In North America, GFCIs are only used in wet environments; kitchens, bathrooms, 
garages, outdoor outlets and such. They are neither require nor used for other 
occupancies. There are exemptions to reduce the risk of nuisance tripping. If 
you want to keep a refrigerator or freezer in your garage, you can wire a 
dedicated circuit with only a single outlet. That outlet would not need a GFCI. 
The concern is more with temporary loads. Permanently connected products don’t 
require a GFCI. (The code requires these products to have a reliable ground 
connection when used in areas that would otherwise require a GFCI.)

The limited use, and the types of loads connected, tend to lead to little 
nuisance tripping.

I did have a case where a GFCI was used in a small data center. (It’s a long 
story as to why it was there and I won’t go into it here.) The GFCI trips at 5 
mA without regards to frequency. We may have a limit of 3.5 mA touch current 
for ITE in certain circumstances, but that is using the human body model. The 
circuit in question measured 1.5 mA touch current using a human body model 
meter. If you used a standard multimeter, the ground current was 9 mA due to 
the higher frequencies. In this case, there was constant nuisance tripping. The 
solution was to rewire the computer room the way it should have been done in 
the first place.

In summary, nuisance tripping of GFCIs has become relatively uncommon in the 
United States.

Ted Eckert
Microsoft Corporation

The opinions expressed are my own and do not necessarily reflect those of my 
employer.

From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Tuesday, January 30, 2018 3:28 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] GFCI vs GFPE


We have an expert on electric shock here, so I won't go further than to say 
that the effect of 30 mA depends very much on how much contact area there is, 
where it is and for how long contact lasts. I am surprised that 6 mA doesn't 
result in nuisance tripping.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
www.woodjohn.uk<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=ViZzB4GPKmnpkKAYIiV9H0xDOgn63brNjp%2BJbbLotx0%3D&reserved=0>

Rayleigh, Essex UK
On 2018-01-30 22:43, Ralph McDiarmid wrote:

Agreed, and current carry-carrying of PE and bonding of internal parts must 
meet stringent UL/CSA requirements. (not mA!)  It seems to me that 30mA is 
close to lethal, and the GFCI outlets Listed over here are 6mA trip.  (still a 
painful shock)



Ralph McDiarmid

Product Compliance Specialist

Solar Business

Schneider Electric





From: John Woodgate [mailto:j...@woodjohn.uk]

Sent: Tuesday, January 30, 2018 2:30 PM

To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>

Subject: Re: [PSES] GFCI vs GFPE



I don't think that is the reason recognized in Europe. The PE circuit has the 
same (or similar) current-carrying capacity as the line circuit(s), so its 
fault-current capacity for 30 s is very large even for a household supply. I 
think the protector is there to prevent fire and to give some protection 
against electric shock, although the latter is compromised so as to prevent 
nuisance-tripping, which would occur if the trip were set at say 5 mA to give 
much better protection.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates 
http://www.woodjohn.uk<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.woodjohn.uk&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=ViZzB4GPKmnpkKAYIiV9H0xDOgn63brNjp%2BJbbLotx0%3D&reserved=0>

Rayleigh, Essex UK

On 2018-01-30 22:03, Kunde, Brian wrote:

I’ve recently come to understand that the 30mA Ground-Fault protectors, often 
built into a circuit breaker, is intended to protect the Protective Earth 
(Safety Ground) circuit in the case of a short circuit (opening the circuit 
before the safety ground could be damaged.  It this correct?



Here is my question. I’m evaluating a cut-off saw (5hp) which uses water to 
keep the blade and material cool.  The manufacturer uses a 3-phase 
supplementary circuit breaker which includes the 30mA GFPE option.  This is a 
very expensive part.  When I asked them why they use the GFPE part, they 
couldn’t give me a good answer.



Would such a part be required on a 3-phase motor driven cutoff saw in either 
North America or Europe?  What standard would dictate this?



If the only purpose of a GFPE is to protect the Ground Circuit, on products 
that can handle shorts without damaging the ground circuit, would a GFPE still 
be necessary?



Where are GFPE typically used? What industry?



Please educate me.  This is a new one on me.



Thanks,

Brian



From: Doug Nix [mailto:d...@ieee.org]

Sent: Friday, January 26, 2018 2:48 PM

To: mailto:EMC-PSTC@LISTSERV.IEEE.ORG

Subject: [PSES] JOB POSTING - ONTARIO, CANADA



PLEASE CONTACT TED TYCZKA DIRECTLY



A very notable, “high-profile” client who is seeking a Safety & Services 
Sales/Business Development Professional - to join their Machine Services 
Division - the focus of the role is to spearhead/lead the sale of Engineering 
Services related to “functional safety.”



The company sells safety training (workshops), machine assessment/audits, 
engineering design per CSA and/or TUV Safety requirements (“Regulatory 
Compliance”).  The company also sells Remediation and Repair Services (of 
industrial machines) together with Service Contracts ... to customers in the 
aerospace, automotive, forestry, food & beverage, as well as, the packaging 
sectors.



The Safety & Services/Business Development Professional can work from a home 
office - anywhere in Ontario. A Bachelor of Science in Mechanical or Electrical 
Engineering, together with the sale of Machine Safeguard devices and the 
application of these, would be desired ... together, with some exposure to 
Industrial Automation and perhaps Robotics. The key is to have some knowledge 
of safety components, safety scanners, switches, controllers, etc. as well as 
machine building experience.



The employer (a very reputable, Global entity/brand) ... who provide a very 
competitive base salary, lucrative annual bonus/incentive program vs. results, 
plus monthly car allowance, Benefits, Matching RRSP + (Training, Career 
Opportunities and upward mobility).



They are good people, seek an ambitious self-starter who can cover sales from 
the “shop floor” level to the “C Suite” (Boardroom). The company have 
established Sales Reps across Canada ... who can work with the Safety & 
Services Sales Specialist ... this role requires “consultative and solutions 
oriented selling ability.



I will ensure absolute confidentiality. Nice opportunity with a great 
organization and strong, capable leadership. Thanks.



Kind professional regards,

Ted Tyczka



President

Golden Mile Management – Consulting Services

2630 Eglinton Avenue East, Toronto, Ontario M1K 2S3

Tel: (416) 266 - 4434

Email: mailto:t...@gmmcs.com

Website: 
http://www.gmmcs.com/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.gmmcs.com%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=HYALta%2BQWDXulyARmb4b5EUHtqqhvkqnUuDgSVcHbi4%3D&reserved=0>

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:emc-p...@ieee.org><mailto:emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=pvyl91TGExXf%2FVUT0oMKFOh%2FzkaERy%2BMkkWUKY4qtwU%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=4wwDnOVYApjmBYO1AyzE6KsLVJhKYk8s0RmrD4F44fU%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=UhEupWkj7H9Piimj%2FLhjWPQZDAGLcmhhAjieRycQsV8%3D&reserved=0>

Instructions: 
http://www.ieee-pses.org/list.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=g1f%2BmaWIMom4w0K8OwCjj%2FDiNOIdZR0cOBsZRZFJme8%3D&reserved=0>

List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=lwjE6Y14JixNkLHWFSrwviv7q7fRn%2FepNNbt8Llk704%3D&reserved=0>

For help, send mail to the list administrators:

Scott Douglas <mailto:sdoug...@ieee.org><mailto:sdoug...@ieee.org>

Mike Cantwell <mailto:mcantw...@ieee.org><mailto:mcantw...@ieee.org>

For policy questions, send mail to:

Jim Bacher <mailto:j.bac...@ieee.org><mailto:j.bac...@ieee.org>

David Heald <mailto:dhe...@gmail.com><mailto:dhe...@gmail.com>

________________________________________

LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:emc-p...@ieee.org><mailto:emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=pvyl91TGExXf%2FVUT0oMKFOh%2FzkaERy%2BMkkWUKY4qtwU%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282906600&sdata=4wwDnOVYApjmBYO1AyzE6KsLVJhKYk8s0RmrD4F44fU%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=PUblcM1pN4b6XJzzSdyHmjreZ%2F2BixZRwK1hqmNtuzY%3D&reserved=0>

Instructions: 
http://www.ieee-pses.org/list.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=qEC4EuVdkxoWtlrRN%2BEyqLWyrAJ2Xg6rS6qkmNKGvg0%3D&reserved=0>

List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=C6agdhqDtCOijP9n26F5MwZ93FEjTA7Y76FOqilZWMI%3D&reserved=0>

For help, send mail to the list administrators:

Scott Douglas <mailto:sdoug...@ieee.org><mailto:sdoug...@ieee.org>

Mike Cantwell <mailto:mcantw...@ieee.org><mailto:mcantw...@ieee.org>

For policy questions, send mail to:

Jim Bacher <mailto:j.bac...@ieee.org><mailto:j.bac...@ieee.org>

David Heald <mailto:dhe...@gmail.com><mailto:dhe...@gmail.com>





______________________________________________________________________

This email has been scanned by the Symantec Email Security.cloud service.

______________________________________________________________________

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<mailto:emc-p...@ieee.org><mailto:emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=629fCWivlVqZXDBbC6CM9SdQdbN6JPeII4SZ0F6rQ%2F0%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=jNyHf%2BQ5txcS8yDNrRTJWMWzFSPfKTC35F8yGsDsm4w%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=PUblcM1pN4b6XJzzSdyHmjreZ%2F2BixZRwK1hqmNtuzY%3D&reserved=0>

Instructions: 
http://www.ieee-pses.org/list.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=qEC4EuVdkxoWtlrRN%2BEyqLWyrAJ2Xg6rS6qkmNKGvg0%3D&reserved=0>

List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=C6agdhqDtCOijP9n26F5MwZ93FEjTA7Y76FOqilZWMI%3D&reserved=0>

For help, send mail to the list administrators:

Scott Douglas <mailto:sdoug...@ieee.org><mailto:sdoug...@ieee.org>

Mike Cantwell <mailto:mcantw...@ieee.org><mailto:mcantw...@ieee.org>

For policy questions, send mail to:

Jim Bacher <mailto:j.bac...@ieee.org><mailto:j.bac...@ieee.org>

David Heald <mailto:dhe...@gmail.com><mailto:dhe...@gmail.com>



-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org><mailto:emc-p...@ieee.org>



All emc-pstc postings are archived and searchable on the web at:

http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=629fCWivlVqZXDBbC6CM9SdQdbN6JPeII4SZ0F6rQ%2F0%3D&reserved=0>



Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=jNyHf%2BQ5txcS8yDNrRTJWMWzFSPfKTC35F8yGsDsm4w%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.



Website:  
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=PUblcM1pN4b6XJzzSdyHmjreZ%2F2BixZRwK1hqmNtuzY%3D&reserved=0>

Instructions:  
http://www.ieee-pses.org/list.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=qEC4EuVdkxoWtlrRN%2BEyqLWyrAJ2Xg6rS6qkmNKGvg0%3D&reserved=0>
 (including how to unsubscribe)

List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=C6agdhqDtCOijP9n26F5MwZ93FEjTA7Y76FOqilZWMI%3D&reserved=0>



For help, send mail to the list administrators:

Scott Douglas <sdoug...@ieee.org><mailto:sdoug...@ieee.org>

Mike Cantwell <mcantw...@ieee.org><mailto:mcantw...@ieee.org>



For policy questions, send mail to:

Jim Bacher:  <j.bac...@ieee.org><mailto:j.bac...@ieee.org>

David Heald: <dhe...@gmail.com><mailto:dhe...@gmail.com>

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=629fCWivlVqZXDBbC6CM9SdQdbN6JPeII4SZ0F6rQ%2F0%3D&reserved=0>

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fproduct-compliance.oc.ieee.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=jNyHf%2BQ5txcS8yDNrRTJWMWzFSPfKTC35F8yGsDsm4w%3D&reserved=0>
 can be used for graphics (in well-used formats), large files, etc.

Website: 
http://www.ieee-pses.org/<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=PUblcM1pN4b6XJzzSdyHmjreZ%2F2BixZRwK1hqmNtuzY%3D&reserved=0>
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282916609&sdata=qEC4EuVdkxoWtlrRN%2BEyqLWyrAJ2Xg6rS6qkmNKGvg0%3D&reserved=0>
List rules: 
http://www.ieee-pses.org/listrules.html<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=02%7C01%7Cted.eckert%40microsoft.com%7C620a3e80f0b34e9c9d1808d568393584%7Cee3303d7fb734b0c8589bcd847f1c277%7C1%7C0%7C636529517282926614&sdata=zSb6pPywC8VkO8%2Blqw6Ea3u%2BFelY8N0ZeFUOfDuaf0I%3D&reserved=0>

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to