John Thornton wrote:
> I just got off the phone with Siemens tech support and "Our systems 
> don't run well on phase converters."
Well, given the way this system works, I'm not surprised by his comment.
But, it is fairly close.  You need to get into it and see WHICH trip it is
getting.  There probably are several different sensing circuits 
(over-voltage,
under-voltage, lost phase, etc.)  and knowing which one is the source of the
trip should be VERY helpful.  Right now you are flying blind, not 
knowing whether
it needs more or less voltage, etc.
>  was the main theme of the 
> conversation as well as we can't run on a Delta system because we need 
> the ground reference I think he said.
>   
But, does the machine bring out the neutral?  I think you said it does 
not, so
his comment does not make sense.  Well, given the way this system works, I'm
not surprised by
> Additionally he suggested a Delta to WYE step up transformer with 
> grounded secondaries between the RPC and the 611
Well, if there's no neutral brought out, that doesn't make sense.  If it 
is SUPPOSED
to have the neutral connected, and the wire has been removed when it was
supposed to be connected, then suddenly, a LOT of things start to make 
sense.

If it needs a neutral connection, it may be possible to connect it to a 
balance
transformer, which is three windings on one core, with all the wires at one
end connected together as the neutral.

When you used the Diesel generator, did you hook the neutral to something?
You said you used the 208 V taps, was this generator a 120-208 Wye
unit?  If it worked fine on the Diesel with NO neutral connection, then
this has no bearing on the problem.  If you DID hook the neutral to
something in the machine, then this may be the most important piece of
data.

Jon

------------------------------------------------------------------------------
Live Security Virtual Conference
Exclusive live event will cover all the ways today's security and 
threat landscape has changed and how IT managers can respond. Discussions 
will include endpoint security, mobile security and the latest in malware 
threats. http://www.accelacomm.com/jaw/sfrnl04242012/114/50122263/
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to