Polarized connectors are not harmonised yet but seems US is following a 
polarized one.  Anyone knows if it is due to this reason?

 

Leakage current is controlled by harmonised safety standard for non-polarized 
connectors.

 

Mains switch on live wire is not mandatory in safety standard.  I encountered 
one occasion during the return analysis that the heater failed in dielectric 
strength test during its product cycle and the customers suffered the 
electrical shock hazard after power off the appliance since the heater was 
connected to live at one end.  Currently the safety standard does not look 
after this area.

 

Scott

 

 

 

 

From: Pete Perkins <peperkin...@cs.com>
Date: Tuesday, 31 January 2017 at 3:32 AM
To: 'Scott Xe' <scott...@gmail.com>, <EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: RE: [PSES] Double Pole Mains Switches, Cord Connected Products

 

Scott, Mike et al,

 

               The single pole switch is intended to be in the line side of the 
input power; in the case where the polarity is reversed, the emc components can 
be powered with line voltage on both Line and  Neutral side increasing the 
electric shock touch current and protective conductor current.  

 

Safety standards need to specify testing in both Normal and Reverse polarity to 
ensure that the touch current and/or protective current is still within the 
limits specified under this condition.  

 

               Use of a double pole switch ensures that this doubling of the 
touch current from the emc filter doesn’t happen.  

 

               This same condition occurs with a single fuse in one pole of the 
input circuit.  

 

:>)     br,      Pete

 

Peter E Perkins, PE

Principal Product Safety & Regulatory Affairs Consultant

PO Box 23427

Tigard, ORe  97281-3427

 

503/452-1201

 

p.perk...@ieee.org

 

From: Scott Xe [mailto:scott...@gmail.com] 
Sent: Monday, January 30, 2017 5:51 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Double Pole Mains Switches, Cord Connected Products

 

Some national plugs may not be reversible but those countries also widely 
acceptable to 2-pin Europe plugs or 3-pin Schuko plugs that are reversible.

 

The safety standards do not need DPDT switch in compliance.  Even though the 
single pole is not restricted to be on the live wire.  Thus the switch on 
neutral wire is still considered acceptance.

 

Needless to say, single pole switch on live wire and DPDT switch are considered 
the best practice in safety perspective.  As I see less and less this practice 
is implemented in the latest products due to no support from harmonised safety 
standards.

 

Regards,

 

Scott

 

 

From: Mike Sherman ----- Original Message ----- <msherma...@comcast.net>
Reply-To: <msherma...@comcast.net>
Date: Sunday, 29 January 2017 at 12:16 AM
To: <EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: [PSES] Double Pole Mains Switches, Cord Connected Products

 

Because of the lack of polarization on many 2 pin European plugs, I have always 
recommended double pole mains switches on cord connected products for the EU 
market. However, I am not finding support for this in standards such as 
60335-1, 60601-1 or 62368-1.

 

Your thoughts will be appreciated, oh experienced group, on:

--safety issue involved

--standards that do require double pole (sometimes referred to as "all-pole") 
mains switches.

 

Mike Sherman

Graco Inc.

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to