I read in !emc-pstc that cherryclo...@aol.com wrote (in <ad.1718da5d.298
29...@aol.com>) about 'EN 61000-3-2 applicability and let-outs', on Fri,
25 Jan 2002:
>    Dear John 
>    Thank you for your replies. 
>    A couple of points... 
>
>    Optional application of standards: I believe there is nothing to stop 
>    purchasers from using any IEC standards in their contracts with suppliers. 
>    So a purchaser of a 30A/phase equipment could specify that the equipment 
>    must meet the emissions limits set out in IEC 61000-3-2. Nothing to do 
> with 
>    CE marking, of course, merely a private agreement. This was what I meant 
> by 
>    'optional' in the below. 

But that is crazy! Pardon my French, but *there are no emission limits
for a 30 A equipment in the standard*. What you are saying is that a
purchaser might impose contractually limits appropriate for, say, a 5 A
equipment to a 30 A equipment, which is indeed true but hardly more
realistic than a requirement for no emissions at all. It falls into the
same category as the all too common 'contractual requirement', 'The
equipment shall comply with all British, European and International
Standards.'. Does that include the one for toilet paper?

>
>    Do I understand from the following correspondence... 
>    QUOTE 
>    >    4) My copy of EN 61000-3-2 has a paragraph at the end of its Scope 
>    section 
>    >    that says: 
>    >    "Special equipment, which is not widely used and is designed in such 
> a 
>    way 
>    >    that it is unable to comply with the requirements (limits), may be 
>    subject 
>    >    to installation restrictions. The supply authorities shall be 
> notified 
>    as 
>    >    authorization may be required before connection." 
>
>    This gobbledegook was deleted by the Millennium Amendment (MA, aka A14 
>    to EN61000-3-2). No-one could define 'special' and 'not widely used', 
>    when challenged to do so, so out it came! 
>
>    >    So custom-made or low-volume manufactured equipment (even if under 
>    >    16A/phase) does not have to comply with EN 61000-3-2, as long as 
> their 
>    users 
>    >    check with their power suppliers that they are OK to be connected. 
>
>    Yes, this is explained *properly* in clause 4 of the MA. 
>    UNQUOTE 
>    ... that although the 'gobbledygook' paragraph has been removed the option 
>    to not comply with EN 61000-3-2 still exists as long as users check with 
>    their power suppliers that they are permitted to connect the equipment 
>    concerned? 
>
Yes. I suggest you get the edition of the standard that is notified in
the OJEC and see for yourself. Be careful! CENELEC in its 'wisdom' has
got out of step with IEC, so there is an amended First Edition of the EN
AND a 'Second Edition' which is actually 6 months out-of-date compared
with the amended First Edition, unless you are into kitchen appliances. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
After swimming across the Hellespont, I felt like a Hero.
PLEASE do NOT copy news posts to me by E-MAIL!

-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Michael Garretson:        pstc_ad...@garretson.org
     Dave Heald                davehe...@mediaone.net