Am 13.01.2013 um 15:12 schrieb Andy Pugh:

> 
> 
> On 13 Jan 2013, at 11:57, Michael Haberler <[email protected]> wrote:
> 
>> .. The Following Error Position field refers to the deviation of current 
>> actual position from the machine commanded position.
> 
> Though that doesn't mention which iteration of the commanded position. 
> I am of the opinion that f-error is how close the machine is to where it was 
> told to be, and the pid "error term", which isn't actually an error in the 
> sense of a problem, is the basis for the PID calculations. 
> 
> They are different things, and the current situation is correct. 

Nobody can falsify your argument because you dont give a correctness criterium 
to verify against - a formal definition of what ferror is supposed to mean for 
you

However, if you are suggesting that ferror means 'the difference between where 
a joint is <now> and where it is supposed to be <now>', then that difference is 
not subject to variation by joint speed or servo period - it is just a distance

if you use that definition, then the current ferror is clearly wrong because 
its absolute value depends proportionally on joint speed and inversely on the 
servo period

to see why a value based on 'the difference between where a joint was <last 
time around> and where it is <now>' isnt useful to determine if a machine is 
off-path, assume the following steady state model:

- perfectly tuned pid loop with an I term, such that commanded vel == actual 
vel hence mean(pid.error) == 0 (mean because of quantisation noise)
- a linear move underway say 

The only ferror which you _ought_ to see in such a situation is the 
quantisation noise, a triangular wave which is zero at the middle of the 
sampling period, and has maxima at vel/dt and -vel/dt (provided you could 
sub-sample the noise with a higher rate)

What you _actually_ see is that noise offsetted by the residual term, which is 
a) wrong and keeps tripping false positives b) there is no explanation why 
ferror should in any way depend on speed or sampling interval.

A second thought experiment to show why it is wrong:

Assume above move, and you could vary the servo period by a knob. 

As long as the servo frequency is sufficiently above 2 * the cutoff frequency 
of the pid/machine system, that system _should_ continue to run in steady 
state. However, by lowering the servo frequency you _increase_ ferror (why?) 
and eventually trip a following error while there is actually no path deviation 
at all.

That said, of course you can conceive a value which compares last commanded to 
current position like in the current code - it's just not meaningful for 
determining path deviation. The only reason why it doesnt bug more folks is 
because machines used around here are too slow to make it an issue.

I think some of the terminology misconceptions about ferror stem from mixup 
with residual error terms of a P-only PID loop. But that is a PID property, not 
a path deviation problem.

-m

re PMAC NC manual: given the thoroughness of that manual I would be very 
surprised to find such a gaffe in a fundamental definition; I'm sure Curtis 
would answer such a question

> ------------------------------------------------------------------------------
> Master Visual Studio, SharePoint, SQL, ASP.NET, C# 2012, HTML5, CSS,
> MVC, Windows 8 Apps, JavaScript and much more. Keep your skills current
> with LearnDevNow - 3,200 step-by-step video tutorials by Microsoft
> MVPs and experts. ON SALE this month only -- learn more at:
> http://p.sf.net/sfu/learnmore_123012
> _______________________________________________
> Emc-developers mailing list
> [email protected]
> https://lists.sourceforge.net/lists/listinfo/emc-developers


------------------------------------------------------------------------------
Master Visual Studio, SharePoint, SQL, ASP.NET, C# 2012, HTML5, CSS,
MVC, Windows 8 Apps, JavaScript and much more. Keep your skills current
with LearnDevNow - 3,200 step-by-step video tutorials by Microsoft