What switch are you installing? Generac or something else? In a
standard 1ph 240 setup, the neutral isn't switched.
The Generac switches with a built-in load center (such as the RTG) are
designed as a sub-panel off of the main. You pull your hot and neutrals
over for circuits that you want on gen. Since it's considered a
sub-panel, the neutrals MUST go with the hots, but the grounds can stay
at the main. I know it's very tempting to leave the neutrals in the
main and pull just the hots over, but it's not to code.
On 8/15/2016 2:16 PM, Adam Moffett wrote:
I was planning to add a Generac to a site and connect the transfer
switch to a subpanel rather than the main panel. The "utility" input
to the transfer switch would come from a 50-amp breaker in the main
service panel.
I was thinking I would remove the ground-neutral bond in the transfer
switch and the subpanel, and that's fine as long as we're on utility
power. It occurred to me today that when the transfer switch triggers
and we switch to generator power that we'll lose the ground-neutral
bonding in the main panel....and there would no longer be any
ground-neutral bond anywhere until it switches back.
I could easily add a 4ga ground-neutral jumper inside the generator,
but I'm wondering if that's Kosher.
I have an electrician I can ask, but I was hoping somebody here
happens to know whether that's ok.