That will do just fine for the three rod decline of potential method.  

But I am too cheap.  I just use my trusty old fluke 87, car battery and my hp 
48G calculator.

From: Joshaven Mailing Lists 
Sent: Wednesday, December 30, 2015 11:59 AM
To: af@afmug.com 
Subject: Re: [AFMUG] WISP insurance

Chuck, what is your reaction to this device: 

http://www.amazon.com/gp/product/B00390G3YA?psc=1&redirect=true&ref_=ox_sc_sfl_title_3&smid=ATVPDKIKX0DER


I’ve been thinking about purchasing it hoping that it will be a nice 
inexpensive miens of measuring the fall off potential… It’s been setting in my 
cart for a while cause I’ve been getting by with what I already have which 
doesn’t include a proper fall off tester.

Sincerely,
Joshaven Potter
Google Hangouts: j...@g2wireless.co
Cell & SMS: 1-517-607-9370
supp...@joshaven.com




  On Dec 30, 2015, at 1:01 PM, <ch...@wbmfg.com> <ch...@wbmfg.com> wrote:

  There is a ground testing method called the “decline of potential” or “fall 
of potential”.  You can do it with three ground rods, 100’ of cat 5 and a car 
battery.  In any event, you measure the resistance of your grounding systems.  
If it is not low enough you keep adding ground rods until it is.

  I have had to do this test for mining operations to make MSHA happy.  

  Fluke makes a nice special meter for this but you really don’t need it if you 
can measure volts, amps and have a car battery somewhere nearby.

  http://www.fluke.com/fluke/inen/solutions/earthground/fall-of-potential

  From: Joshaven Mailing Lists 
  Sent: Wednesday, December 30, 2015 10:28 AM
  To: af@afmug.com 
  Subject: Re: [AFMUG] WISP insurance

  This is good stuff.   When replying I was worried that I was gonna get 
smeared for being that little voice in the background that keeps bringing up 
the grounding discussion.  It seems to always be the story that operators 
already have things grounded “properly” yet keep getting destroyed by surges.  
I would say that almost every tower I have visited has been poorly grounded.  A 
friend of mine who travels the country fixing issues for AM, FM & TV stations 
says the number one issue is grounding.  (I’ve picked his brain quite a lot to 
validate my opinions on this issue and owe much of my understanding to him.)  
Interestingly he also says that in some cases he has had to drive a well into 
the water table to get an adequate ground to fix sensitive locations.  So if 
your gauge of proper grounding stops at a 10’ rod next to the tower and you are 
still having problems then don’t dismiss the grounding question too easily.  
10’ into a layer of dry sand won’t fix your issue especially if you have split 
grounds like discussed below. 

  Sincerely,
  Joshaven Potter
  Google Hangouts: j...@g2wireless.co
  Cell & SMS: 1-517-607-9370
  supp...@joshaven.com




    On Dec 30, 2015, at 12:06 PM, Chuck McCown <ch...@wbmfg.com> wrote:

    You have two or more grounding circuits that are not bonded together 
properly.
    Say one circuit for the tower and radio gear that goes into some ground 
rods and then the power company with their neutral and ground circuit.  If 
those two are not tied together with a very low impedance heavy duty connection 
you will generate a large voltage difference during strikes.

    I prefer the PANI grounding system that the telco world uses.
    Combine that with a halo /franklin system and I really do not know how much 
better you can do it.
    Perhaps put up some ground towers like NASA does surrounding the space 
craft on the launch pad.

    -----Original Message----- From: Jay Weekley
    Sent: Wednesday, December 30, 2015 9:53 AM
    To: af@afmug.com
    Subject: Re: [AFMUG] WISP insurance

    What is split grounding?

    Faisal Imtiaz wrote:

      one of the most classic examples of a 'split ground' situation is when 
you loose gear with rain during hot days (first rains after dry season). 
Because there is rain involved most folks chalk this off to 'Lightning' ... in 
reality it is not, it is due to Tower Ground, Bldg Ground and Power Ground 
being at a different potential causing current to flow thru the ground wires 
etc.

      :)

      Faisal Imtiaz
      Snappy Internet & Telecom
      7266 SW 48 Street
      Miami, FL 33155
      Tel: 305 663 5518 x 232

      Help-desk: (305)663-5518 Option 2 or Email: supp...@snappytelecom.net

      ------------------------------------------------------------------------

         *From: *"George Skorup" <geo...@cbcast.com>
         *To: *af@afmug.com
         *Sent: *Wednesday, December 30, 2015 12:15:33 AM
         *Subject: *Re: [AFMUG] WISP insurance

         For about a month at one site during the summer (maybe last year,
         I don't remember, too much shit in my head), we got a bunch of
         popped fuses and surge suppressors. Our local 911 dispatch joined
         the site months before and we didn't have any problems. We finally
         figured out that the grounding sorta got split. Everything was
         still interconnected, just not optimally. So we all made sure that
         everything was tied to a single point, aka R56. No more issues. We
         do still get some popped fuses once in a while, but that's mostly
         Chuck's surge suppressors clamping on nearby lightning strikes.
         I'd rather have that than dead or degraded ethernet ports.

         It was also a very wet spring and then things dried out. We've
         noticed this pattern for >10 years. If the soil is pretty dry for
         a lot of the year, we lose more gear. Which brings up another
         point. Up to a couple years ago, we had a site where we'd lose
         everything 2-3 times per year. The power company came out and ran
         a load test at our transformer. 20A is all it would do. The ground
         rod at the pole/transformer was almost completely gone. I think
         they said there was maybe 2 feet left and they pulled it out by
         hand. Of course it was probably 40 years old.

         On 12/29/2015 10:28 PM, Jaime Solorza wrote:

             When I wear  my SCADA hat grounding takes a front seat.   We
             take great care to insure we follow sound methodology and take
             no short cuts.  I have shared many posts on how we do it...
             basically all of it hinges of Franklin method.  Those who know
             me, know I don't pull punches...if we were getting hit allot I
             would post it.  Yes we have had hits and lost equipment but it
             is extremely rare. Consider that one SCADA network alone has
             over 500 sites with elevated tanks, towers and masts all with
             yagis, sectored and omni antennas with heliax cabling.  Wisps
             around here get more hits.  I will share some links you might
             find useful.

             On Dec 29, 2015 8:08 PM, "Faisal Imtiaz"
             <fai...@snappytelecom.net <mailto:fai...@snappytelecom.net>>
             wrote:

                 I thought about commenting, walked away,  but decided to
                 comment at the risk of offending someone, but it would be
                 worth it if the point being made and the information being
                 shared was understood properly..

                 So here goes... Joshaven took the time and provided a
                 farily accurate, detailed post on how to do grounding
                 properly, and the potential issues when it is not proper.
                 There is a lot of good information in there.....

                 Glen I don't know if you realize what you did with your
                 replies .... while sounding dismissive you actually have
                 described the exact thing that Joshaven was trying to
                 point out, as to what happens when grounding is not proper !

                 'Grounding' is not just running some copper wires to be
                 visually satisfying.... your statement about  'it is
                 grounded pretty well...'  followed by .. I have lost
                 equipment there is an Oxymoron....

                 Grounding when done correctly will protect your equipment
                 from having the type of damage you are describing.... and
                 yes there are some ways to measure and determine if your
                 grounding is proper !


                 BTW, Audio affects of a Lightning strike,  shaking stuff
                 etc etc is due to sound waves generated.. (sort of a mini
                 explosion)... makes for great sound effect, but has
                 nothing to do with electrical damage to equipment.

                 :)


                 Faisal Imtiaz
                 Snappy Internet & Telecom
                 7266 SW 48 Street
                 Miami, FL 33155
                 Tel: 305 663 5518 x 232 <tel:305%20663%205518%20x%20232>

                 Help-desk: (305)663-5518 <tel:%28305%29663-5518> Option 2
                 or Email: supp...@snappytelecom.net

                 
------------------------------------------------------------------------

                     *From: *"Glen Waldrop" <gwl...@cngwireless.net
                     <mailto:gwl...@cngwireless.net>>
                     *To: *af@afmug.com <mailto:af@afmug.com>
                     *Sent: *Tuesday, December 29, 2015 6:02:24 PM
                     *Subject: *Re: [AFMUG] WISP insurance

                     Forgot to mention, this was one hell of a storm.

                     Lightning from *several* miles away shook my home
                     enough that the dishes rattled, the TV moved, cabinet
                     doors opened and closed, etc, for upwards of 45 seconds.

                     I’m honestly surprised we only lost one tower in that
                     storm. I was preparing myself for putting up at least
                     a couple of replacement towers over my Christmas break
                     instead of goofing with the wife and kids. We got
                     lucky and only lost some electronics.
                     *From:* Glen Waldrop <mailto:gwl...@cngwireless.net>
                     *Sent:* Tuesday, December 29, 2015 4:57 PM
                     *To:* af@afmug.com <mailto:af@afmug.com>
                     *Subject:* Re: [AFMUG] WISP insurance
                     It is grounded pretty well, couple of ground rods,
                     tower is grounded and the copper goes to the top,
                     tallest point for quite a ways out there. The strike
                     also blew out the neighboring transformer (didn’t hit
                     my equipment directly).

                     I have not been tying in my electrical ground with my
                     tower ground. I do believe I’m about to change that.
                     I do have a few other towers where the electrical
                     ground is tied into the tower ground which is also
                     tied to a copper wire (6 or 8, depending on what I had
                     at the time) the entire length of the tower, bolted to
                     the tower at the top and bottom.

                     Those have also been struck.

                     One of my most recent ones ran up the ethernet cable,
                     fried the equipment at the top. POE on the ground
                     survived, UPS survived and the surge suppressor
                     (10/100M fusible link essentially) survived. The only
                     radio to survive the strike was the only one I had
                     forgotten to install a suppressor on. They were all
                     replaced of course. The only equipment I’ve seen
                     survive an actual lightning strike without a hiccup is
                     the RB600. Everything else seems to die within 6 months.

                     It appears the surge went through the ground (which
                     we’ve gone over several times) into the surge
                     suppressor, into the ethernet and blew out the radios.

                     Any speculation on that would be awesome. The only
                     thing that makes sense is that maybe the static was
                     close enough to hit the electrical ground and go up
                     the tower, but we’ve checked the ground rods and
                     copper, bolts, etc.
                     *From:* Joshaven Mailing Lists
                     <mailto:lis...@joshaven.com>
                     *Sent:* Tuesday, December 29, 2015 1:18 PM
                     *To:* af@afmug.com
                     *Subject:* Re: [AFMUG] WISP insurance
                     Kinda off topic... Insurance of another type (avoidance)
                     I often find locations where the grounds are hooked up
                     to the tower ground which includes one or more ground
                     rods… but what often goes unrealized is that the
                     system is also grounded to another system through the
                     utility company… and the tower and the utility company
                     may not be properly bonded.  So the lightning finds
                     the big tower, and thinking it is a lightning rod…
                     uses some of the path to ground through rods at the
                     base of the tower but then also uses the path through
                     the equipment to get to the power utility ground…. and
                     pop goes the radio and router and such… Just don’t be
                     that guy that connects the big lightening rod to the
                     utility power ground through your router...
                     Your equipment should be surviving lightning strikes.
                     Large towers can be struck multiple times per month
                     and equipment can be on them for years without any
                     damage at all.  The fact that you lost equipment says
                     that the strike was either direct to your equipment or
                     you have a grounding issue that made your equipment a
                     better path to ground.
                     At some sites commercial radio engineers will even
                     bring in a beaded cable from the tower and spread it
                     across the floor to set all equipment on just to be
                     sure that the ground panes are entirely bonded.  The
                     reason that equipment blows is that the difference in
                     positive to negative current is out of range.  When
                     you get a lightning strike and things are not well
                     bonded then you can have variances between grounds in
                     the order of thousands of volts which will make your
                     equipment pop like a fire cracker…  if your ground is
                     at 10,000v (relative to an average earth voltage) and
                     your equipment is at 10,024v then the potential
                     between them is 24v.  It is like a bird setting on a
                     high voltage line… somehow they don’t “feel” the high
                     voltage… The trick to surviving a lightning strike is
                     to bond all grounds well so ground is constant and
                     then to have your power level referenced from that
                     ground.  This way if the earth ground or the tower
                     ground or anything else has a sudden change then your
                     equipment changes with it and remains relatively the
                     same. After bonding your grounds properly so that you
                     don’t end up with thousands of volts difference
                     between two grounds like your power company ground and
                     the tower that your equipment is mounted to… then you
                     can install good surge equipment that will handle
                     current overages in the event that you need it.
                     The thing to keep in mind when grounding your
                     equipment is that you don’t want your equipment to
                     experience a situation like 0v for negative, 24v for
                     positive and 50,000v for ground.  If your equipment
                     ground plane floats with a strike then it won’t even
                     know that it experienced a surge. Just like a boat
                     going over shallower and deeper water — who knew
                     unless they had a fish finder running?
                     During a strike, you don’t want a 5,000v on the
                     utility ground while you have a 25,000v on the tower…
                     If the cable between the two (or patch of earth
                     between rods) won’t handle the surge or the impedance
                     is too high then your equipment will possibly have two
                     grounds with two very different power levels so the
                     power will transfer from your shielded cable through
                     your router chassis to the utility power until a
                     something pops.  The bottom line make the tower,
                     earth, & utility power all the same and properly
                     ground your equipment to that and you’ll survive most
                     strikes perfectly fine.
                     if you want some good reading google the terms:
                     “copper.org <http://copper.org> lightning”  they have
                     some great write-ups with pictures of the good, bad
                     and ugly.
                     Sincerely,
                     Joshaven Potter
                     Google Hangouts: j...@g2wireless.co
                     Cell & SMS: 1-517-607-9370 <tel:1-517-607-9370>
                     supp...@joshaven.com <mailto:supp...@joshaven.com>

                         On Dec 27, 2015, at 10:31 PM, Craig House
                         <cr...@totalhighspeed.net> wrote:
                         2 in a year?  We had 7 last night.

                         Sent from my iPhone

                         On Dec 27, 2015, at 21:22, Glen Waldrop
                         <gwl...@cngwireless.net> wrote:

                             We’ve had another lightning strike, at least
                             the second one this year.

                             I’ve got this feeling that our insurance
                             company is probably going to start to get a
                             little difficult in the near future.

                             Who do you guys recommend?

                             I’ve read about a few that cover everything,
                             CPE, tower equipment, towers, labor, etc... I
                             imagine those probably cost roughly what we
                             bring in a year, but...
                             Thanks guys.








Reply via email to