On 03/16/2011 12:23 AM, Peter Blodow wrote:
> Hello Kirk,
> I don't see why you should not be able to measure your mains phases with
> an ordinary oscilloscope, set up as usual. At least in this country, the
> three phases of mains current are ground referenced, 230 V effective
> voltage to neutral. Between the phases, as can be figured with a
> triangle formula or by trigonometry, there are 400 V eff. (not ground
> referenced, of course). Connect each phase with a high resistance probe
> or, if exact magnitude is not important, with a small capacitor. It's
> just measuring a ground referenced voltage, a little higher than usual,
> but still. No floating oscar, as long as you don't want to measure
> differentially between phases.
>
>    
I think what he is trying to do is move the scope common the the 
center-tap point of the motor.
When using a 2-phase to 3-phase converter, the motor's center point is 
NOT at ground potential.
This is also true when using several of the unbalanced 3-phase supply 
systems available in the
US, such as corner-grounded and center-grounded open delta supplies.

Jon

------------------------------------------------------------------------------