Dear John
Thank you for your replies.
A couple of points...

Optional application of standards: I believe there is nothing to stop 
purchasers from using any IEC standards in their contracts with suppliers. So 
a purchaser of a 30A/phase equipment could specify that the equipment must 
meet the emissions limits set out in IEC 61000-3-2. Nothing to do with CE 
marking, of course, merely a private agreement. This was what I meant by 
'optional' in the below.

Do I understand from the following correspondence...
QUOTE
>    4) My copy of EN 61000-3-2 has a paragraph at the end of its Scope 
section 
>    that says: 
>    "Special equipment, which is not widely used and is designed in such a 
way 
>    that it is unable to comply with the requirements (limits), may be 
subject 
>    to installation restrictions. The supply authorities shall be notified 
as 
>    authorization may be required before connection." 

This gobbledegook was deleted by the Millennium Amendment (MA, aka A14
to EN61000-3-2). No-one could define 'special' and 'not widely used',
when challenged to do so, so out it came!

>    So custom-made or low-volume manufactured equipment (even if under 
>    16A/phase) does not have to comply with EN 61000-3-2, as long as their 
users 
>    check with their power suppliers that they are OK to be connected. 

Yes, this is explained *properly* in clause 4 of the MA.
UNQUOTE
... that although the 'gobbledygook' paragraph has been removed the option to 
not comply with EN 61000-3-2 still exists as long as users check with their 
power suppliers that they are permitted to connect the equipment concerned?

Regards, Keith Armstrong
www.cherryclough.com

In a message dated 24/01/02 22:31:21 GMT Standard Time, j...@jmwa.demon.co.uk 
writes:

> Subj:Re: EN 61000-3-2 applicability and let-outs
> Date:24/01/02 22:31:21 GMT Standard Time
> From:    j...@jmwa.demon.co.uk (John Woodgate)
> Sender:    owner-emc-p...@majordomo.ieee.org
> Reply-to: <A HREF="mailto:j...@jmwa.demon.co.uk";>j...@jmwa.demon.co.uk</A> 
> (John Woodgate)
> To:    emc-p...@majordomo.ieee.org
> 
> I read in !emc-pstc that cherryclo...@aol.com wrote (in <84.222da8c6.298
> 1a...@aol.com>) about 'EN 61000-3-2 applicability and let-outs', on Thu,
> 24 Jan 2002:
> >    Dear John 
> >    I understand the following statements to be true. 
> >    Please make corrections / comments where necessary. 
> >
> >    1) EN 61000-3-2 only applies to equipment consuming up to 16A/phase, 
> and 
> >    there are no mandatory harmonic limits in the EU (yet) for 
> higher-powered 
> >    equipment, other than what the power supplier might impose. 
> 
> Yes. Furthermore , it applies only to equipment intended to be connected
> to the *public* LV supply.
> >
> >    So EN 61000-3-2 is optional for equipment consuming >16A/phase. 
> 
> No. It *does not apply*. There are no limits stated for over 16A.
> >
> >    2) EN 61000-3-2 currently has a let-out for "professional equipment" 
> that 
> >    consumes more than 1kW, so its application is optional for that 
> category of 
> >    equipment too. 
> 
> I don't know what you mean by 'optional'. Since there are *no limits*
> for professional equipment above 1 kW, there is nothing to 'apply'.
> >
> >    This could exclude many of the larger products sold solely for 
> commercial 
> >    and/or industrial use from EN 61000-3-2. 
> 
> Yes, up to 16A/phase. These products are relatively few in number and
> have diverse 'harmonic signatures' (complex spectra). Their impact on
> the network is small.
> >
> >    (Maybe the combined air-conditioner / personal computer may not be 
> such a 
> >    bad idea if it gets consumption up above 1kW!). 
> 
> Yes, we have heard a lot about joke products like that in the WG. The
> joke is wearing a bit thin now.
> >
> >    3) The 'public low voltage supply' is a 4156/230V supply with more 
> than one 
> >    consumer connected. Large plants or office building often take their 
> power 
> >    at MV (11kV or more) and transform their own LV supply with their own 
> >    distribution transformer - creating a 'private' low voltage supply 
> dedicated 
> >    for their own use. 
> >
> >    EN 61000-3-2 is optional for any equipment sold solely for use on such 
> >    dedicated low voltage supplies. 
> 
> It *does not apply*.
> >
> >    Privately-generated LV supplies ditto. 
> 
> It *does not apply*. I think your references to 'optional' may create
> (even more!) confusion, which we definitely do not need.
> >
> >    4) My copy of EN 61000-3-2 has a paragraph at the end of its Scope 
> section 
> >    that says: 
> >    "Special equipment, which is not widely used and is designed in such a 
> way 
> >    that it is unable to comply with the requirements (limits), may be 
> subject 
> >    to installation restrictions. The supply authorities shall be notified 
> as 
> >    authorization may be required before connection." 
> 
> This gobbledegook was deleted by the Millennium Amendment (MA, aka A14
> to EN61000-3-2). No-one could define 'special' and 'not widely used',
> when challenged to do so, so out it came!
> 
> >
> >    So custom-made or low-volume manufactured equipment (even if under 
> >    16A/phase) does not have to comply with EN 61000-3-2, as long as their 
> users 
> >    check with their power suppliers that they are OK to be connected. 
> 
> Yes, this is explained *properly* in clause 4 of the MA.
> >
> >    Maybe they could agree to deal with any harmonic issues at site-level, 
> by 
> >    installing an active harmonic cancellation unit. 
> 
> Yes, if necessary, but it may not be necessary.
> >
> >    I realise that none of the above give much comfort to manufacturers of 
> >    domestic or consumer products, but maybe a computer manufacturer could 
> offer 
> >    a version without PFC only for use in installations that have a 
> dedicated LV 
> >    supply. 
> 
> They don't want to do that, but some test equipment manufacturers do.
> >
> 
> -- 
> Regards, John Woodgate, OOO - Own Opinions Only. 
> http://www.jmwa.demon.co.uk 
> After swimming across the Hellespont, I felt like a Hero.
> PLEASE do NOT copy news posts to me by E-MAIL!
> 