On 12/21/2015 12:59 AM, John Thornton wrote:
> An update, I made a star grounding configuration so EVERY ground comes 
> from the same place. I tested with the VFD unplugged and all is fine, 
> plug the VFD in and same problem sserial errors. The VFD is 220v so to 
> use one power source I'd have to run new wire from the panel to the 220v 
> outlet and get a 4 wire plug. Not impossible but a PIA to work up in the 
> attic....

If you have a dual supply and a transformer for AC 110V -> 220V (or the
other way around), then you may need to reverse the polarity of phase
and neutral of the transformer.

You may see common-mode injection because the phase-polarity of the two
supplies are 180 degrees out of sync. The chassis will then be
conducting the capacitively coupled common-mode, which may interfere a lot.


-- 
Greetings Bertho

(disclaimers are disclaimed)

------------------------------------------------------------------------------