In message <6.1.0.6.2.20090327004517.030f4...@pop.randolph-telecom.com>, 
dated Fri, 27 Mar 2009, Joe Randolph <j...@randolph-telecom.com> writes:

>A Class 2 supply is the most common type of supply that I have seen for 
>POE injection.  And yes, the output should be isolated from earth 
>ground to comply with IEEE 802.3af.

Can somebody explain to me why an isolated power supply is 'safer' than 
an earthed one? I am particularly concerned that this applies to IT 
networks and anything else that may run through, for example, roof voids 
and similar spaces. Within one room, as for Class II consumer products, 
the techniques is probably acceptable.

I know there are 'segregation' requirements, but cable runs can be 
disturbed by non-electrical people during maintenance. The point is that 
cable damage (by humans, rodents or building movements) can create a 
connection between live mains and the 'SELV' circuit. Since the latter 
is not earthed, the fault can persist indefinitely, until someone 
contacts the SELV circuit. The hazard is great, the probability is low, 
and to me that results in a tick in the 'unacceptable risk' box.

We now have the concept of 'PELV', protected extra-low voltage, which 
has reinforced insulation from mains voltage AND is earthed (preferably 
at one point only, to avoid currents due to earth potential differences. 
I think that all 'SELV' requirements must be re-examined to see if they 
should be changed to 'PELV'. In hazard-based terms, there is no contest. 
SELV has two safeguards, PELV has three.
>
>Personally, I do not see any safety compliance problems with this 
>construction when used as intended (inside lines).
>
>By the way, one problem that I *have* seen with this construction is 
>performance related.  Most of these POE injection power supplies are 
>switching converters, and the Y-caps used on the input for EMI 
>suppression create a voltage divider that places a very high 50/60 Hz 
>common mode noise signal (typically one half of the AC mains voltage) 
>on the Ethernet outputs. 

How can Y-caps do that? Y caps go from both mains poles to earth.

>This means that an IP telephone powered by the POE injector will be 
>riding on the 50/60 Hz common mode noise.  The analog audio circuits in 
>the IP phone, such as the microphone for a hands-free mode, can be 
>sensitive to this common mode noise and produce audible hum. 
>
>Grounding the chassis of the POE injector fixes the problem, but most 
>of these devices are ungrounded. 

Then they cannot possibly have Y-caps.

>So, the IP telephone has to be designed with an extraordinary level of 
>50/60 Hz common mode immunity in order to avoid hum in the analog audio 
>path.

It sounds as though people are making some fundamental error that shows 
up as this problem.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
Things can always get better. But that's not the only option.
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@ptcnh.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to