Does the transfer switch just switch the two main hot legs?  I assume so or you 
would not be asking.  

No problem bonding gen neutral to gnd.  
But how do your loads get a good bonded neutral when on utility power if you 
lift that bond?

I think you are safe in keeping them all connected.  With the gen neutral 
bonded at the transfer switch, there should not be any risk of a neutral 
floating high and back feeding the sub panel.  

Am I missing something?

From: Adam Moffett 
Sent: Monday, August 15, 2016 1:16 PM
To: Animal Farm 
Subject: [AFMUG] Ground-Neutral bond for generator subpanel

I was planning to add a Generac to a site and connect the transfer switch to a 
subpanel rather than the main panel.  The "utility" input to the transfer 
switch would come from a 50-amp breaker in the main service panel.  

I was thinking I would remove the ground-neutral bond in the transfer switch 
and the subpanel, and that's fine as long as we're on utility power.  It 
occurred to me today that when the transfer switch triggers and we switch to 
generator power that we'll lose the ground-neutral bonding in the main 
panel....and there would no longer be any ground-neutral bond anywhere until it 
switches back.  

I could easily add a 4ga ground-neutral jumper inside the generator, but I'm 
wondering if that's Kosher.  

I have an electrician I can ask, but I was hoping somebody here happens to know 
whether that's ok. 