Leave as is... Don't create issues... Like folks that cut ground plugs off
!!!

On Aug 15, 2016 1:39 PM, "Adam Moffett" <dmmoff...@gmail.com> wrote:

> @George & Seth, yup I was being dense, neutral is not switched.
>
>
> ------ Original Message ------
> From: "George Skorup" <geo...@cbcast.com>
> To: af@afmug.com
> Sent: 8/15/2016 3:36:41 PM
> Subject: Re: [AFMUG] Ground-Neutral bond for generator subpanel
>
>
> What switch are you installing? Generac or something else? In a standard
> 1ph 240 setup, the neutral isn't switched.
>
> The Generac switches with a built-in load center (such as the RTG) are
> designed as a sub-panel off of the main. You pull your hot and neutrals
> over for circuits that you want on gen. Since it's considered a sub-panel,
> the neutrals MUST go with the hots, but the grounds can stay at the main. I
> know it's very tempting to leave the neutrals in the main and pull just the
> hots over, but it's not to code.
>
> On 8/15/2016 2:16 PM, Adam Moffett wrote:
>
> I was planning to add a Generac to a site and connect the transfer switch
> to a subpanel rather than the main panel.  The "utility" input to the
> transfer switch would come from a 50-amp breaker in the main service
> panel.
>
> I was thinking I would remove the ground-neutral bond in the transfer
> switch and the subpanel, and that's fine as long as we're on utility
> power.  It occurred to me today that when the transfer switch triggers and
> we switch to generator power that we'll lose the ground-neutral bonding in
> the main panel....and there would no longer be any ground-neutral bond
> anywhere until it switches back.
>
> I could easily add a 4ga ground-neutral jumper inside the generator, but
> I'm wondering if that's Kosher.
>
> I have an electrician I can ask, but I was hoping somebody here happens to
> know whether that's ok.
>
>
>

Reply via email to