Gentlemen,

although this may exceed the borders of this list's topics: I have been 
facility manager of a large research company in Germany for 36 years 
now, I have seen many others, talked and bargained t with many power 
providers and thus have a good picture of the power supply situation in 
Germany and, though limited, in Europe (The British sometimes refuse to 
belong to Europe :-) ). I want to explain some things for all to get the 
right idea of how we are running this country electrically:

I want to bet that there is not a single machine shop or even factory in 
all of Germany still running a rotary power converter, except for some 
antique fly wheel DC welding generators or the railway repair teams with 
their 16  2/3  Hz machinery.

We have in Europe

500 kV to 1 MV DC European compound lines between states and countries
380 kV AC power plant and large city connections
220 kV federal state distribution lines
110 kV lines for very large customers as steel companies etc.
50 and 20 kV for city and local supply and large consumers
(10 kV for low energy density regions, dieing out)
400 Volts  for all others

and that's it - all three phase Y, center grounded, down to the smallest 
village, farmstead or house. A small to medium farm hereabouts needs 
about 50 to 100 kW at hop harvest time, so this installation is quite 
necessary. Neutral is made at every 20 kV / 400 V transformer station 
individually by a grounded lead system, connected to the center tap of 
the transformer(s) and distributed as the fourth lead, though less in 
diameter, in the cables. From 10 sq. mm down a fifth lead is split from 
the neutral lead and used as protective earth (PE) in the buildings, 
which usually happens at the distribution box at a building's cable 
entrance. 230 Volts for ordinary home use is made by simply splitting 
off a single phase, each referenced to neutral.

This is part of the basic supplying conditions set by the power 
providers, not to get by when erecting new appliances or buildings. And 
low voltage lines, i.e. 400 V, with the exception of low density 
regions, are all cabled underground, even in our little village. We had 
the roof mounted power line on our house replaced some years ago by 
underground cable on our own demand (it was an obstacle for the 
observatory) which cost about 2000 D-marks at the time, maybe $ 1000 at 
the time. I am sure this is the most reliable regional supply I can imagine.

There is a lot to do, let's wait for it!

Peter Blodow



Jon Elson schrieb:
> On 03/16/2011 2:00 PM, Peter Blodow wrote:
>   
>> Jon Elson schrieb:
>>    
>>
>>     
>>> When using a 2-phase to 3-phase converter, the motor's center point is
>>> NOT at ground potential.
>>>
>>>      
>>>       
>> This is highly dangerous. Never let a motor float electrically! It's
>> wire insulation could be stressed with any voltage to ground, e.g., if
>> the high potential DC circuit insulation fails!
>>    
>>     
> Well, there are many thousands of users running shops, even fairly large 
> commercial shops
> with rotary phase converters in this manner.  Assuming most of these 
> motors are 240/480
> Volt motors and are being run from 240 V single-phase mains, their 
> insulation is not being
> overstressed.  Also, running a motor this way is IDENTICAL in voltage to 
> running from
> a center-grounded open-delta system.  This has one traditional 
> center-tapped 240 V transformer
> as is used in residential service, with one additional 240 V transformer 
> to provide the 3rd phase
> wire.  There are thousands of commercial shops using this service 
> provided by the utilities.
> This allows you to run 120 V appliances from the same service as the 
> 3-phase loads, which
> is a major convenience in the US.  The alternative is either 120/208 
> 3-phase, or separate
> single and 3-phase feeds, or providing your own transformer for office 
> loads.
>
> Jon
>   
>>> This is also true when using several of the unbalanced 3-phase supply
>>> systems available in the US, such as corner-grounded and center-grounded 
>>> open delta supplies.
>>>
>>>      
>>>       
>> Center grounded sounds not so bad. Corner grounded  is less economical,
>> but acceptable from a supplier's point of view. For measuring it's less
>> favourable...
>>
>> I remember two rules from my electricity course at Muskegon, Mich. High
>> School: Ground everything you can get a hold of and always leave one
>> hand in your pocket!
>>
>> Peter Blodow
>>
>> ------------------------------------------------------------------------------
>> Colocation vs. Managed Hosting
>> A question and answer guide to determining the best fit
>> for your organization - today and in the future.
>> http://p.sf.net/sfu/internap-sfd2d
>> _______________________________________________
>> Emc-users mailing list
>> Emc-users@lists.sourceforge.net
>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>
>>    
>>     
>
>
> ------------------------------------------------------------------------------
> Colocation vs. Managed Hosting
> A question and answer guide to determining the best fit
> for your organization - today and in the future.
> http://p.sf.net/sfu/internap-sfd2d
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users
>
>   


------------------------------------------------------------------------------
Colocation vs. Managed Hosting
A question and answer guide to determining the best fit
for your organization - today and in the future.
http://p.sf.net/sfu/internap-sfd2d
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to