> Not strictly EMC but I am sure people here will know the answer. We all
> know that a 3-phase VFD can often be used off one-phase. Since all the
> current is then pulled off the one leg of the input rectifier, the standard
> wisdom says that you derate the VFD power in this situation by a factor of
> 2 or so.
>
> It occurred to me that since the input circuit should be just a 3-phase
> rectifier, it should work to connect all three input terminals together,
> and feed that from the single phase.
>
> Would it work on  the VFDs you're familiar with?

It should be noted that the de-rating is chiefly because of the much larger 
ripple voltage and ripple current in the filter capacitors (100/120Hz 
ripple frequency vs 300/360 Hz)