 5 and a car 
battery.  In any event, you measure the resistance of your grounding systems.  
If it is not low enough you keep adding ground rods until it is.

I have had to do this test for mining operations to make MSHA happy.  

Fluke makes a nice special meter for this but you really don’t need it if you 
can measure volts, amps and have a car battery somewhere nearby.

http://www.fluke.com/fluke/inen/solutions/earthground/fall-of-potential

From: Joshaven Mailing Lists 
Sent: Wednesday, December 30, 2015 10:28 AM
To: af@afmug.com 
Subject: Re: [AFMUG] WISP insurance

This is good stuff.   When replying I was worried that I was gonna get smeared 
for being that little voice in the background that keeps bringing up the 
grounding discussion.  It seems to always be the story that operators already 
have things grounded “properly” yet keep getting destroyed by surges.  I would 
say that almost every tower I have visited has been poorly grounded.  A friend 
of mine who travels the country fixing issues for AM, FM & TV stations says the 
number one issue is grounding.  (I’ve picked his brain quite a lot to validate 
my opinions on this issue and owe much of my understanding to him.)  
Interestingly he also says that in some cases he has had to drive a well into 
the water table to get an adequate ground to fix sensitive locations.  So if 
your gauge of proper grounding stops at a 10’ rod next to the tower and you are 
still having problems then don’t dismiss the grounding question too easily.  
10’ into a layer of dry sand won’t fix your issue especially if you have split 
grounds like discussed below. 

Sincerely,
Joshaven Potter
Google Hangouts: j...@g2wireless.co
Cell & SMS: 1-517-607-9370
supp...@joshaven.com




  On Dec 30, 2015, at 12:06 PM, Chuck McCown <ch...@wbmfg.com> wrote:

  You have two or more grounding circuits that are not bonded together properly.
  Say one circuit for the tower and radio gear that goes into some ground rods 
and then the power company with their neutral and ground circuit.  If those two 
are not tied together with a very low impedance heavy duty connection you will 
generate a large voltage difference during strikes.

  I prefer the PANI grounding system that the telco world uses.
  Combine that with a halo /franklin system and I really do not know how much 
better you can do it.
  Perhaps put up some ground towers like NASA does surrounding the space craft 
on the launch pad.

  -----Original Message----- From: Jay Weekley
  Sent: Wednesday, December 30, 2015 9:53 AM
  To: af@afmug.com
  Subject: Re: [AFMUG] WISP insurance

  What is split grounding?

  Faisal Imtiaz wrote:

    one of the most classic examples of a 'split ground' situation is when you 
loose gear with rain during hot days (first rains after dry season). Because 
there is rain involved most folks chalk this off to 'Lightning' ... in reality 
it is not, it is due to Tower Ground, Bldg Ground and Power Ground being at a 
different potential causing current to flow thru the ground wires etc.

    :)

    Faisal Imtiaz
    Snappy Internet & Telecom
    7266 SW 48 Street
    Miami, FL 33155
    Tel: 305 663 5518 x 232

    Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net

    ------------------------------------------------------------------------

       *From: *"George Skorup" <geo...@cbcast.com>
       *To: *af@afmug.com
       *Sent: *Wednesday, December 30, 2015 12:15:33 AM
       *Subject: *Re: [AFMUG] WISP insurance

       For about a month at one site during the summer (maybe last year,
       I don't remember, too much shit in my head), we got a bunch of
       popped fuses and surge suppressors. Our local 911 dispatch joined
       the site months before and we didn't have any problems. We finally
       figured out that the grounding sorta got split. Everything was
       still interconnected, just not optimally. So we all made sure that
       everything was tied to a single point, aka R56. No more issues. We
       do still get some popped fuses once in a while, but that's mostly
       Chuck's surge suppressors clamping on nearby lightning strikes.
       I'd rather have that than dead or degraded ethernet ports.

       It was also a very wet spring and then things dried out. We've
       noticed this pattern for >10 years. If the soil is pretty dry for
       a lot of the year, we lose more gear. Which brings up another
       point. Up to a couple years ago, we had a site where we'd lose
       everything 2-3 times per year. The power company came out and ran
       a load test at our transformer. 20A is all it would do. The ground
       rod at the pole/transformer was almost completely gone. I think
       they said there was maybe 2 feet left and they pulled it out by
       hand. Of course it was probably 40 years old.

       On 12/29/2015 10:28 PM, Jaime Solorza wrote:

           When I wear  my SCADA hat grounding takes a front seat.   We
           take great care to insure we follow sound methodology and take
           no short cuts.  I have shared many posts on how we do it...
           basically all of it hinges of Franklin method.  Those who know
           me, know I don't pull punches...if we were getting hit allot I
           would post it.  Yes we have had hits and lost equipment but it
           is extremely rare. Consider that one SCADA network alone has
           over 500 sites with elevated tanks, towers and masts all with
           yagis, sectored and omni antennas with heliax cabling.  Wisps
           around here get more hits.  I will share some links you might
           find useful.

           On Dec 29, 2015 8:08 PM, "Faisal Imtiaz"
           <fai...@snappytelecom.net <mailto:fai...@snappytelecom.net>>
           wrote:

               I thought about commenting, walked away,  but decided to
               comment at the risk of offending someone, but it would be
               worth it if the point being made and the information being
               shared was understood properly..

               So here goes... Joshaven took the time and provided a
               farily accurate, detailed post on how to do grounding
               properly, and the potential issues when it is not proper.
               There is a lot of good information in there.....

               Glen I don't know if you realize what you did with your
               replies .... while sounding dismissive you actually have
               described the exact thing that Joshaven was trying to
               point out, as to what happens when grounding is not proper !

               'Grounding' is not just running some copper wires to be
               visually satisfying.... your statement about  'it is
               grounded pretty well...'  followed by .. I have lost
               equipment there is an Oxymoron....

               Grounding when done correctly will protect your equipment
               from having the type of damage you are describing.... and
               yes there are some ways to measure and determine if your
               grounding is proper !


               BTW, Audio affects of a Lightning strike,  shaking stuff
               etc etc is due to sound waves generated.. (sort of a mini
               explosion)... makes for great sound effect, but has
               nothing to do with electrical damage to equipment.

               :)


               Faisal Imtiaz
               Snappy Internet & Telecom
               7266 SW 48 Street
               Miami, FL 33155
               Tel: 305 663 5518 x 232 <tel:305%20663%205518%20x%20232>

               Help-desk: (305)663-5518 <tel:%28305%29663-5518> Option 2
               or Email: supp...@snappytelecom.net

               
------------------------------------------------------------------------

                   *From: *"Glen Waldrop" <gwl...@cngwireless.net
                   <mailto:gwl...@cngwireless.net>>
                   *To: *af@afmug.com <mailto:af@afmug.com>
                   *Sent: *Tuesday, December 29, 2015 6:02:24 PM
                   *Subject: *Re: [AFMUG] WISP insurance

                   Forgot to mention, this was one hell of a storm.

                   Lightning from *several* miles away shook my home
                   enough that the dishes rattled, the TV moved, cabinet
                   doors opened and closed, etc, for upwards of 45 seconds.

                   I’m honestly surprised we only lost one tower in that
                   storm. I was preparing myself for putting up at least
                   a couple of replacement towers over my Christmas break
                   instead of goofing with the wife and kids. We got
                   lucky and only lost some electronics.
                   *From:* Glen Waldrop <mailto:gwl...@cngwireless.net>
                   *Sent:* Tuesday, December 29, 2015 4:57 PM
                   *To:* af@afmug.com <mailto:af@afmug.com>
                   *Subject:* Re: [AFMUG] WISP insurance
                   It is grounded pretty well, couple of ground rods,
                   tower is grounded and the copper goes to the top,
                   tallest point for quite a ways out there. The strike
                   also blew out the neighboring transformer (didn’t hit
                   my equipment directly).

                   I have not been tying in my electrical ground with my
                   tower ground. I do believe I’m about to change that.
                   I do have a few other towers where the electrical
                   ground is tied into the tower ground which is also
                   tied to a copper wire (6 or 8, depending on what I had
                   at the time) the entire length of the tower, bolted to
                   the tower at the top and bottom.

                   Those have also been struck.

                   One of my most recent ones ran up the ethernet cable,
                   fried the equipment at the top. POE on the ground
                   survived, UPS survived and the surge suppressor
                   (10/100M fusible link essentially) survived. The only
                   radio to survive the strike was the only one I had
                   forgotten to install a suppressor on. They were all
                   replaced of course. The only equipment I’ve seen
                   survive an actual lightning strike without a hiccup is
                   the RB600. Everything else seems to die within 6 months.

                   It appears the surge went through the ground (which
                   we’ve gone over several times) into the surge
                   suppressor, into the ethernet and blew out the radios.

                   Any speculation on that would be awesome. The only
                   thing that makes sense is that maybe the static was
                   close enough to hit the electrical ground and go up
                   the tower, but we’ve checked the ground rods and
                   copper, bolts, etc.
                   *From:* Joshaven Mailing Lists
                   <mailto:lis...@joshaven.com>
                   *Sent:* Tuesday, December 29, 2015 1:18 PM
                   *To:* af@afmug.com
                   *Subject:* Re: [AFMUG] WISP insurance
                   Kinda off topic... Insurance of another type (avoidance)
                   I often find locations where the grounds are hooked up
                   to the tower ground which includes one or more ground
                   rods… but what often goes unrealized is that the
                   system is also grounded to another system through the
                   utility company… and the tower and the utility company
                   may not be properly bonded.  So the lightning finds
                   the big tower, and thinking it is a lightning rod…
                   uses some of the path to ground through rods at the
                   base of the tower but then also uses the path through
                   the equipment to get to the power utility ground…. and
                   pop goes the radio and router and such… Just don’t be
                   that guy that connects the big lightening rod to the
                   utility power ground through your router...
                   Your equipment should be surviving lightning strikes.
                   Large towers can be struck multiple times per month
                   and equipment can be on them for years without any
                   damage at all.  The fact that you lost equipment says
                   that the strike was either direct to your equipment or
                   you have a grounding issue that made your equipment a
                   better path to ground.
                   At some sites commercial radio engineers will even
                   bring in a beaded cable from the tower and spread it
                   across the floor to set all equipment on just to be
                   sure that the ground panes are entirely bonded.  The
                   reason that equipment blows is that the difference in
                   positive to negative current is out of range.  When
                   you get a lightning strike and things are not well
                   bonded then you can have variances between grounds in
                   the order of thousands of volts which will make your
                   equipment pop like a fire cracker…  if your ground is
                   at 10,000v (relative to an average earth voltage) and
                   your equipment is at 10,024v then the potential
                   between them is 24v.  It is like a bird setting on a
                   high voltage line… somehow they don’t “feel” the high
                   voltage… The trick to surviving a lightning strike is
                   to bond all grounds well so ground is constant and
                   then to have your power level referenced from that
                   ground.  This way if the earth ground or the tower
                   ground or anything else has a sudden change then your
                   equipment changes with it and remains relatively the
                   same. After bonding your grounds properly so that you
                   don’t end up with thousands of volts difference
                   between two grounds like your power company ground and
                   the tower that your equipment is mounted to… then you
                   can install good surge equipment that will handle
                   current overages in the event that you need it.
                   The thing to keep in mind when grounding your
                   equipment is that you don’t want your equipment to
                   experience a situation like 0v for negative, 24v for
                   positive and 50,000v for ground.  If your equipment
                   ground plane floats with a strike then it won’t even
                   know that it experienced a surge. Just like a boat
                   going over shallower and deeper water — who knew
                   unless they had a fish finder running?
                   During a strike, you don’t want a 5,000v on the
                   utility ground while you have a 25,000v on the tower…
                   If the cable between the two (or patch of earth
                   between rods) won’t handle the surge or the impedance
                   is too high then your equipment will possibly have two
                   grounds with two very different power levels so the
                   power will transfer from your shielded cable through
                   your router chassis to the utility power until a
                   something pops.  The bottom line make the tower,
                   earth, & utility power all the same and properly
                   ground your equipment to that and you’ll survive most
                   strikes perfectly fine.
                   if you want some good reading google the terms:
                   “copper.org <http://copper.org> lightning”  they have
                   some great write-ups with pictures of the good, bad
                   and ugly.
                   Sincerely,
                   Joshaven Potter
                   Google Hangouts: j...@g2wireless.co
                   Cell & SMS: 1-517-607-9370 <tel:1-517-607-9370>
                   supp...@joshaven.com <mailto:supp...@joshaven.com>

                       On Dec 27, 2015, at 10:31 PM, Craig House
                       <cr...@totalhighspeed.net> wrote:
                       2 in a year?  We had 7 last night.

                       Sent from my iPhone

                       On Dec 27, 2015, at 21:22, Glen Waldrop
                       <gwl...@cngwireless.net> wrote:

                           We’ve had another lightning strike, at least
                           the second one this year.

                           I’ve got this feeling that our insurance
                           company is probably going to start to get a
                           little difficult in the near future.

                           Who do you guys recommend?

                           I’ve read about a few that cover everything,
                           CPE, tower equipment, towers, labor, etc... I
                           imagine those probably cost roughly what we
                           bring in a year, but...
                           Thanks guys.







Reply via email to